• Skip to main content
  • Skip to primary sidebar

Homemade Circuit Projects

Need circuit help? Post them in the comments! I've answered over 50,000!

Blog | Categories | About | Contact | Calculators-online
You are here: Home / Inverter Circuits / How to Calculate Solar Panel, Inverter, Battery Parameters

How to Calculate Solar Panel, Inverter, Battery Parameters

Last Updated on May 5, 2025 by Swagatam 166 Comments

In this post I have explained through calculations how to select and interface the solar panel, inverter and charger controller combinations correctly, for acquiring the most optimal results from the set up.

Table of Contents
  • Calculating Solar Panel, Inverter and Battery Charger Specifications
  • Solar Panel, Inverter, Battery Calculator
  • Solar Panel, Inverter & Battery Calculator
  • Results:
  • Estimating Load Wattage
  • Determining Approximate Solar Panel Dimension
  • Calculating Battery Ah
  • Evaluating Charger Controller Specifications
  • Assessing Inverter Specifications

GridTieInverter252CWiringDetails252CDiagram

Calculating Solar Panel, Inverter and Battery Charger Specifications

For the sake of convenience, let's believe you possess a a 100 watt appliance or load that you would like to operate, free of charge through solar power, for around ten hours every night.

In order to exactly determine the dimensions of the solar panel, batteries, charge controller and inverter the following mentioned parameters will need to be strictly calculated and configured.

If you do not want to do all the calculations manually, you can simply use the following calculator for getting the results quickly:

Solar Panel, Inverter, Battery Calculator

Solar Panel, Inverter & Battery Calculator

Solar Panel, Inverter & Battery Calculator

This calculator determines the required solar panel wattage, inverter size, and battery capacity based on your power consumption and backup time.

Results:

Solar Panel WattageInverter SizeBattery Capacity
0 W0 W0 Ah (12V)

Estimating Load Wattage

1) First you will need to estimate how much watts of electricity you may require for the specified load.

Let's say  you have a 100 watt load that needs to be operated for approximately 10 hours, in that case the total power required could be estimated simply by multiplying the load with hours, as given under

100 Watts x 10 hours = 1,000 Watt hours. This becomes the absolute power necessary from the panel.

Determining Approximate Solar Panel Dimension

2) Next, we need to determine the approximate dimensions of the solar panel for satisfying the above estimated load requirement. If we assume a roughly ten hour daily optimal sunshine, the specifications for the solar panel could be simply and quickly calculated as explained in the following expression:

1,000 Watt hours / 10 hours sunlight = 100 Watt solar panel.

However, you may notice that mostly during the summer seasons you may normally get around 10 hours of reasonable amount of sunshine, but the winter season may produce roughly around 4-5 hours of effective sunshine.

Contemplating the above scenario, you too might agree and recommend considering the worst possible sunshine hour into calculation so that even on the weakest of sunshines your load keeps running optimally.

Therefore taking into account the 4 to 5 hours sunshine per day consideration, we calculate the true power for the solar panel which would enable your load to keep running throughout the year .

1,000 Watt hours / 5 hours sunlight = 200 Watt solar panel.

Calculating Battery Ah

3) Once you have calculated the solar panel as per the above calculations, it's time to calculate the AH rating for the batteries that might be required for operating the specified load under all conditions. If the selected battery is rated at 12V, in that case:

Dividing 1,000 Watt hours by 12 Volts = 83 Amp Hours of reserve battery power.

Let's upgrade this value a little more with a 20% added tolerance, which finally gives a rounded up figure of  around 100 AH. Hence, a 100AH 12V battery is what you may finally require for the inverter.

Evaluating Charger Controller Specifications

4) Now, to figure out how big your solar charge controller would need to be for the above calculated parameters, you might need to take your solar panel current or the Amperage specs into consideration, which may be simply gotten by dividing the panel's wattage rating with its voltage rating (Ohms law remember?)

100 / 12 = 8.3 Amps.

We have so far applied a "plus tolerance" to all the previous parameters, so let's show some generosity to the Amp spec of the panel also, and instead of sticking to the 8.3 amps limit, you might be happy raising the level to around 10 Amps? That looks good, right?

Assessing Inverter Specifications

5) Finally we boil down to the inverter specifications, and determine the reasonably exact capacity that would keep the unit compatible with the above discussed results, and keep the load running without issues, whenever required.

Well, calculating the inverter specs doesn't look difficult at this point of the discussion.

Since we already know the maximum load wattage which is 100 Watts, implies that we simply choose an inverter which might be capable of handling a 100 watt comfortably.

That implies, we simply need to get an inverter rated at 100 watts,.... OK, you may be thinking of adding some tolerance to this candidate also, not an issue, instead of 100 watts you can opt for a 125 watt inverter, allowing all the gadgets to happily "shake-hands" and your house powered round the clock forever, free of cost.

You'll also like:

  • 1.  Single Transformer Inverter/Charger Circuit
  • 2.  Generator/Alternator AC Voltage Booster Circuit
  • 3.  Dual A/C Relay Changeover Circuit
  • 4.  Self Regulating Battery Charger Circuit
  • 5.  Op Amp Battery Charger Circuits with Auto Cut Off
  • 6.  Gel Cell Battery Charger Circuit [Constant Current, Constant Voltage]

About Swagatam

I am an electronics engineer with over 15 years of hands-on experience. I am passionate about inventing, designing electronic circuits and PCBs, and helping hobbyists bring their projects to life. That is why I founded homemade-circuits.com, a website where I share innovative circuit ideas and tutorials. Have a circuit related question? Leave a comment.... I guarantee a reply!

Previous Post: « Car Speed Limit Warning Indicator Circuit
Next Post: Automatic Voltage Regulator (AVR) Analyzer »

Reader Interactions

Comments

  1. Richard Jombo says

    December 6, 2024 at 2:00 pm

    dear Swagatam
    in calculating the actual power delivered by a solar panel do we have to consider the efficiency of that panel so as not to undersized the panels required?

    Reply
    • Swagatam says

      December 6, 2024 at 2:22 pm

      Hi Richard,
      Yes, when calculating how much power a solar panel really delivers, we need to consider its efficiency. Efficiency tells us how well the solar panel turns sunlight into electricity. If we ignore this, we might end up with a system that’s too small and can’t provide enough energy to meet our needs.

      Reply
  2. Hendry says

    September 12, 2024 at 3:39 am

    What does c37 & c38 stand for and what it does in the circuit.
    Thank you

    Reply
    • Swagatam says

      September 12, 2024 at 8:07 am

      Which circuit are you referring to?

      Reply
  3. Callistus says

    March 5, 2024 at 10:25 pm

    very insightful. thanks.

    Reply
  4. nouha hanna says

    December 10, 2023 at 12:45 am

    pleas tell me How much the design insulation (ESH)?

    Reply
  5. George says

    August 30, 2023 at 10:20 am

    Your Discussions are very helpfull

    Reply
  6. AYUBA BALA CHONOKO says

    June 28, 2023 at 5:56 am

    I have 900w,72v DC brushless intelligent self-priming pump, how many panels are needed to run it.

    Reply
    • Swagatam says

      June 28, 2023 at 8:47 am

      You will need a 900 watt 72 V solar panel, you can create this by adding many small panels in series and parallel.

