• Skip to main content
  • Skip to primary sidebar

Homemade Circuit Projects

Need circuit help? Post them in the comments! I've answered over 50,000!

Blog | Categories | About | Hire Me | Contact | Calculators-online
You are here: Home / Security and Alarm / Earth Leakage Indicator Circuit for Detecting Current Leakages in Ground Wires

Earth Leakage Indicator Circuit for Detecting Current Leakages in Ground Wires

Last Updated on July 30, 2019 by Swagatam 75 Comments

A simple earth leakage indicator circuit discussed here can be used for getting some very useful results regarding current leakages from an appliance body into the earth pin. The idea was requested by Mr. SS kopparthy.

Table of Contents
  • Circuit Operation
    • Parts List
    • Parts List
    • Test Set-Up for the above circuits:
      • Earth Leakage Indicator

The circuit of the proposed earth leakage indicator is shown in the figure below.

Each such unit may be used for individual appliances having earth pins, or a single circuit may be placed near the MCB for detecting a possible common leakage from all the appliances.The circuit may be understood with the points I have explained below:

Circuit Operation

R2 is positioned as a current sensing resistor which should have a relatively low value so that the actual earthing feature doesn't get obstructed due to its resistance.

T1 here forms a current sensing and a voltage amplifier stage. The detected small voltage across R2 is quickly amplified by T1 and fed to the LED inside an opto coupler.

As long as the leakage is not relatively significant (below 20mA) the LED inside the opto does not respond, however the moment this value exceeds the set limit, the LED inside the opto illuminates switching ON the corresponding built-in transistor, which in turn actuates the red LED connected across its collector and positive lead indicating a possible earth leakage.

The supply for the entire operation is derived through a small trasformerless power supply using C1, D1, C2 as its main components.

The red LED may be replaced with a 12V piezo buzzer for getting an audio indication, or both may be used in parallel for facilitating a dual mode indication.

The value of R2 may be calculated using the following formula:

R = 0.2/I. where I is allowable current leakage through the earthing cable, assuming this to be 20mA we can calculate it as:

R = 0.2/.02 = 10 ohms

Since the collector resistance if T1 is quite high, T1 could get triggered with as low as 0.2 across its base/emitter, that's the reason why 0.2 is selected in the above formula.

The T2 stage is introduced for monitoring the "health" of the earthing connection, as long as it's at par with the neutral, T2 stays switched off since its base remains grounded via the good earthing, however the moment a weak earthing is formed, T2 base gets enough voltage through R5 to trigger itself and the opto which in turn triggers the connected alarm.

The situation of a weak or open earthing is indicated by the red and yellow LEDs together, while the red LED alone indicates an earth leakage.

CAUTION: THE CIRCUIT IS NOT ISOLATED FROM MAINS, ALL PARTS COULD CARRY LETHAL ELECTRIC CURRENT, EXERCISE UTMOST CAUTION WHILE HANDLING UNCOVERED.

Parts List

R1 = 1K ohms
R2 = see text
R3, R4 = 22k
R5 = 56K
R6 = 1M
D1 = 15V 1watt zener diode
C2 = 100uF/25V
T1, T2 = BC547
C1 = 0.47uF/400V
opto = any standard 4-pin type

The above circuit could be improved by adding a few more components to it, as shown below:

In this circuit we have added a rectifier diode D1 (1N4007) for an improved rectification.

T1 has been enhanced with another BC547 transistor T2 wired as Darlington in order to make the earth leakage detection even more sensitive and allow the use of smaller in-line resistance R2 for better "earthing" experience for the appliances.

C2 (0.22uF) ensures that T1/T2 does not get rattled with unwanted electrical disturbances.

Parts List

R1 = 1K
R2 = see text
R3, R4 = 22k
R5 = 56K
R6 = 1M
Z1 = 15V 1watt zener diode
D1, D2 = 1N4007
C0 = 0.47uF/400V
C1 = 100uF/25V
C2 = 0.22uF
T1, T2, T3 = BC547
C1 = 0.47uF/400V
opto = any standard 4-pin type

Test Set-Up for the above circuits:

Earth Leakage Indicator

The above diagram shows the test set-up for the proposed earth leakage indicator circuit.
It's conducted in the following manner:

The circuit powered up using an external 12V AC/dC adapter output, remember do not plug-in the circuit to mains while doing this procedure

In the set-up test 12V AC supply is connected across the earth/appliance points via a 12V bulb.

R5 link is kept disconnected for the time being.

The above implementation should instantly switch ON the red LED indicating a current leakage through R2.

Disconnecting the 12V bulb, the red led must also switch OFF, indicating the stoppage of the leakage condition.

Now reduce the 12V bulb load to some lower value, could be done by including another 12V bulb in  series to it.

