• Skip to main content
  • Skip to primary sidebar

Homemade Circuit Projects

Need circuit help? Post them in the comments! I've answered over 50,000!

Blog | Categories | About | Contact | Calculators-online
You are here: Home / Inverter Circuits / How to Design an Uninterruptible Power Supply (UPS) Circuit

How to Design an Uninterruptible Power Supply (UPS) Circuit

Last Updated on August 4, 2020 by Swagatam 64 Comments

In this brief tutorial I have explained how to design a customized UPS circuit at home using ordinary components such as a few NAND ICs and a some relays.

What is an UPS

UPS which stands for uninterruptible power supply are inverters designed to provide a seamless AC mains power to a connected load without a slightest bit of interruption, regardless of sudden power failures or fluctuation or even a brown-out.

An UPS becomes useful for PCs and other such equipment which involve critical data handling and cannot afford mains power interruption during a vital data processing operation.

For these equipment UPS becomes very handy due to its instantaneous power back-up to the load, and for providing the user with ample time to save computer's crucial data, until actual mains power is restored.

This means that an UPS must be extremely quick with its changeover from mains to inverter (back up mode) and vice versa during a possible mains power malfunction.

In this article I have explained how to make a simple UPS with all the bare minimum features, ensuring that it conforms with the above fundamentals and provides the user with a good quality uninterrupted power throughout the course of its operations.

UPS Stages

A basic UPS circuit will have the following fundamental stages:

1) An inverter circuit

2) A Battery

3) A battery charger circuit

4) A changeover circuit stage using relays or other devices such as triacs or SSRs.

Now I have explained how the above circuit stages may be built and integrated together for implementing a reasonably decent UPS system.

Block Diagram

The mentioned functional stages of an uninterruptible power supply unit could be understood in detail through the following block diagram:

UPS block diagram

Here we can see that the main UPS changeover function is carried out by a couple of DPDT relay stages.

Both the DPDT relays are powered from a 12 V AC to DC power supply or adapter.

The left side DPDT relay can be seen controlling the battery charger. The battery charger gets powered when AC mains is available through the upper relay contacts, and supplies the charging input to the battery via the lower relay contacts. When AC mains fails, the relay contacts changeover to the N/C contacts. The upper relay contacts switches OFF power to the battery charger, while the lower contacts now connects the battery with the inverter to initiate the inverter mode operation.

The right side relay contacts are used for changing over from grid AC mains to the inverter AC mains, and vice versa.

A Practical UPS Design

In the following discussion I will try to explain and design a practical UPS circuit.

1) The Inverter.

Since an UPS has to deal with crucial and sensitive electronic appliances, the involved inverter stage must be reasonably advanced with its waveform, in other words an ordinary square wave inverter may not be recommended for an UPS, and therefore for our design we make sure that this condition is aptly taken care of.

Although I have posted many inverter circuits in this website, including sophisticated PWM sinewave types, here we select a completely new design just to make the article more interesting, and add a new inverter circuit in the list

The UPS design utilizes just a single IC 4093 and yet is able to execute a good PWM modified sine wave functions at the output.

inverter circuit for the UPS construction

Parts List

  • N1---N3 NAND gates from IC 4093
  • Mosfets = IRF540
  • Transformer = 9-0-9V / 10 amps / 220V or 120V
  • R3/R4 = 220k pot
  • C1/C2 = 0.1uF/50V
  • All resistors are 1K 1/4 watt

Inverter Circuit Operation

The IC 4093 consists of 4 Schmidt type NAND gates, these gates are appropriately configured and arranged in the above shown inverter circuit, for implementing the required specifications.

One of the gates N1 is rigged as an oscillator to produce 200 Hz, while another gate N2 is wired as the second oscillator for generating 50Hz pulses.

The output from N1 is used for driving the attached mosfets at the rate of 200Hz while the the gate N2 along with the additional gates N3/N4, switches the mosfets alternately at the rate of 50Hz.

This is to ensure that the mosfets are never allowed to conduct simultaneously from the output of N1.

The outputs from N3, N4 break the 200Hz from N1 into alternate blocks of pulses which are processed by the transformer to produce a PWM AC at the intended 220V.