      Reply
    • AYUBA BALA CHONOKO says

      August 5, 2023 at 6:43 am

      How many solar panels are needed to run a 850w DC BRUSHLESS INTELLIGENT SELF-PRIMING PUMP ON 72V

      Reply
  7. Swagatam says

    June 21, 2023 at 9:14 am

    Sorry, I do not have it at this moment.

    Reply
  8. Ajah ThankGod Ejima says

    June 3, 2023 at 4:44 pm

    Not 5000 load is 500 load for 12 hours

    Reply
    • Swagatam says

      June 3, 2023 at 5:04 pm

      I have explained the procedures in the above article. Please use the above data to calculate it yourself.

      Reply
  9. Ajah ThankGod Ejima says

    June 3, 2023 at 4:27 pm

    Pls help me to size panel, charge controller, inverter and battery (5000 load, 12 hours night run) God bless you

    Reply
  10. Onodjaje lucky says

    May 28, 2023 at 10:26 am

    What is the fault of my inverter displaying zero input and output voltage

    Reply
  11. Engr. Abdulhafeezh says

    April 17, 2023 at 5:20 pm

    I really appreciate the presentation on this site. Very beneficial, precise and informative. Thank you.

    Reply
    • Swagatam says

      April 18, 2023 at 9:05 am

      Thank you Engr. Abdulhafeezh

      Reply
  12. Alao kolawole says

    April 10, 2023 at 8:32 pm

    After going through the tutorial above, the question i want to ask is how do I calculate or determine the amount of voltage and Ampere to charge 2 units of 200ams battery and 4 units of 300watts solar panel

    Reply
    • Swagatam says

      April 11, 2023 at 8:51 am

      For a 200 Ah battery, you will require minimum 20 amp current.

      Reply
  13. Idowu Oshoja Ojulari says

    March 25, 2023 at 7:51 pm

    I have a total load of 600w to run for 6 hours, what is my calculations to know the batteries, inverter, panels and charge control I should have

    Reply
  14. Fatoba Kolawole says

    February 11, 2023 at 4:34 am

    Thanks for the good works. Plz can you help on printed circuit?

    Reply
    • Swagatam says

      February 11, 2023 at 8:02 am

      Sorry, I can’t supply PCBs.

      Reply
  15. Ama says

    December 24, 2022 at 7:14 pm

    I have a 4kva inverter with 4 batteries if i am charging it with 8 unit of 300watts solar panels how fast can the sun charge the batteries while supplying light after the sun has gone down

    Reply
    • Swagatam says

      December 24, 2022 at 7:59 pm

      Please provide battery voltage and Ah specifications, and how are they connected, in series or parallel?

      Reply
  16. Alhassan says

    September 2, 2022 at 9:46 pm

    Thanks

    Reply
  17. Benard says

    June 8, 2022 at 12:55 am

    Please, what can i alter to change to the desired solar charge controller(referring to solar charge controller circuit)

    Reply
    • Swagatam says

      June 8, 2022 at 9:12 am

      You will have to alter the solar panel and the battery to match your solar controller

      Reply
  18. Mussie says

    May 27, 2022 at 3:53 pm

    thank you

    Reply
  19. Jezreel says

    February 21, 2022 at 4:05 pm

    Pls what is the best way to connect panels, is it series or parallel when using a 4x 220amps batteries and a 60amps charge controller.
    Mind u my panels are in 200watts.

    Reply
    • Swagatam says

      February 22, 2022 at 8:59 am

      It will depend on the battery voltage and current.

      Reply
  20. olufemi says

    December 10, 2021 at 4:59 am

    Hello our able instructor,I ‘ll need your attention on transformer less inverter circuit with a clearer analysis sir, since I have little knowledge about the construction remain bless sir and more grease to the elbow

    Reply
    • Swagatam says

      December 10, 2021 at 1:02 pm

      Hello Olufemi, for transformerless inverters you can refer to the following post:

      3 Best Transformerless Inverter Circuits

      Reply
  21. Godfrey says

    December 5, 2021 at 2:38 pm

    What is the recommended setting on the solar charge ontroller

    Reply
  22. Godfrey says

    December 5, 2021 at 2:37 pm

    Morning sir I have two 200watts solar panels and 2000watts inverter and 200ah battery but still can’t have power for 5hrs

    Reply
    • Swagatam says

      December 5, 2021 at 8:26 pm

      Hello Godfrey, a 200 Ah battery will require a charging current of at least 30 amps for first few hours which must be reduced to 20 amps after sometime….A 200 watt panel will not be able to supply such high current, and therefore the battery will remain under charged.

      Reply
  23. OLUFUNSHO ODUNEYE says

    September 27, 2021 at 11:29 pm

    Thank you God will bless your wisdom
    Total Home load is 3600W expected to run for 20H daily let us say 30-40%
    I have 12pcs 350w 36v solar panels
    I also have 4.5kva inverter
    I also want to have 6-8pcs 12v 220AH batteries
    I want to know the size of charge controller to use since I have 36v from Panels and 12v for batteries and inverter.

    Reply
    • Swagatam says

      September 28, 2021 at 10:51 am

      For charging 12V 220 Ah batteries, you can use a 12V/30 ampere charger with auto cut off, and install them individually on each battery.

      Reply
  24. OLUFUNSHO ODUNEYE says

    September 27, 2021 at 4:31 pm

    Thank you for the knowledge you are giving.
    I want to get something out.
    I have
    3 TVs 105W=315W( 12hrs)
    1 Washing Machine =450w(3hrs)
    5 Fans 50W =250w
    3 Laptop 80W= 240w(18 hrs)
    20LED light 30W= 600w (20hrs)
    Cooker = 400w (3hr)
    Deep freezer= 300w
    2 A.C 1.5hp(1125 W) =2250w(24/7) (12 hrs)
    something yet to be added= 95w
    The total wattage is 5000w.
    Can you please do the breakdown to the barest minimum for me.
    1.Would like to know amount of watt estimated per day
    2.best inverter voltage to be used and best and Ah calculate
    3.Solar panel calculated
    4. How many kva is best and volt system and number of batteries
    5.solar charge controller calculation

    Reply
    • Swagatam says

      September 27, 2021 at 7:27 pm

      Thank you for your question, however I have already explained the entire process in the above article for quick calculations…

      Reply
  25. Zaiham says

    September 13, 2021 at 12:45 pm

    You have calculate the solar panel watt peak rating by depending on load list. You did not considered the amount of power required to charge the battery. Wil that design able to fully charge the battery while it supply the power to inverter ?

    Reply
    • Swagatam says

      September 13, 2021 at 1:55 pm

      I have shown how to calculate the Ah value of the battery and the optimal current required for charging the battery in 5 hours.

      Reply
  26. Daudi Mfinanga TZ says

    July 26, 2021 at 10:54 pm

    Dear sir,
    can you help me that problem
    In pv system the distance betweeb the solar PV module is 10metres. The system voltage is choosen to be 12VDC. the PV module and battery are connected by copper cable 2.5mm² cross section area. estimate voltage drop in the cable if it is carrying 3.5A current. What would happen if the cable of 1.5mm² cross section area as used (Assume density of cable is 1.67×10^-8)

    Reply
    • Swagatam says

      July 27, 2021 at 9:16 am

      Hello Daudi, the calculations can be time consuming, you can try the following software instead:

      https://www.homemade-circuits.com/56492-2/

      Reply
  27. Peter says

    July 19, 2021 at 7:32 pm

    Hello sir,having a solar rating 250w what is the size of charger controller needed and the number of batteries plus their rating

    Reply
    • Swagatam says

      July 20, 2021 at 1:14 pm

      Hello Peter, please provide the voltage and current specs of the solar panel?

