The circuit explained here will provide LED indications and show if there's a possible fault in the wiring of your home AC Phase, Neutral, and Earth connections. The idea was requested by Mr. SS kopparthy.

Table of Contents
  • Technical Specifications
    • Using 3 LEDs for the Indications
    • Simplified Schematic

Technical Specifications

sir, very good morning. I thank you for your help. I further wanted you to consider a circuit whose pics are attached with links given.

This pcb would indicate me when earth is leaking(at that time the tester would burn when touched to earthing pin in 220v socket and will get a strong shock when touched by mistake.

Even the metal bodies of appliances give shock at that time.) by switching on the first two led's.if you look at the attached pics, you can see that the circuit has only a few resistors and diodes, and a black colored capacitor at back.

i also tried to draw the circuit diagram by seeing that pcb. the same pcb indicates the fuse blown condition.for circuit diagram and pictures of pcb, please see "


sir, i hope you understand the working of circuit and also hope you'll tell how its working to me also.......the purpose of writing this is that i would like you to help me by designing the circuit which has buzzer with led indication when something goes wrong. thank you very very very very very very very very much sir.........i cannot forget your help......

Using 3 LEDs for the Indications

The above circuit can be much simplified and implemented using a just three LEDs and some resistors.

The circuit may be understood as follows.

The design of the proposed LIVE or phase, neutral, earth indicator circuit is rather simple.

As can be seen in the given diagram one LED is connected across the phase/neutral, another LED across phase/earth and a third one across neutral/earth.

Each LED has its own limiting resistor rated at 56K 1 watt.

The illuminations from the LEDs in response to the different L/N/E faulty conditions could be witnessed as given under:

LED1 and LED2 ON and LED3 OFF indicates a good overall situation wherein the phase, neutral and earth could be assumed to all wired correctly.

LED2 and LED3 ON and LED1 OFF indicates a wrong polarity of phase/neutral but earth and neutral may be assumed to be rightly configured.

All three LEDs ON indicates an open earth or neutral which may be diagnosed further. Since an open neutral is rare, the possibility of an open "earth" could be considered and investigated.

In addition to the phase, neutral, earth fault indications the circuit also employs a blown fuse indicator in the form of LED4 which simply lights up if the fuse is blown or open and a appliance hooked up.

Note tat the polarity of the LEDs are not crucial and could be used any way round.

Use of red LEDs is recommended, other types could show unusual responses.

The earth leakage sensor and buzzer circuit will be soon updated.

Simplified Schematic

You'll also like:

  • largedigitalclockcircuitSimple Digital Clock using LM8650 IC Circuit
  • low side current sensingPrecision Current Sensing and Monitoring Circuit using IC NCS21xR
  • MQ-135 Air Quality Sensor Circuit – Working and Interfacing with Program Code
  • digitalvolumecontrolcircuitDigital Up/Down Volume Control Circuit

Filed Under: Sensors and Detectors Tagged With: AC, Earth, Fault, Indicator, Neutral, Phase

About Swagatam

I am an electronics engineer and doing practical hands-on work from more than 15 years now. Building real circuits, testing them and also making PCB layouts by myself. I really love doing all these things like inventing something new, designing electronics and also helping other people like hobby guys who want to make their own cool circuits at home.

And that is the main reason why I started this website homemade-circuits.com, to share different types of circuit ideas..

If you are having any kind of doubt or question related to circuits then just write down your question in the comment box below, I am like always checking, so I guarantee I will reply you for sure!



Previous Post: « Microcontroller Basics Explored
Next Post: Earth Leakage Indicator Circuit for Detecting Current Leakages in Ground Wires »

Reader Interactions

Questions & Answers

Total Posts: 22
Newest Oldest
Ahmed Askar
May 15, 2014 • 12 years ago #22513

hi Swagatam..
is there any chance to see a circuit of a transformless power inverter like 12/9amps to 220 v or 6v/4 amps to 15v ?