This concludes the inverter stage for our UPS making tutorial.

The next stage explains the changeover relay circuit, and how the above inverter needs to be wired with the changeover relays for facilitating the automatic inverter back up and battery charging operations during mains failure, and vice versa.

Relay Changeover Stage and Battery Charger Circuit

The image below shows how the transformer section of the inverter circuit may be configured with a few relays for implementing the automatic changeover for the proposed UPS design.

The figure also shows a simple automatic battery charger circuit using the IC 741 on the left side of the diagram.

First I have explained how the changeover relays are wired and then we can proceed with the battery charger explanation.

UPS automatic relay changeover

In all there are 3 sets of relays which are used in this stage:

1) 2 nos of SPDT relays in the form of RL1 and RL2

2) One DPDT relay as RL3a and RL3b.

RL1 is attached with the battery charger circuit and it controls the high/low cut charge level cut-off for the battery and determines when the battery needs is ready to be used for the inverter and when it needs to be removed.

The SPDT RL2 and the DPDT (RL3a and RL3b) are used for the instant changeover actions during a power failure and restoration. RL2 contacts are used for connecting or disconnecting the center tap of the transformer with the battery depending on the mains availability or absence.

RL3a and RLb which are the two sets of contacts of the DPDT relay become responsible for switching the load across the inverter mains or the grid mains during power outages or restoration periods.

The coils of RL2 and DPDT RL3a/RL3b are joined with a 14V power supply such that these relays quickly activate and deactivate depending on the input mains status and do the necessary changeover actions. This 14V supply is also used as the source for charging the inverter battery while the mains power is available.

The coil of the RL1 can be seen connected with the opamp circuit which controls the battery charging of the battery and ensures the supply to the battery from the 14V source is cut-off as soon as it reaches the same value.

It also makes sure that while the battery is in the inverter mode and is consumed by the load, its lower discharge level never goes below 11V, and it cuts off the battery from the inverter when it reaches around this level. Both these operations are executed by the relay RL1 in response to the opamp commands.

The setting-up procedure for the above UPS battery charger circuit can be learned from this article which discuses how to make a low high cut off battery charger using IC 741

Now it simply needs to integrate all the above stages together for executing a decent looking small UPS, which could be used for providing an uninterruptible power to your PC or any other similar gadget.

That's it, this concludes our tutorial for designing a personal UPS circuit which can be easily done by any new hobbyist by following the above detailed guide.

You'll also like:

  • 1.  Design your own Sine Wave Inverter Circuit from the Scratch [Tutorial]
  • 2.  Simple 48V Inverter Circuit
  • 3.  PWM Inverter Using IC TL494 Circuit
  • 4.  Sinewave UPS using PIC16F72
  • 5.  Homemade 100VA to 1000VA Grid-tie Inverter Circuit
  • 6.  What’s Islanding in GTI (Grid Tie Inverter)

About Swagatam

I am an electronics engineer with over 15 years of hands-on experience. I am passionate about inventing, designing electronic circuits and PCBs, and helping hobbyists bring their projects to life. That is why I founded homemade-circuits.com, a website where I share innovative circuit ideas and tutorials. Have a circuit related question? Leave a comment.... I guarantee a reply!

Previous Post: « Temperature Controlled DC Fan Circuits
Next Post: 3 Phase Induction Motor Speed Controller Circuit »

Reader Interactions

Comments

  1. Anto Das8 says

    February 27, 2025 at 5:39 pm

    But isn’t the following circuit (in the link) even simpler
    " rel="ugc">comment image

    Reply
    • Swagatam says

      February 27, 2025 at 6:42 pm

      That looks like an online UPS, the above article explains an offline UPS.

      For a correct online UPS you can refer to the following post:
      https://www.homemade-circuits.com/simple-online-ups-circuit/

      Reply
  2. Andrew says

    May 29, 2024 at 9:52 pm

    You mention relays as the switchover mechanism, but do these not create a very short interruption? If so, then this is not truly uninterruptible, just a battery backup?

    Reply
    • Swagatam says

      May 30, 2024 at 8:27 am

      An appropriately rated, good quality relay changeover time will be within 10 ms which is sufficient not to have any impact on any critical appliance.