      Reply
  28. Jebb says

    July 7, 2021 at 10:32 am

    Why did you base your SCC calculation on a 100-watt panel? You have computed it as 200 watts, right? i.e. 1,000 Watt-hours / 5 hours sunlight = 200 Watt solar panel.

    Reply
    • Swagatam says

      July 7, 2021 at 12:08 pm

      The actual requirement is 100 watt but only if sunlight is available for 10 hours, but since 10 hours is not feasible, we have considered 5 hours, which calls for a 200 watt panel. This will charge the battery optimally in 5 to 10 hours.

      Reply
  29. John Lee says

    June 8, 2021 at 10:34 am

    Hi Mr. Swagatam,
    I reside in Western Australia where we get the best sun throughout the year.
    I am interested to build up a tilted solar power panel that could keep pointing to the sun ray at 90 degree.
    I would be able to construct the tilted revolving base for the panel, but need your expertise advise as follow:
    1. Could you provide the complete set of the MPPT Solar Charge Controller and the inverter? If not, then please advise which is the most reliable brand to purchase in Australia. Thanks.
    2. How many panels (as minimum as possible) with the highest power rating do I need for the following loads:
    (a) 1 x 1.5 Air-conditioner operating mostly from 10 am to 6 pm, summer and winter days
    My backyard is huge, with 500 c.m. free space for installing any rotating panel assembly.
    (b) 1 x 2000 watts storage water heating tank of 50 gallons capacity
    For all other loads, I don’t mind to get regular supplies from the power grid.
    3. Please also advise the most suitable panel size for maximum efficiency.
    Kindly advise all prices and delivery lead-time, if you could provide.
    Thanks for help.
    John Lee

    Reply
    • Swagatam says

      June 8, 2021 at 12:30 pm

      Hi John,
      I do not have a full fledged working design of an MPPT in my blog, so I may not be able to help you with that. I think if you Google a bit regarding MPPTs you may be able to find many good options online. I personally do not have much experience with the MPPT brands available in the market.

      As far as the solar panel is concerned, the following calculations can provide an approximate idea regarding the panel wattage.

      1500 + 2000 = 3500 watts x 8hours = 28000 watt hour
      assuming peak sunlight is available for 5 hours, we get
      28000/5 = 5600 watt solar panels.

      Reply
  30. Devin says

    May 20, 2021 at 10:52 pm

    Hello,

    I have a 5.43 KW Solar system installed. The solar output is through an inverter and then to a breaker box to a 40amp Breaker. My question is, I would like to add another inverter and more panels with a separate system but to the same Breaker box. Can I install two 20 amp breakers to replace the 40amp breaker. There is no more room on this breaker box to add a separate breaker box. How do I determine if a 20 amp breaker will be enough for each system? First system 5.4 KW, Second system is 3KW

    Thank you!

    Reply
    • Swagatam says

      May 21, 2021 at 11:57 am

      Hello, you can divide the 5.43 KW with the voltage of the panel to get the required maximum amp rating for your breakers. If your existing breaker is rated at 40 amps then adding more panels and inverters would demand even higher rated breakers than your 40 amp breaker.

      Reply
  31. Adeoye Blessing says

    May 2, 2021 at 12:10 am

    This I all I need for my basics in solar power installation/estimation

    Really helpful, God bless the writer

    Reply
    • Swagatam says

      May 2, 2021 at 8:06 am

      Thank you, glad you found the post helpful…

      Reply
  32. Abhisek Behera says

    March 5, 2021 at 12:00 pm

    Sir,

    Thank you very much for being so generous. God will bless you more with deep knowledge.

    I want to know sir, For a 5KW System,6KVA PCU and load is 4KW, How many 2V ,C10 batteries required and what will be its Ah ????

    Awaiting Your Valuable Response Sir…

    Reply
    • Swagatam says

      March 6, 2021 at 8:59 am

      Abhishek,

      you will require 3 such batteries which may give aback up of more 1.5 hours for a 4kva load

      Reply
  33. Marlon Joseph Laurel says

    March 3, 2021 at 5:54 pm

    Hi Sir Swagatam;

    Thank you for sharing your knowledge with us. However, I really acknowledge that I am short in understanding your illustration because I have no formal education in Electronics. I and my wife plan to DIY install Solar Power as an alternative source of energy on our home. Luckily I found your article online which we really need on what and how can we implement our plan. Can we request your help to compute for us what size of Solar Panel, Battery, Charge controller and Inverter we need for our project based on the following load/s we currently have?

    1 Fridge – 95W – 24/7/365 continuous running
    5 Wall fans (50W each) 250W – 2 runs for 10-12 hrs/day
    4 laptops (65W each) 260W – 3 runs for 12 hrs/day
    2 LED Lights (36W each) 72W – runs for 3 hrs/day
    1 Rice Cooker 450W – 3 hrs/day
    1 Water Heater 600W – 20 mins/day
    1 flourescent lamp 20W – 1 hr/day
    1 Water pump 450W – 30 mins/day
    1 Washing Machine 400W – 1 hr/week

    Approximately/Roughly we have 2,700 watts load but not all runs continuously.

    We express our gratitude as early as this time for your generosity.

    Marlon Joseph Laurel
    Philippines

    Reply
    • Swagatam says

      March 3, 2021 at 8:41 pm

      You are welcome Marlon, I will try to calculate it for you!

      It seems we can assume on an average 30% of 2700 watts would be always running 24×7, then this would call for a 810 x 24 = 19440 watts
      Since the wattage is high I will advise using a 24 V or 48 V inverter with battery. So considering 5 hours of peak sunshine on a average the solar panel will need to be 19440 / 5 hours = 3888 watts, and this should be rated at 36 V for charging a 24 V battery. The current will depend on the type of battery selected.
      Assuming a 24 V system, the battery will need to be 19440 / 24 = 810 Ah @ 24 V
      Inverter can be a 1kva or 1.5 kva at the most.
      Charge controller will depend on the battery type.

      Please let me know what will be the battery like, Li-Ion or lead acid

      Reply
      • Marlon says

        March 4, 2021 at 11:47 am

        Sir Swagatam,

        Thank you very much for being so generous. God will bless you more with deep knowledge.
        The most common battery here in our Province in the Philippines is Lead Acid battery and that’s is what I am planning to buy unless I can buy Li-Ion battery online or somewhere in Manila.

        Will it be okay if I buy 2 x 2000W Solar panel and be connected in series to meet the 3880 watts rated 36 V to charge the 24V battery?

        By the way sir, how many batteries will it be for 19440/24=810Ah @24V? will it be 1, 2, 3, 4 or 6 batteries in parallel connection?

        1KVA or 1.5KVA inverter means 1000W or 1500W?

        Sorry for these additional queries sir because I am not knowledgeable in electronics. I just wanted to ease the heavy monthly bill we have here in the Philippines.

        Marlon

        Reply
        • Swagatam says

          March 4, 2021 at 5:44 pm

          No problem Marlon,

          The panels must be able to provide 4000 / 60 V = 66 amps for charging the 810 Ah battery, which must be actually 1000 Ah, to ensure some additional margin. This means the solar panels must be rated at a net value of 60 V, 60 to 70 amps, which can be configured as per convenience.