Reply
SwagatamAdmin
May 17, 2014 • 12 years ago #22540

Hi Ahmad,
I'll start publishing them serially as soon as I crack how to design ferrite transformers as per the specific needs without using complex formulas, until then it would be difficult.

Reply
vivek bhakta
October 1, 2014 • 12 years ago #26141

sir i build this and working fine but my collage sir ask me how i choose 56k resistor i need formula and explanation i mailed u also please reply as soon as possible thankx in advance

Reply
SwagatamAdmin
October 2, 2014 • 12 years ago #26149

Vivek, it has been selected arbitrarily such that the LED produces good brightness and also the resistor stays cool…

although the actual formula is (220V – 3.3)/0.02….this gives around 11k but this value will need to be of 220 x 0.02 = 4.4 watts which can be bulky therefore 56k was chosen so that 1/4 watt could be used.

Reply
vivek bhakta
October 6, 2014 • 12 years ago #26233

thankx a lot sir

Reply
Unknown
February 26, 2016 • 10 years ago #39182

What is the reason for C1?

Reply
SwagatamAdmin
February 27, 2016 • 10 years ago #39196

It could be an MOV, not a capacitor

Reply
Hamid Gh
December 10, 2016 • 10 years ago #47226

Hi Mr Swagatam Majumdar

In my country (Iran) there is no earth and I have circuit that need real phase and null entered , and
If the reverse were entered ،
The circuit does not work until the phase and neutral are correct.

Please guide me

Reply
SwagatamAdmin
December 11, 2016 • 10 years ago #47238

Hi Hamid,

you can use a neon line tester to verify which side was the phase, and then plugin the device with correct polarity.

I hope I understood your requirement correctly…

Reply
Aslan
November 3, 2017 • 9 years ago #55535

Hi dear Swagatam

I have 3 questions about the first pic circuit :
1) In which amount of earth resistance, this instrument shows that earth is faulty?
2) If earth is disconnected, are the other tests (like L&N inverse) possible?
3) Can this instrument show that earth and ground are connected to each other, inside wall ?(if yes, which fault will be showed ?)
thank you for your help

Reply
SwagatamAdmin
November 4, 2017 • 9 years ago #55547

Aslan, I cannot interpret the first circuit because it is not designed by me, and also because I feel it is not correctly designed.

Reply
Binoj K
March 27, 2020 • 6 years ago #77512

Hi swagath sir, can you please send me the pcb schematic for the circuit. I was looking for it for quite a long time. And is there any problem for the first given circuit? I have one similar to that but burnt out some way .All the three LEDs and 2 resistors are burnt.

Reply
SwagatamAdmin
March 28, 2020 • 6 years ago #77522

Hi Binoj, sorry I do not have a PCB design for this project. use 1 watt wirewound resistors, they won’t burn

Reply
Umesh
August 10, 2020 • 6 years ago #81185

Hi Swagatam,

I am working on EMI/RFI filter and Surge suppression circuit for Extension board (230-250 VAC,50 Hz supply) and looking for standard circuit for the same. Can you please send me the optimized PCB circuit and schematic for EMI/RFI filter and Surge suppression circuit?

Regards,
Umesh

Reply
SwagatamAdmin
August 10, 2020 • 6 years ago #81195

Hi Umesh, you can try the following circuit:

RFI EMI filter with surge supression circuit

Reply
Umesh
August 10, 2020 • 6 years ago #81200

Thank Swagatam for your prompt response. Is it possible to include indicator LED’s for Phase,Neutral and Earth. I am having modified circuit but don’t know if it is right or wrong? I am not able to share image of circuit with you in comment box. Is any other way of sharing circuit?

Regards,
Umesh

Reply
SwagatamAdmin
August 11, 2020 • 6 years ago #81228

Umesh, for LED connections you may have to implement the second circuit which is explained in the above article. You can also try your modified design by connecting the L, N. E wires across the relevant lines. You can share the image through Google drive.