      Reply
      • Andrew says

        May 30, 2024 at 9:28 am

        Thanks. That is valuable information. I guess the 10ms is bridged by a simple capacitor?

        Reply
        • Swagatam says

          May 30, 2024 at 9:55 am

          Sorry, I did not understand what you meant by, “I guess the 10ms is bridged by a simple capacitor?”

          Reply
          • Andrew says

            May 30, 2024 at 3:47 pm

            Even 10ms is a break in the supply — perhaps enough to cause a microprocessor to restart? I wonder however whether a largish capacitor added to the power supply might hold charge for long enough to stop the supply being interrupted — i.e. to “bridge” that 10ms gap?

            My fundamental point is that there is a distinction between battery backup and uninterrupted power. I am trying to determine whether the design you propose is truly uninterrupted, or just a battery backup with a fast switchover.

            My situation is that I have an alarm system, broadband router, and computers –including a home automation system that is part of the alarm system — in a house that already has a Tesla Powerwall. The Powerwall is effectively a battery backup for the whole house. It can (I gather) take 1 or 2 seconds to switch over to battery in the event of a mains power cut.

            I therefore want a (truly uninterruptible) UPS for these sensitive devices — alarm system, broadband router, and computers — that will keep them operating during the switchover to Powerwall battery.

            When the Powerwall battery is nearly flat, it should warn the computers in advance so they can fire off last messages and shut down gracefully.

            Reply
            • Swagatam says

              May 30, 2024 at 5:27 pm

              Yes, that’s right, all electronic gadgets will have an associated filter capacitor across their supply terminals which should be able to bridge any supply interruption for at least a second.
              The design explained in the above article can be considered a full-fledged UPS, or simply an offline UPS, because it will fulfill the purpose of an UPS, if the 10ms issue is not a concern to the load.
              The main advantage of an offline UPS is that it allows the load to access the pure AC from the grid while the mains AC is available and also allows the inverter section to be completely switched OFF, keeping the stress level on the inverter minimal.
              Nevertheless if you are interested in having a 100% seamless transition between the AC supplies then you can opt for an online UPPS, as explained in the following article:

              https://www.homemade-circuits.com/simple-online-ups-circuit/

              However, in your case it seems your system can work with a DC UPS, which does not require an AC inverter?
              In that case the Supply transition can be absolutely seamless without any interruption at all, even for a fraction of a second.
              I have a related article on this concept too, you can read it here, it can be modified as per personal preferences:
              https://www.homemade-circuits.com/simple-dc-ups-circuit-for-modemrouter/
              Let me know your thoughts on this.

              Reply
              • Andrew says

                May 30, 2024 at 6:06 pm

                Right on all counts! Thanks for the detailed clarification and pointers to your other interesting articles.

                Yes, this one and your first reference assume that continuity of mains AC is required, and I appreciate the distinction between online snd offline.

                In my case the simple DC solution should suffice. The alarm system needs 12v DC. The home automation computer needs 19V DC and the router also needs 12V DC I think. I guess your DC design drops the voltage by 0.6V due to the diodes, but should be near enough.

                I want to add a battery test mode, which will temporarily shut off the input and measure the voltage, and a sensor to tell the system that it is running on the battery— probably an optocoupler on the input side.

                Thanks again for the ideas!

                Reply
                • Swagatam says

                  May 31, 2024 at 8:59 am

                  Sure, a battery test mode can be included, by adding a series current sensing resistor with the battery positive, and then sensing the voltage drop across this resistor to indicate that battery is being used by the load. Optocoupler can be less sensitive than a transistorized sensor, so a transistor should be more preferable.

                  Reply
                  • Andrew says

                    June 4, 2024 at 2:31 pm

                    Cheers

                    Reply
  3. Pieter says

    October 31, 2023 at 10:29 am

    Good day sir

    Thank you for the amazing content.
    Can I please ask that if I use a 6ah 12v battery is it still going to work or am I only going to have to use a 10 amp battery? My second question is what is the power output (watts)of this circuit when running on ups?

    Thank you in advance.