          For a lead acid battery, the charge controller must be a 3-step charge controller, with SMPS buck converter 60 V to 30 V with automatic cut-off

          You can configure of 24 V 1000 Ah by any possible means, either by using 24 V batts in parallel, or by using 12 V batts in series/parallel connections.

          Please note that the above calculations are only assumed approximately, therefore could be some errors in this, but we can always upgrade it if it is required.

          Yes the 1kva = 1000 watts approximately and so on.

          If the estimated figures are higher than the present requirements, then it can be an added reserve facility that could be utilized some time in future for operating additional electrical appliances.

          Reply
          • Marlon says

            March 4, 2021 at 6:58 pm

            Sir Swagatam,

            Thank you so much for your guidance. I will be very happy to inform you once our project is done. Should you wish to visit my Country, the Philippines, in the near future I will be very glad to assist you or be our guest in our humble home. Just a humble gesture of reciprocity for your generosity.

            By the way sir, I have 2 motors that i have been keeping for a while with the intent of using them for DIY project. 1 is an induction motor, 135W, from our old washing machine and the other 1 is a DC motor which can produce electricity of up to 230 V, 10A.

            I am planning to use my induction motor to drive my DC motor, using pulley and pump belt so it can produce electricity, as reserve power.

            This is my planned schematic:

            12V battery > Inverter > Induction motor > DC motor

            then…

            DC motor > battery charger/charge controller > 12V Batteries(including the battery that runs the induction motor) > 12V to 1000W Inverter (?) > Load/s

            Would such schematic be possible, sir?

            Thanks again!

            Marlon

            Reply
            • Swagatam says

              March 5, 2021 at 10:42 am

              Hello Marlon, your idea of using the motor output back to the batteries so that the system can work in a perpetual will not work, due to the huge losses that would happen during the conversion of the power from one form to the other…

              Reply
  34. Wi says

    February 23, 2021 at 8:14 am

    Solar charge controller calculated should be 200W /12v, isn’ it?

    Reply
  35. Ernest Sunday says

    November 18, 2020 at 1:49 am

    Very insightful.

    Reply
  36. Richard Shoffit says

    October 9, 2020 at 5:15 am

    Hello Sir. I have a 20 amp MPPT charge controller. Battery is about 9’ from controller, what size wire is needed.
    Thank you
    Rick

    Reply
    • Swagatam says

      October 9, 2020 at 10:09 am

      Hello Richard, you can try the following software to calculate the wire thickness:

      https://www.homemade-circuits.com/56492-2/

      Reply
  37. Patrick says

    July 14, 2020 at 4:42 pm

    Dear sir
    I have been visiting your tech. site regularly.I am not here to ask question but to say thank you so much for sharing these invaluable lessons free of charge.Many Technicians out there would not do it.How i wish you form a marketing outlet for sourcing electronics components, equipments and books.If that is your related field,and for those us with some electronics knowledge,it will be highly welcomed if you delve into programming.I mean ic programming lessons.
    Once again i say thank you so much.

    Reply
    • Swagatam says

      July 14, 2020 at 6:25 pm

      Thank you Dear Patrick, I appreciate your thoughts. I too want to upgrade my knowledge and innovate my website with new features but due to lack of time I am unable to proceed with any of these ventures, although I am always trying my best.

      Reply
  38. Karan says

    June 23, 2020 at 6:51 pm

    Hello Swagatam,
    I am working on a solar car project and need some guidance regarding the number of solar panels required and their specifications.I want to run a 5-6kW BLDC motor directly through the solar panels,i am not sure about the approach so it will be of great help if you can throw some light on it.

    Reply
    • Swagatam says

      June 24, 2020 at 10:50 am

      Hi Karan, If you implement the steps mentioned in the above article you will be able to get the answers to your questions correctly. Along with load specifications, there are a few other parameters which you will need to include in the calculations. Please try it and let me know if you have any problems.

      Reply
  39. yusuf makalo says

    May 29, 2020 at 1:43 am

    Hello sir.hop u fine.i have a 50ah solar battery.my panel is 120w.my load at night is only 50w TV,roughly 70w.problem is when I power on my inverter with TV on the battery drains from 13.4v to 12.3v in that moment.then inverter goes off after only 2hrs not even 4-5hrs I expected.please help sir,am using a computer ups as inverter….

    Reply
    • Swagatam says

      May 29, 2020 at 10:33 am

      Yusuf, to get 5 hour back up for 70 watt load, your battery must be rated at 50 Ah. If your battery is 60 Ah, then check the current consumption by connecting an ammeter in series with the battery positive, it should be around 6 amps at 70 watts, if it is higher then either your inverter is malfunctioning or your load is above 70 watts. If it is 6 amps then your battery has gone bad.

      Reply
  40. Jibril says

    May 23, 2020 at 2:24 pm

    Thanks so much. This article looks much educative

    Reply
    • Swagatam says

      May 23, 2020 at 4:44 pm

      Thank you, Glad it helped you!

      Reply
  41. Adekunle says

    February 15, 2020 at 2:32 pm

    Good morning, please I have 96 batteries of 12v 150ah With inverter of 48v. Please how many watts of solar panel will be required? To charge it effectively?

    Reply
    • Swagatam says

      February 16, 2020 at 9:11 am

      Hi Adekunle, the solar panel specs will depend on how the batteries are configured, and the number of batteries connected in series and parallel. If you specify this then I can give you a rough idea regarding the solar panel capacity.

      Reply
    • Francis says

      July 23, 2020 at 10:24 pm

      What is the energy demand or load

      Reply
  42. Glen Perry says

    February 4, 2020 at 6:17 am

    Hello Swagatam, I’m trying to figure out roughly what I’ll need in battery size and solar panel size. I’ll be powering music amplifiers and laptop, with a total draw of about 8 amps AC, using a 1500W inverter connected to a 12V battery. I’ll need a minimum of 5 hours run time, with the solar panels charging the battery as I go.
    So my question is, will a 100Ah 12 volt SLA battery be enough, and if so how much solar panel wattage will I need to keep the battery going for 5 hours under my load? I’ll be using the amplifiers at a volume you’d expect in a very small venue.
    Thank you!!

    Reply
    • Swagatam says

      February 4, 2020 at 10:19 am

      Hello Glen, I think the calculations given in the article quite matches your requirement. So a 200 watt panel is what you may need for your application.

      A 100 Ah battery should work fine.

      Reply
  43. John Payne says

    January 15, 2020 at 4:35 pm

    Hello , I would like an estimate of how many panels and battery’s i might need for an all electric 40 square meter house . The hot water heater is only 20 liters , the lights are LED , the stove top is induction and the oven is like a normal oven .The frig is a single door. The water pump is demand pump and a computer AIO. There are other appliances such as kettle for water , rice maker , toaster , oven and microwave . all which could be removed or not. Cheers, John

    Reply
  44. Siva DS says

    January 13, 2020 at 7:39 am

    Hello Mr Swagatam

    I need to install 100 watts street light with solar panel.
    Can you advise me which type of battery I should use and is it 100Ah 12V enough?

    Siva

    Reply
    • Swagatam says

      January 13, 2020 at 10:09 am

      Siva, if the light is also 12 V then 100 Ah will be enough, provided the panel gets vertical sunshine at least for 8 hours.