Reply
Umesh
August 11, 2020 • 6 years ago #81245

Hi Swagatam,

Again Thanks for your response. Based on your circuit details and combining it with LED indications I prepared modified circuit. Please check on following google drive link for comments and let me know if changes required.

https://drive.google.com/file/d/1KEQghUqLpgeGl9pI4kFfMxBHs85t_orP/view?usp=sharing

Regards,
Umesh

Reply
SwagatamAdmin
August 11, 2020 • 6 years ago #81246

Hi Umesh, please change the link to sharing mode so that it becomes accessible to me.

Reply
Umesh
August 11, 2020 • 6 years ago #81249

Hi Swagatam,

Please access following link.

https://drive.google.com/file/d/1KEQghUqLpgeGl9pI4kFfMxBHs85t_orP/view?usp=sharing

Regards,
Umesh

Reply
SwagatamAdmin
August 12, 2020 • 6 years ago #81266

Hi Umesh, the LEDs should be on the switch side according to me, as shown below.

computer strip board circuit diagram

But the RFI section is not as per my design so I cannot comment on that.

Reply
Sandeep
September 25, 2020 • 6 years ago #82578

Can we get a PCB for assembling the Phase-Earth-Neutral fault indicator circuit?

Reply

Need Help? Please Leave a Comment! We value your input—Kindly keep it relevant to the above topic! Cancel reply

Your email address will not be published. Required fields are marked *

Primary Sidebar



My Youtube Channel

Circuit Simulator

circuit simulator image



Subscribe to get New Circuits in your Email



Categories

  • Arduino Projects (95)
  • Audio and Amplifier Projects (134)
  • Automation Projects (18)
  • Automobile Electronics (103)
  • Battery Charger Circuits (88)
  • Datasheets and Components (109)
  • Electronics Theory (149)
  • Energy from Magnets and Earth (40)
  • Games and Sports Projects (11)
  • Grid and 3-Phase (20)
  • Health related Projects (27)
  • Home Electrical Circuits (13)
  • Indicator Circuits (16)
  • Inverter Circuits (99)
  • Lamps and Lights (162)
  • Meters and Testers (72)
  • Mini Projects (28)
  • Motor Controller (68)
  • Oscillator Circuits (28)
  • Pets and Pests (15)
  • Power Supply Circuits (91)
  • Remote Control Circuits (50)
  • Security and Alarm (65)
  • Sensors and Detectors (107)
  • SMPS and Converters (45)
  • Solar Controller Circuits (60)
  • Temperature Controllers (43)
  • Timer and Delay Relay (50)
  • Voltage Control and Protection (44)
  • Water Controller (37)
  • Wireless Circuits (31)



Other Links

  • Privacy Policy
  • Cookie Policy
  • Disclaimer
  • Copyright
  • Videos
  • Sitemap

People also Search

555 Circuits | 741 Circuits | LM324 Circuits | LM338 Circuits | 4017 Circuits | Ultrasonic Projects | SMPS Projects | Christmas Projects | MOSFETs | Radio Circuits | Laser Circuits | PIR Projects |



Recent Comments

  • Swagatam on 3 Tested 220V High and Low Voltage Cut OFF Circuits Using IC LM324 and Transistors
  • ENGR BRIGHT on 3 Tested 220V High and Low Voltage Cut OFF Circuits Using IC LM324 and Transistors
  • Swagatam on IC LM393 Complete Datasheet with Circuit Diagram
  • Norman D Kelley on IC LM393 Complete Datasheet with Circuit Diagram
  • Swagatam on Simple Capacitive Discharge Ignition (CDI) Circuit

Social Profiles

  • Twitter
  • YouTube
  • Instagram
  • Pinterest
  • My Facebook-Page
  • Stack Exchange
  • Linkedin

© 2026 · Swagatam Innovations