    Reply
    • Swagatam says

      October 31, 2023 at 2:52 pm

      Hi Pieter,
      You can use a 6Ah battery but that will give you lower backup than a 10Ah battery.
      Power will depend on the transformer rating and battery rating.

      Reply
  4. Ochima Joh says

    June 10, 2023 at 2:55 am

    I have always follow your post. I am just a beginner and will wish you send me a functional inverter circuit that I can practice and develop and learn from your wealth of experience.

    Reply
    • Swagatam says

      June 10, 2023 at 8:43 am

      No problem, you can try the first design from this article:

      https://www.homemade-circuits.com/7-simple-inverter-circuits/

      Reply
  5. zied badri says

    August 12, 2021 at 7:03 pm

    hello again sir
    i’m wondering about the ups system i should purchase for the oxygene concetrator system
    can u help with a suggestion
    thank u

    Reply
    • Swagatam says

      August 12, 2021 at 7:37 pm

      Hi Zied, I am sorry, I do not have much information regarding which UPS brand would be best suitable for your application!

      Reply
  6. zied badri says

    August 5, 2021 at 5:26 pm

    hi sir
    i hope ur well
    I’m a student working on an oxygéne concetrator that works with energy 3kw/h , u=220 v , p=1500 w
    i need the circuit of its UPS circuit with its failure system
    Thank you .

    Reply
    • Swagatam says

      August 5, 2021 at 6:11 pm

      Hello zied, do you want an online UPS or offline UPS….I can only provide a basic design

      Reply
      • zied badri says

        August 5, 2021 at 6:25 pm

        i want offline ups
        thank u very much

        Reply
        • Swagatam says

          August 5, 2021 at 6:37 pm

          You will have to make or buy a 1500 watt inverter, and then integrate with it the last circuit from the following article

          https://www.homemade-circuits.com/how-to-convert-inverter-to-ups/

          Reply
          • zied badri says

            August 5, 2021 at 6:42 pm

            thank u sir have a good day

            Reply
            • Swagatam says

              August 5, 2021 at 7:10 pm

              You are welcome!

              Reply
  7. Devesh Singh says

    April 28, 2021 at 9:41 pm

    Hey! Thank you for your explanation.
    I have a doubt about Relays.
    My UPS has 4 Relays (SPDT) (2 – 4pin and 2 – 5pin) [Black outline]
    1st relay (4pin) connects from Mains [Brown Square] input to another relay common.
    2nd relay (5pin) outputs to two windings of the transformer [green and blue Square]
    3rd relay (5pin) outputs to two windings of the transformer [green and yellow Square]
    4th relay (4pin) connects from 3rd relay common to UPS output [Brown Square-bottom left]
    Here are the images – https://drive.google.com/drive/folders/1Mx6_oDjlHnM-KjAIyRmf9EYQ4ut5g9Pe?usp=sharing
    Numbers along the transformer input wires are – when you apply 240V between green and black you get 7.3V at the secondary, similarly for other windings.
    The Black and Red square are connected to the battery and, the blue and red rectangle are connected to the secondary of the transformer.

    I want to ask “How does the current flows?” “How does it charges the battery?” “How are the relay connections?”

    What I know (guess),
    The current flows from live wire (main) to common (relay 1) to Normally open (relay 1) to common (relay 2) to normally closed (relay 2) to normally closed (relay 3) to common (relay 3) to common (relay 4) to normally open (relay 4) to UPS output.
    I made a block diagram also.

    “Why are there different connections to different windings?”

    Reply
    • Swagatam says

      April 29, 2021 at 6:54 pm

      Hi, It is extremely difficult to figure out the wiring and the functioning of the relay just by referring to the images your provided…I will need schematic diagram to actually know how the system is configured and its working.

      Reply
  8. Uday says

    August 13, 2020 at 3:37 pm

    Hi Sir,
    Could you pls post circuit for 2 to 5KW UPS.

    Thank and Regards
    Uday Joshi

    Reply
    • Swagatam says

      August 13, 2020 at 6:38 pm

      Uday, please build a smaller version first, may be a 100 watt design, if you succeed then you can easily upgrade it to any desired higher level….