      Reply
  45. Ma'aruf Aminu says

    January 11, 2020 at 9:33 pm

    God day sir, I really appropriate this article, and I benefited from it, my question is if the system voltage is 24v how the calculation will be for total wattage of 2000w.thanks sir, I am expecting the answer via my email

    Reply
  46. guy says

    November 30, 2019 at 1:01 pm

    Hi swagatam,
    let’s say that i need a 25W solar panel to power a camera with load of 5W, to 24 hours a day (average sunlight in my country is 5 hours a day).
    [(5W camera * 24 hours) / 5 hours of sunshine] = 24W ~ 25W solar panel needed.

    now let’s say im using a 12V battery. so, [(25W*24 hr) / 12 V] = 48 AH ~ 50 AH battery.

    how to calculate the charge controller ? (25W solar panel / 12 Volts battry) =~2 Amps?
    im waiting for your reply, thank you
    guy

    Reply
    • Swagatam says

      December 1, 2019 at 1:02 pm

      Hi Guy, in real life batteries are hugely less efficient compared to theoretical calculations. So 50 Ah will not work, it has to be around 65 Ah, and dividing 65 Ah with 12V gives 5.41 amps. Again at this rate the battery would require to 12 hours to get fully charged. So solar panel must be rated at 10 amps, so that at peak sunlight it gives 10 amps and gradually becomes lower until it drops at 2 amps by evening. So the solar panel practically should be 12 x 10 = 120 watts. Or you can use a 12 x 5 = 60 watt panel if you can keep its direction continuously angled towards the sun.

      Reply
  47. Peter French says

    November 6, 2019 at 5:47 pm

    Hi Swagatam
    I have a problem that I need help with. I will briefly describe my system, so that you have an understanding of the problem.
    I am running 4 x 100w solar panels, series parallel connected. Thus supplying 200w x 24v to my controller.
    I have a 40a MPPT controller connected to 2 x 105ah 12v deep cycle batteries in parallel. This then feeds a 200w inverter. I built this circuit to run my 10a 110vac well pump when the mains power fails.
    I built a control box circuit to control switching automatically from mains to inverter when the power fails.
    I am using a 110v DPDT relay for the main switching. My problem is that in order to use this circuit I have to have the coil of the relay energised continuously, this leads to probable overheating of the coil and thus failure. Can you suggest a simple circuit that I can use which will switch power to the pump from the mains, to the inverter without the need for constant energising of my relay coils.
    I would really like to do this without the relay if possible but at the moment cannot see how this can be achieved. Thanks. Pete

    Reply
    • Swagatam says

      November 6, 2019 at 9:19 pm

      Hi Peter, what is the coil voltage of the relay, is it 110V DC? The relay coil will get damaged only when the input voltage is considerably higher than its specified rating. In your case what is the coil supply voltage that you are using to energize the relay, is it much higher than 110V?

      Please clarify this, I’ll try to figure out the solution. I would recommend using a relay only since they are more reliable and easy to wire, compared to other options like a triac or SCR

      Reply
  48. Paul says

    October 5, 2019 at 4:12 pm

    Hi Swagatam

    need some help with solar panel setup I have an air con and a fridge,that i want to run of solar.
    air con will be running 24/7, air con spec 1200 btu current 5.3 amps rated power input 1550 watts rated current 7.5 amps voltage 220v 50 hz solar panel 250 w open circuit voltage37.25 volts. max system voltage 1000v max power voltage 29.8 . this will be off grid setup using batteries I live in Barbados Thanks Paul

    Reply
    • Swagatam says

      October 5, 2019 at 5:04 pm

      Hi Paul,
      as you can see I have explained everything in minute details in the article, so can you please try calculating the required results, if you have problems I will help you out.

      Reply
  49. Abubakar Alee says

    September 14, 2019 at 6:15 pm

    Thank you once again!
    I prefer the complex one,i can construct it anyway.
    Best regard!

    Reply
    • Swagatam says

      September 14, 2019 at 8:41 pm

      OK, then you can try this concept:

      https://www.homemade-circuits.com/5v-pwm-solar-battery-charger-circuit/

      For this you will need a 24V panel, at 7 amps, this will be converted to 14V 10amps for your battery

      Reply
  50. Abubakar Alee says

    September 13, 2019 at 12:57 pm

    Hello sir swagatam.
    Pls refer me to the home made controller circuit.moreover am i right inthe calculation.it ‘s blessing to here everything from you.
    I can’t thank you enough!

    Reply
    • Swagatam says

      September 14, 2019 at 5:45 pm

      Thanks Abubakar, yes your calculations look right to me. controllers are of many types, from most complex to most easy ones, the easy ones will also charge your battery effectively although slightly less efficiently than the complex ones, which type do you prefer?

      Reply
  51. Abubakar Alee says

    September 13, 2019 at 2:09 am

    Good day sir.
    It’s Abubakar again.
    Sir, i do the load analysis nd i found the ff values.i would like to use
    20watt dc fan*2
    5watt dc bulb*3 All were in DC.
    From 9am to 9pm daily,my T load is 55w and total wh is 660wh.
    # i choose panel 660/12=55w
    Truepower is 660/5=132w.I chose150watt panel.
    #EMF Ah is 660/12=55Ah i upgrade it 65Ah.
    #charge contrller 132/12=11A
    The issue is that i went to the sellers thy told me that i can only get 20A c contrller and above,he then suggest i can use It in panel range for 20A to 1A,which is fairly nor agree with him.could you PLS help me out?
    Dhanyavaad!

    Reply
    • Swagatam says

      September 13, 2019 at 12:13 pm

      Hi Abubakar, 20A is the maximum limit of the controller. A 20A controller will restrict the current to 20A and will have the maximum range of 20A for the load, so it can be used with a 11A solar panel also, no problem at all. You can also built one at home if you need to.

      Reply
  52. Abubakar Alee says

    September 7, 2019 at 3:26 pm

    Hi
    Thank you for helping me out,truely fine person.would you let me know the advantage of using DC system alone or AC system?

    Reply
    • Swagatam says

      September 7, 2019 at 7:38 pm

      Hi, thanks, can you please elaborate your question, because solar inverter works only with DC, not AC

      Reply
  53. uden says

    August 18, 2019 at 10:27 pm

    Hi,
    I have the 3.5W Led Bulb 24 nos ( working to AC power), operating hour per day 12 H and need to (2day run backup) what is the Solar panel, Battery, Charger controller, and Inventor capacity?

    tks

    Reply
  54. Choubey says

    June 24, 2019 at 10:39 pm

    Hi,

    I have 180 Ah battery with 12v and inverter. I want to install solar pannel. How much watt is required ?

    Reply
    • Swagatam says

      June 25, 2019 at 6:38 am

      Hi, you can use a 20V 20 amp solar panel.

      Reply
  55. Santhosh Olympuss says

    April 3, 2019 at 9:01 am

    Looking for 2KW OFF THE GRID system for a house in Eco Village. i have chosen a 2.5 k inverter, what can be the panel and battery specs?

    2K panels are needed? of 1- 1.5 k is enough?
    how many 150 AH batteries? 2 or 3

    Looking for a guidance

    Reply
    • Swagatam says

      April 3, 2019 at 10:50 am

      Hello, kindly go through the step by step explanations above and calculate the required parameters. If you have any difficulty in the process let me know I’ll help you out

      Reply
  56. srinivas says

    March 26, 2019 at 2:11 pm

    Sir ,I have a hybrid solar pcu, grid input is 130-270VAC, PV input is 45VDC,PV Charger is 1KW mppt,Inverter 1KVA,Battery 24V, AC output 230V. Suggest the rating of panels and quantity of panels required .All should be in series or parallel .

    Reply
    • Swagatam says

      March 26, 2019 at 2:27 pm

      Srinivas, what is the intended maximum load and for many hours per day.

      Reply
  57. AJITH KUMAR says

    March 24, 2019 at 8:29 pm

    Hay, swagatham, I am Ajith, and I need your help to get a 12v 50amp Solarcharge control circuit diagram for my home unit., Thanks.

    Reply
    • Swagatam says

      March 24, 2019 at 9:23 pm

      Hi Ajith,

      please provide the solar panel specifications, in terms of open circuit voltage and short circuit current, I will try to help!

      Reply
  58. Paaker says

    August 2, 2018 at 2:12 pm

    I have ask the same question from many, but they all give me very lengthy lectures.and confuse me as much they can.even most of the Solar reseller don’t know how to simply explain this.

    This is one of the clear and simply detailed explanation on internet, about calculating solar/battery and inverter.

    Swag, you are great.
    Thank you very much for your valuable time to spend here to teach others.

    Reply
    • Swagatam says

      August 2, 2018 at 4:02 pm

      Thank you Paaker, I am so glad you liked this post. Please keep up the good work!

      Reply
    • Andrew says

      May 30, 2019 at 9:29 am

      What a lovely and educated example, Sir your explaination is truly the best solution to make all the calculations needed from A to Z and am very honoured to come across your site, thanks 4 ur motivation to share all your ideas with D world and i pray that God will feed u with more???? knowledge so we can lean more from u ????????????

      Reply
      • Swagatam says

        May 30, 2019 at 10:27 am

        Glad you liked it Andrew, I hope it helps you to accomplish the required objectives. All the best to you!

        Reply
  59. David Ifeagbason says

    October 13, 2017 at 3:38 pm

    Good day sir…Thanks for your post. I want to achieve a 60kva solar power and i have a 310watts panel..Am looking at using 24 solar panels and i have a 20kva inverter how many battries do i need to achieve this

    Reply
    • Swagatam says

      October 14, 2017 at 2:57 am

      Hi David, you can calculate the parameters with the help of the explanation presented in the above article, you can also refer to the examples which I have discussed in the comment section.

      Reply
  60. Gurvinder says

    September 28, 2017 at 12:32 am

    Good day
    I would like your help in the following scenario. I have been to many websites and each shows a different outcome and formula. I really appreciate your guidance
    Total WH: 20000WHR per day (12 hours during night) 18kVa load
    Panel : 310W x 80
    Can you advise size of inverter and battery (off grid only)

    Reply
    • Swagatam says

      September 28, 2017 at 4:32 am

      Hi, your panel output is 310 x 80 = 24,800 watts, multiplying this with minimum 6 hours sunshine gives 148,800 watt hour.

      to operate a 18kva load you will require a 180kwh battery.

      to charge a 180kwh battery, you will need at least 200kva power for minimum 6 hours.

      your solar panel is 148.8kwh, which seems to be a little short for the battery.

      you must upgrade to to at least 200kwh panel

      inverter power handling capacity must be 20kva

      Reply
  61. ola korede says

    September 23, 2017 at 7:27 am

    hello sir am having a 3000va inverter and four 200AH/12v batteries connected serially but in term of usage consumption stays on just two when the remaining two remains full even after the former is low. what can I do to make the remaining two full battery work simultaneously or switch over former is low

    Reply
    • Swagatam says

      September 23, 2017 at 8:38 am

      OLa, that can be difficult to solve if the batts are in series….because the batts which are getting discharged faster could be the defective ones and while getting discharged these may be causing a high resistance for the good batteries and preventing their current from reaching the inverter…you can try shuffling the positions of the batts withing the series or simply change the defective ones with new.

      Reply
    • ola korede says

      September 24, 2017 at 8:27 am

      pls do you think the wiring can be responsible for the battery not working properly

      Reply
      • Swagatam says

        September 24, 2017 at 12:14 pm

        not the wiring, most probabaly it could be due to defective batts.

        Reply
  62. OM KUWAR says

    May 27, 2017 at 3:07 pm

    frds…without controller dangerous for battery .if full charge battery …batterys supply retun to solar panel …and anothr things you can use the formula i = p÷v …55w÷12

    Reply
  63. Swagatam says

    May 23, 2017 at 11:22 am

    Hello, have you confirmed whether your battery is getting fully charged or not?, and whether your battery is working good or not?

    you will need a 1kW solar panel for running a 850 watt load

    Reply
  64. Unknown says

    May 9, 2017 at 7:57 am

    I have 900 watts inverter what rating battry and solar panel should use

    Reply
    • Swagatam says

      May 10, 2017 at 1:51 am

      what is your inverter's battery specification?

      Reply
  65. SinnSabs says

    April 28, 2017 at 10:31 am

    Hello Sir.
    One Question only I want to clarify is the matching of Solar Voltage module to the Charge controller module.
    Is 12 volts Charge controller can handle a 18 Volts solar panel?
    or If we buy 12 volts charge controller, I will also buy a 12 volts Solar panel?

    Reply
    • Swagatam says

      April 28, 2017 at 12:45 pm

      Hello Sinn,

      You will have to check the specification details of the controller, which will tell you the maximum input it may be designed to handle.

      However in most cases a controller for a 12V battery would be rated to handle 18V easily.

      No, a 12V controller will definitely not correctly work with a 12V input and will require require a minimum of 15V as the input.

      as stated earlier an 18V input in most cases would be quite normal and recommended

      Reply
  66. Laptop Arcade Anura says

    January 26, 2017 at 4:10 pm

    Hello sir I try build a solar system for my home.to run 5hours on battery backup.3X45w led tv's,20X12w led bulbs
    1X95w refrigerator at night only. I have this item for solar system (1X200W mono panel,1X max solar input >50 12~24v 20Amp charging control unit,1X 2000W inverter,which type battery I need for 5 hours battery backup.and how many hours get it battery full charge.please help sorry for my bad English.

    Reply
    • Swagatam says

      January 27, 2017 at 9:20 am

      Please provide the total wattage of the solar panel, and the total wattage of the load, only then I would be able to suggest you the approximate results

      Reply
    • Laptop Arcade Anura says

      January 31, 2017 at 4:28 pm

      2 solar Panel 100W 17W 5.68A
      max load 100W per hour.need 5 hour's battery backup for night time only.

      Reply
      • Max says

        December 18, 2017 at 12:23 am

        Hello Sir
        Total Home load is 3600W expected to run for 10H daily
        I have 12pcs 300w 36v solar panels
        I also have 5000w inverter
        I also have 6pcs 24v 250AH batteries
        I needed to know the size of charge controller to use since I have 36v from Panels and 24v for batteries and inverter

        Reply
        • Swagatam says

          December 18, 2017 at 8:06 am

          5kva inverter for for a 3.6kva load is OK.