      Reply
      • uday joshi says

        August 15, 2020 at 8:19 pm

        Yes , I thing you are right. Any link for 100 watt??

        Regards
        Uday

        Reply
        • Swagatam says

          August 16, 2020 at 9:14 am

          You can try the concept explained in the above post, if everything goes well, you can upgrade it to higher levels.

          Reply
  9. Prashant says

    June 15, 2020 at 6:24 pm

    Hi Swagatam,

    I am looking to make a simple DC-DC UPS for my modem. I found this solution on instructables – however the flaw in the design is that if mains goes off when battery is discharged, it will fail to supply power. This design does not have a relay in it.

    Can you help me with similar component selection – however by adding a relay that allows fallback on battery ONLY when mains go off. I would like to use below set of parts for this design –

    1. DC DC Boost – MT3608
    2. LiIon Charger – TP4056

    Let me know if I need to go for different components. Appreciate your help and response.

    ~Prashant

    Reply
    • Swagatam says

      June 16, 2020 at 10:14 am

      Hi Prashant, Please see the following image, I hope this may fulfill your requirement:

      comment image" alt="router UPS using TP4056 Li-Ion charger" />

      Reply
    • Swagatam says

      June 16, 2020 at 10:33 am

      You can build the same without a relay as shown below:

      comment image" alt="DC UPS with diodes and li-ion charger" />

      Reply
      • Prashant says

        June 16, 2020 at 12:49 pm

        Really appreciate the inputs!!! And prompt response. Will build both of them and get back with final product feedback. Thanks!

        ~Prashant

        Reply
        • Swagatam says

          June 16, 2020 at 2:05 pm

          No Problem!

          Reply
  10. Rashaka Lufuno says

    May 21, 2020 at 7:13 pm

    Thanks again for such a useful UPS post in a need full time. I just have few question though,
    1. Since I will be using a 9v-0-9v / 220 Trafo , is it advisable to wind another auxiliary 14V for charging purpose avoiding using external adapter .
    2.Considering the availability and cost of high freaquency Ferrite Trafo, can the charger and change over switch be integrated to high freaquency smps inverter
    I will appreciate your assistance

    Reply
    • Swagatam says

      May 22, 2020 at 9:58 am

      Glad you liked the post, I’ll try to help you:
      1) you can have an auxiliary winding, no problem, although using an external adapter appears to be an easier and hassle free option.
      2) If the SMPS also employs the same center tap MOSFET topology then the above system can e applied in it for getting the same results.

      Reply
      • Evans says

        June 14, 2020 at 4:25 pm

        Hello sir swagatam, please if you don’t mind help me a circuitry for 24v system. Most circuits you use are 12v based, please help. Also sir we can as well make use of the internal mosfet diodes instead of the tedious work of looking for a separate power supply for charging battery coz getting a high current rl3 say for a 6000w ups is much expensive. Do you have any I deal about this?

        Reply
  11. Ariel says

    June 15, 2018 at 6:11 pm

    I like the circuit, but what are the values ​​of the Resistances?

    Reply
    • Swagatam says

      June 15, 2018 at 7:51 pm

      resistors are all 1K

      Reply
  12. mara says

    May 1, 2018 at 8:29 am

    Hi sir.can i know the simulation of offline uninterruptible power supply(UPS) on the MATLAB Simulink and how can i know the system can works as backup power supply when the main supply is powered off from the simulation? Then, what can i do for the improvement harmonic distortion on UPS as the the system is already designed to mitigate distortion? I hope ur can help me. Thanks in advanced !

    Reply
    • Swagatam says

      May 1, 2018 at 12:09 pm

      Hi Mara, you can verify the design by testing it practically and you will find it working with 100% results (if done correctly). I do not have any simulation results for my circuits.

      Reply
  13. K Premila says

    December 30, 2017 at 3:01 pm

    Dear sir,

    The above circuit works with 12 V DC battery, i assume. What should be the current rating of the battery. It is mentioned that refrigerator will work. What is the maximum load(s) that can be connected with the above circuit. If i want to increase the loads, say double the load what modifcation is to be done? Thanks and regards.