          Now 3600 x 10 = 36000 gives us the total power requirement for the load.

          you have 12 x 300 = 3600 watt solar panel output, but since the average sunshine can be expected to be around 6 hours a day, the power output is not sufficient for 36000 watt power requirement.

          your solar panel would provide just 3600 x 6 = 21600 watts of average power, whereas the requirement is 36000 watts.

          for a 3.6kva load the inverter operating at 24V would require 3600/24 = 150 amps.

          your battery Ah rating is 250 x 6 = 1500 Ah, so it can be comfortably discharged at 150amp rate, that’s OK, so the battery specs is fine.

          your charger should be able to charge your battery at the rate 150 amp for at least 10 hours, which implies that your charger controller must be rated to output 28V at 150 amps….however again since the sunshine could be just for 6 hours, this will fall short. To compensate this you will have to upgrade the solar panel appropriately, or you can can use a solar tracker that will enable the solar panels to absorb sunshine for 10 hours optimally, and your existing devices can be used without any modifications or upgrades.

          Reply
    • Swagatam says

      February 1, 2017 at 2:49 am

      for a 100 watt load to run for 5 hours you will need a minimum 500 watt hour battery, if it's a 12V batt then it would need to be 500/12 = 41 or 40 AH rated.

      you can use your 100watt panel to charge the battery withing 8 hours,,,preferably using an MPPT charger circuit.

      Reply
  67. Swagatam says

    October 8, 2016 at 11:28 am

    If the panel voltage is within 60V then it would be fine, however if the inverter load is too high then the batteries might not charge properly….in other words the inverter load and the battery charging consumption must be less than 250 watt combined

    Reply
  68. JITENDRA PATEL says

    August 20, 2016 at 2:44 am

    Sir , second question .your answer to Ms. Achilles Hector should be direct I.e. Battery V = 24 , Amp Hr = 44+@ 24 v , Inverter w = 216+ w , but you replied her to follow calculation as per yr blog.I know you can't calculate for everybody but how can we cross check whether our calculation is right until and unless you or any other reader give her the answer.I request you and atleast one reader to confirm my answer.

    Reply
  69. JITENDRA PATEL says

    August 20, 2016 at 2:34 am

    Sir , I read all posts today.in your blog for calculation , in point #2 , you calculate 1000 wh/ 5 hr sunlight= 200 w but in point #4 , you wrote , 100 w panel /12 v = 8.33 Amp charge controller.why you took 100 w instead of 200 w ???

    Reply
    • Swagatam says

      August 20, 2016 at 8:45 am

      Jitendra, 200 watt is for countries with weaker average sunlight, and 100 watt is for countries for stronger average sunlight…

      the example is given for a 100watt panel, anybody can easily convert the results for 200watt also….

      there's nothing too difficult or confusing about the calculations.

      Reply
  70. owor paskr says

    August 10, 2016 at 11:12 pm

    Hello mr Swagatam.

    I have 8 solar panels of 200watts each. I would like to ask which inverter size is the most suitable for these panels when wired all together.
    Can I use the inverter which come with inbuilt charge controller?
    Which battery sizes and how many pieces do I need to make the wiring.
    Which wiring method would give me the most efficient power outputs.
    Can I use the solar power output out of these 8 panels to run a Panasonic home theater of 13200watts?

    Thanks in advance

    PASCAL

    Reply
    • Swagatam says

      August 11, 2016 at 9:38 am

      Hello Pascal,

      the most suitable inverter that could be used with the mentioned 200 x 8 = 1600 watt panel is around a 1300 watt inverter, 13200watt is out of question, since it's way out of the range of the panel.

      connecting the panels in parallel would be a more convenient option….

      the battery voltage will need to be matched with the panel output if no MPPT is used in the middle, and therefore will need to be wired accordingly.

      Reply
  71. Andy Fisher says

    July 27, 2016 at 4:17 pm

    I have a solar company getting ready to do my solar. I will have 28 lg 315 watt panels. They are giving me a 7600 watt inverter. I asked why my inverter is less wattage than my panels. He said you divide the wattage of the panels by the inverter and get 1.17. He said as long as it's. Between .75 and 1.35. Is this right??

    Reply
    • Swagatam says

      July 28, 2016 at 2:44 am

      The technician is probably correct. the inverter wattage should be much less than the panel wattage otherwise the solar panel could be forced to run at an inefficient zone causing huge drop in inverter voltage

      Reply
  72. Unknown says

    May 26, 2016 at 10:57 am

    I hv a 1000 wt invetor and a 240 solar panel and battery but if I try to connect the invetor it just says faulty Wat cn be the problem with it

    Reply
    • Swagatam says

      May 26, 2016 at 4:24 pm

      your specs are not sufficient for judging the fault…

      Reply
  73. NANDULA SUBRAHMANYAM says

    February 25, 2016 at 5:19 am

    Hello sir. Can you suggest me what are all the components to be bought by me including their grades as I am not much aware of electrical components

    Reply
    • Swagatam says

      February 25, 2016 at 8:31 am

      Hi Nandula, please specify your requirement specifications….only then I would be able to suggest.

      Reply
    • NANDULA SUBRAHMANYAM says

      February 26, 2016 at 3:23 am

      My requirement is making a speed restrictor for vehicles.

      Reply
      • Swagatam says

        February 26, 2016 at 6:41 am

        you can try the following circuit

        https://www.homemade-circuits.com/2013/12/vehicle-speed-limit-alarm-circuit.html

        Reply
  74. kanu kamliya says

    May 15, 2014 at 4:41 am

    hello sir I am student from Anand,Gujarat, I
    want to make 100 watt solar
    inverter,so how many watts solar panel and
    battery require for it?

    Reply
    • Swagatam says

      May 15, 2014 at 2:09 pm

      please see the above comment.

      Reply
  75. kanu kamliya says

    May 15, 2014 at 4:11 am

    hello sir I want to run 100 watt inverter on solar panel so how many watts panel require for it???

    Reply
    • Swagatam says

      May 15, 2014 at 2:08 pm

      hello kanu, you can try a 25 watt panel and a 25 AH battery

      Reply
  76. eshkariel tapiador says

    April 23, 2014 at 3:31 am

    Don't forget the circuit…

    Reply
    • Swagatam says

      April 23, 2014 at 11:48 am

      eshkariel, I think it's already published in my blog, you can refer to this post for more info:

      https://www.homemade-circuits.com/2013/04/solar-water-heater-with-battery-charger.html

      Reply
  77. Swagatam says

    April 8, 2014 at 4:19 am

    Good Morning Eshkariel,

    Your calculations look OK to me.

    You can try the inverter that's been covered in this article although it's not a pure sine wave, just a modified one.

    https://www.homemade-circuits.com/2013/04/how-to-modify-square-wave-inverter-into.html

    transformer rating could be = required wattage divided by available voltage, this will give the amp rating for the trafo.

    Battery could be rated at = required wattage divided by voltage,this will give the AH of the battery, but make it twice at least for a reasonable back up time.

    Reply
  78. achilles hector says

    March 18, 2014 at 4:41 am

    Good day Swags!!!
    How's my circuit?

    Reply
    • Swagatam says

      March 18, 2014 at 3:45 pm

      Good day Eshkariel,
      you can try calculating the parameters with the help of the data given in the above article. It isn't very difficult if you see.

      I'll try to design the solar charger that you have asked and will let you know soon, pls remind me if i forget, though:)

      Reply
  79. achilles hector says

    December 16, 2013 at 12:24 pm

    Dear Mr. Majumdar

    Can you help me in installing a solar panel at home?

    I have the following data:

    Solar panel wattage: 216 watts
    Electricity required in our home: 106 watts
    Hours of use: it doesn't matter to me as long the hours wont go below 10 hours.
    Hours of sunlight (based on the normal daylight ): Max.- 7 hrs.; Min.- 6 hrs

    Can you fill in the blanks? :
    battery: voltage:___; amp-hours:___
    inverter: wattage:___; voltage: 220

    Can I ask if you can make me a solar charge controller out of the data above?

    And can you add a function to the solar charge controller? : If the sun has enough light,
    the inverter will get the source from the solar panel while the battery is being charged.
    Then the moment the cloud dims, in which the solar panel can't produce enough voltage,
    the relay will change the inverter's source, which is from solar panel to battery. With this function I can protect the appliances from low voltage and use the solar panel during daytime.

    thanks a lot for your kind consideration!!!!

    yours truly
    Eshkariel Tapiador

    Reply
    • Swagatam says

      December 17, 2013 at 6:17 am

      Dear Achiless,

      I'll try to do it and respond soon.

      Reply
      • Dereje Hailemariam says

        December 14, 2021 at 6:03 pm

        hello
        I’m dereje from ethiopian
        My design is commercial building and I need solar system for lighting. total power of lighting is 30KW. so how many solar panel, battery and inverter ues?
        If you can send the answer with calculation?
        thank you
        dereje

        Reply
        • Swagatam says

          December 14, 2021 at 7:26 pm

          Hello, the whole procedure is explained in the above article, please calculate your parameters accordingly.

          Reply
          • Hussein says

            March 14, 2022 at 12:46 am

            I want the calculation of 200wat item for 24 hours to use I need the calculation

            Reply
            • Swagatam says

              March 14, 2022 at 10:23 am

              The calculation procedure is provided in the article, you can easily follow them.

              Reply
        • Tokkummaa says

          December 29, 2021 at 1:27 am

          It is easy, so just follow the steps he wrote down. Berta Dereje. lol

          Reply
      • Hussein says

        March 13, 2022 at 8:09 pm

        I wanna use a fridge of 160watt 1.35amp how many solars, batteries, and inverter and charge controller do I need?

        Reply
    • Olamide says

      December 3, 2019 at 3:51 pm

      Hello sir, I want you enlighten me on this, I have a battery bank of 19v 47ah lithium ion battery that I used to charge my laptop, but I want to use it with my 1000W inverter, when I read the normal out of the battery it was 16.8v, the battery was connected in parallel and series, I have 20amps charge controller. Now my question is that, (can 12v 40watt solar with 20amps charge controller charge the battery without giving out any problem) thanks sir

      Reply
      • Swagatam says

        December 3, 2019 at 4:21 pm

        Hello Olamide, A 40 watt panel will only produce 3.33 amps from 12 V, which is way too less for the battery in terms of voltage and current both, so your solar panel will not be able to charge the mentioned battery. Even with a boost charger the current will drop to 2 amps which is not sufficient for the battery. Your panel must be rated at 24 V 15 amps or 10 amps for charging the battery efficiently and quickly.

        Reply
        • Vijayalakshmi M says

          August 28, 2020 at 3:50 pm

          to charge 48volt, 50Ah lithium ion battery , suggest solar panel rating

          Reply
          • Swagatam says

            August 28, 2020 at 7:21 pm

            You can use a 65 V 20 amp solar panel.

            Reply
            • Paulo Racho says

              May 18, 2021 at 6:43 am

              Hello Sir Swagatam,
              I am from the Philippines and I am would like to ask how many batteries I need for the system.
              Status: I have 1HP Aircon and I want it to run the aircon from 10hrs/day and I want to use my reserve energy for this aircon, I want to isolate the aircon and put off-grid system how many batteries I need for this? I have a Lifepo4 3.4v 100Ah battery. what would be my solar PV system?

              thank you for your fast response

              Reply
              • Swagatam says

                May 18, 2021 at 10:51 am

                Hello Paulo, In the above article I have explained step wise so you can easily calculate the parameters required for your application. For example the total power required for your AC will be
                1000 x 10 = 10000 watts
                solar panel will be 10000/10 = 1000 watts. Keeping 10% more margin gives 1100 to 1200 watt panel.
                Battery can be also calculated by using the information given in the article.

                Reply

Need Help? Please Leave a Comment! We value your input—Kindly keep it relevant to the above topic! Cancel reply

Your email address will not be published. Required fields are marked *

Primary Sidebar

Subscribe to New Circuit Ideas

Categories

  • Arduino Projects (87)
  • Audio and Amplifier Projects (132)
  • Automation Projects (17)
  • Automobile Electronics (101)
  • Battery Charger Circuits (83)
  • Datasheets and Components (104)
  • Electronics Theory (143)
  • Free Energy (37)
  • Games and Sports Projects (11)
  • Grid and 3-Phase (19)
  • Health related Projects (25)
  • Home Electrical Circuits (12)
  • Indicator Circuits (14)
  • Inverter Circuits (87)
  • Lamps and Lights (142)
  • Meters and Testers (69)
  • Mini Projects (46)
  • Motor Controller (64)
  • Oscillator Circuits (27)
  • Pets and Pests (15)
  • Power Supply Circuits (108)
  • Remote Control Circuits (50)
  • Security and Alarm (64)
  • Sensors and Detectors (101)
  • Solar Controller Circuits (59)
  • Temperature Controllers (42)
  • Timer and Delay Relay (49)
  • Transmitter Circuits (29)
  • Voltage Control and Protection (37)
  • Water Controller (36)

Calculators

  • Battery Back up Time Calculator
  • Capacitance Reactance Calculator
  • IC 555 Astable Calculator
  • IC 555 Monostable Calculator
  • Inductance Calculator
  • LC Resonance Calculator
  • LM317, LM338, LM396 Calculator
  • Ohm’s Law Calculator
  • Phase Angle Phase Shift Calculator
  • Power Factor (PF) Calculator
  • Reactance Calculator
  • Transistor Astable Calculator
  • Transistor base Resistor Calculator
  • Voltage Divider Calculator
  • Wire Current Calculator
  • Zener Diode Calculator
  • Filter Capacitor Calculator
  • Buck Converter Calculator
  • Boost Converter Calculator
  • Solar Panel, Inverter, Battery Calculator
  • Wire Current Calculator
  • SMPS Transformer Calculator
  • IC SG3525, SG3524 Calculator
  • Inverter LC Filter Calculator

People Also Search

555 Circuits | 741 Circuits | LM324 Circuits | LM338 Circuits | 4017 Circuits | Ultrasonic Projects | SMPS Projects | Christmas Projects | MOSFETs | Radio Circuits | Laser Circuits | PIR Projects |

Recent Comments

  • Swagatam on EGS002 Datasheet, Circuit Diagram Explained
  • Swagatam on How to Make IC LM339 Circuits
  • Swagatam on How to Make Dog Barking Preventer Circuit using High Frequency Deterrence
  • Swagatam on How to Buy and Use RF Remote Control Modules – Control Any Electrical Gadget Remotely
  • Swagatam on How to Generate PWM Using IC 555 (2 Methods Explored)

Company

  • Privacy Policy
  • Cookie Policy
  • About Me
  • Contact
  • Disclaimer
  • Copyright
  • Videos
  • Sitemap

Social Profiles

  • Twitter
  • YouTube
  • Instagram
  • Pinterest
  • My Facebook-Page
  • Quora
  • Stack Exchange
  • Linkedin
  • © 2025 · Swagatam Innovations