    Reply
    • Swagatam says

      December 30, 2017 at 5:39 pm

      Dear Premila,

      You can upgrade the inverter wattage as per your requirement. You just have to use a transformer that matches the specs of the load, similarly use a battery as per the transformer and the load…and the mosfets which can handle the trafo and battery current confortably, only these 3 parameters should be matched for ensuring the required output wattage.

      Reply
  14. Tun says

    May 7, 2017 at 5:17 pm

    Thanks for the tip, and keep on the good work Sir.

    Reply
    • Swagatam says

      May 8, 2017 at 2:42 am

      you are welcome Tun

      Reply
  15. Tun says

    May 6, 2017 at 7:32 pm

    Hi, Mr Swagatam, I do really like to ask you these question that seem to be bothering for a long time. It all about modifying a 650va UPS (introducing two way power source e.g both battery and solar panels), besides, I need to know the suitable nos(watt ratting) for panels. Thank you

    Reply
    • Swagatam says

      May 7, 2017 at 8:40 am

      Hi Tun, please refer to the following article for solving your doubts

      https://www.homemade-circuits.com/2013/05/how-to-calculate-and-match-solar-panel.html

      Reply
  16. christian manoppo says

    November 22, 2016 at 1:56 am

    Hi, mr.swagatam, I need your help, I have transformer from old ups, I want to built inverter 12vcd to 220vac used this transformer, but the transformer not have center tap, how can I used,, thanks for help..

    Reply
    • Swagatam says

      November 22, 2016 at 6:13 am

      Hi Christian, without a center tap you may have to employ a full bridge inverter topology, as shown below

      https://www.homemade-circuits.com/2014/01/simplest-full-bridge-inverter-circuit.html

      Reply
  17. Swagatam says

    October 23, 2016 at 3:50 am

    son muy bienvenidos a Jesús, agradezco su interés

    Reply
  18. Jesus Te Ama says

    October 22, 2016 at 1:01 pm

    Genial amigo swagatam. Siga así con su trabajo que es exelente. Cuando lo tenga terminado le enviaré fotos o un video del funcionamiento del inversor. Otro gran abrazo

    Reply
  19. Jesus Te Ama says

    October 22, 2016 at 3:56 am

    as this friend Swagatam. I am eager to build this investor to prove it in a refrigerator. I would appreciate greatly place the list of components. a big hug from Argentina

    Reply
    • Swagatam says

      October 22, 2016 at 5:45 am

      Thanks Jesus, I have updated the parts list for you….a big hug to you too from India 🙂

      Reply
  20. Jesus Te Ama says

    October 15, 2016 at 2:26 pm

    Muchísimas gracias has sido muy amable. Exelente tu trabajo te felicito. Saludos

    Reply
    • Swagatam says

      October 17, 2016 at 2:53 am

      De nada jesus!!

      Reply
  21. Jesus Te Ama says

    October 15, 2016 at 4:59 am

    Hello, again

    Where do I find the list of materials investor.

    Officer with a refrigerator? and also with induction motors? thank you very much and sorry to bother you.

    Thank you

    Reply
    • Swagatam says

      October 15, 2016 at 2:05 pm

      Hello Jesus, yes the above inverter circuit can be used with refrigerator and induction motors…I'll try to update the parts list soon in the aboev article

      Reply
  22. Jesus Te Ama says

    October 15, 2016 at 4:17 am

    Y otra pregunta. Sirve este circuito para motores de inducción?

    Reply
  23. Jesus Te Ama says

    October 14, 2016 at 6:59 pm

    Hola nuevamente exelente trabajo. Donde encuentro la lista de materiales del inversor. Y otra pregunta. Funcionaria para un refrigerador? Gracias

    Reply
    • Swagatam says

      October 15, 2016 at 4:39 am

      Hola, please tranlate in English….

      Reply
  24. Swagatam says

    September 3, 2016 at 1:48 am

    Thanks, I already have both of these ideas posted in this website, please use the search box at top right and search for.."humidity", and "incubator" you will be taken to the articles of your choice….

    Reply
  25. NvD says

    July 20, 2016 at 2:21 pm

    sir
    tell me whether this circuit of automatic candle works.The concept is that bulb lights when a lighted match stick is brought near the ldr and off using condensor mic puff off..If not can you tell me the changes in circuit so that it works
    https://drive.google.com/folderview?id=0B-dWJVKXq45-QmxydFA1SXVFYms

    Reply
    • Swagatam says

      July 21, 2016 at 2:38 am

      sorry, the linked circuit will not work.

      and I just missed the MIC function, it means the circuit is supposed to work like a bistable or a flip flop, now it's looking doubtful….can't say just by looking at the diagram will need to be built and checked practically.

      most probably it will not work.

      Reply
    • Swagatam says

      July 21, 2016 at 11:12 am

      you can try the following design:

      https://www.homemade-circuits.com/2011/12/make-electronic-candle-at-home.html

      replace C3 with the LDR

      Reply

Need Help? Please Leave a Comment! We value your input—Kindly keep it relevant to the above topic! Cancel reply

Your email address will not be published. Required fields are marked *

Primary Sidebar

Subscribe to New Circuit Ideas

Categories

  • Arduino Projects (87)
  • Audio and Amplifier Projects (132)
  • Automation Projects (17)
  • Automobile Electronics (101)
  • Battery Charger Circuits (82)
  • Datasheets and Components (102)
  • Electronics Theory (143)
  • Free Energy (37)
  • Games and Sports Projects (11)
  • Grid and 3-Phase (19)
  • Health related Projects (25)
  • Home Electrical Circuits (12)
  • Indicator Circuits (14)
  • Inverter Circuits (87)
  • Lamps and Lights (142)
  • Meters and Testers (69)
  • Mini Projects (46)
  • Motor Controller (64)
  • Oscillator Circuits (27)
  • Pets and Pests (15)
  • Power Supply Circuits (108)
  • Remote Control Circuits (50)
  • Security and Alarm (64)
  • Sensors and Detectors (100)
  • Solar Controller Circuits (59)
  • Temperature Controllers (42)
  • Timer and Delay Relay (49)
  • Transmitter Circuits (29)
  • Voltage Control and Protection (37)
  • Water Controller (36)

Calculators

  • Battery Back up Time Calculator
  • Capacitance Reactance Calculator
  • IC 555 Astable Calculator
  • IC 555 Monostable Calculator
  • Inductance Calculator
  • LC Resonance Calculator
  • LM317, LM338, LM396 Calculator
  • Ohm’s Law Calculator
  • Phase Angle Phase Shift Calculator
  • Power Factor (PF) Calculator
  • Reactance Calculator
  • Transistor Astable Calculator
  • Transistor base Resistor Calculator
  • Voltage Divider Calculator
  • Wire Current Calculator
  • Zener Diode Calculator
  • Filter Capacitor Calculator
  • Buck Converter Calculator
  • Boost Converter Calculator
  • Solar Panel, Inverter, Battery Calculator
  • Wire Current Calculator
  • SMPS Transformer Calculator
  • IC SG3525, SG3524 Calculator
  • Inverter LC Filter Calculator

People Also Search

555 Circuits | 741 Circuits | LM324 Circuits | LM338 Circuits | 4017 Circuits | Ultrasonic Projects | SMPS Projects | Christmas Projects | MOSFETs | Radio Circuits | Laser Circuits | PIR Projects |

Recent Comments

  • Swagatam on Simple Delay Timer Circuits Explained
  • Swagatam on The Role of Inductor Coil in SMPS
  • Swagatam on 7 Modified Sine Wave Inverter Circuits Explored – 100W to 3kVA
  • Swagatam on 7 Modified Sine Wave Inverter Circuits Explored – 100W to 3kVA
  • Victor on 7 Modified Sine Wave Inverter Circuits Explored – 100W to 3kVA

Company

  • Privacy Policy
  • Cookie Policy
  • About Me
  • Contact
  • Disclaimer
  • Copyright
  • Videos
  • Sitemap

Social Profiles

  • Twitter
  • YouTube
  • Instagram
  • Pinterest
  • My Facebook-Page
  • Quora
  • Stack Exchange
  • Linkedin
  • © 2025 · Swagatam Innovations