Even with such lower loads, the red LED should be able to indicate the leakages across R2 confirming the proper working of the circuit.

Now removing the above load should instantly switch off the red LED, assuring a correct working of the circuit.

Restore the circuit to its original condition and now it's ready for the actual installation near your MCB.

The functioning of the yellow LEd can be witnessed after the actual installation and connections are done.

If it starts glowing immediately after the installation would indicate a bad or incorrectly wired earthing line.

You'll also like:

  • high voltage moduleGadgets to Protect Women from Assaults and Harassment
  • flashlight activated burglar alarm circuitFlashlight Activated Burglar Alarm Circuit
  • ACFieldDetectorAnti Spy RF Detector Circuit – Wireless Bug Detector
  • touch code lockTouch Operated Code Lock Switch Circuit

Filed Under: Security and Alarm Tagged With: Current, Detecting, Earth, Indicator, Leakage, Leakages

About Swagatam

I am an electronics engineer and doing practical hands-on work from more than 15 years now. Building real circuits, testing them and also making PCB layouts by myself. I really love doing all these things like inventing something new, designing electronics and also helping other people like hobby guys who want to make their own cool circuits at home.

And that is the main reason why I started this website homemade-circuits.com, to share different types of circuit ideas..

If you are having any kind of doubt or question related to circuits then just write down your question in the comment box below, I am like always checking, so I guarantee I will reply you for sure!



Previous Post: « AC Phase, Neutral, Earth Fault Indicator Circuit
Next Post: Remote Controlled Wireless Water Level Controller Circuit »

Reader Interactions

Questions & Answers

Total Posts: 75
Newest Oldest
Tushar
June 4, 2026 • 2 months ago #207931

How do you understand which components to choose and how many to choose like you have used 3 transistors I don’t know it how it’s done and then connecting them like how should I connect according to my needs please help I also want to design my own circuits

Reply
SwagatamAdmin
June 4, 2026 • 2 months ago #207937

Designing circuits becomes easier when you first understand the function of each component. For example a transistor can be used as a switch, amplifier, oscillator, current booster, etc. The number of transistors depends on what functions are needed in the circuit.
Normally circuit design starts by defining the required input, output, voltage, current, and control functions. Then suitable stages are added one by one. For instance, you may need one transistor for sensing, another for amplification, and a third for driving a relay or a load.
The best way to learn is to study existing circuits and analyze why each component is used. Then try making small modifications and observe the results. After some practice you will naturally begin to understand how many components are needed and how they should be connected to achieve a specific function. Circuit design is mostly a combination of theory, experience, and experimentation.

Reply
Duminda Bandurathna
November 20, 2024 • 2 years ago #165692

Dear sir,

Can you provide a circuit for if the Earth line is disconnected led to be light on for in 230v AC?

Reply
DUMINDA BANDURATHNA
November 22, 2024 • 2 years ago #165766

Dear Sir,
I have tested it, It’s working as expected. can I improve the LED brightness?
Thank you very much, sir.

Reply
SwagatamAdmin
November 22, 2024 • 2 years ago #165768

That’s great Duminda, thanks for updating…
You can try reducing the 100k to some lower value and check the response, maybe to 68k or 47k…

Reply
Duminda Bandurathna
December 22, 2024 • 2 years ago #167513

Dear Sir,
I have implemented the circuit according to your advice, and it is functioning as expected. However, the circuit turns on and off continuously, and the 4148 diode and BC547 transistor frequently burn out. I intend to use this circuit continuously at my home.
Could you please advise on how to resolve this issue?

Reply
SwagatamAdmin
December 22, 2024 • 2 years ago #167514

Thanks for the update Duminda,
The circuit which I provided you above runs on 12V DC, so the BC547 and the diodes can never burn. If your 12v zener diode is fine, then the rest of the circuit components should be also fine and intact, nothing should burn.
Please check the voltage across the zener diode and the circuit, if you find it to be 12V then there’s no way anything should burn in the circuit.
Be careful, the circuit is not isolated from mains AC, and therefore is extremely dangerous to touch..

Reply
Duminda Bandurathna
December 22, 2024 • 2 years ago #167515

Dear Sir, I have used this circuit with my power guard circuit power supply. It also includes a 225J 400V capacitor for AC voltage reduction, which is further regulated to 12V using a 12V, 1W Zener diode.

Reply
SwagatamAdmin
December 23, 2024 • 2 years ago #167519

Thank you Duminda,
If it is regulated with a 12V zener and if the zener diode is working fine, then nothing should burn in the circuit.
Please replace the 1N4148 diodes with 1N4007 for increased safety of the diodes.

Reply
SwagatamAdmin
November 20, 2024 • 2 years ago #165694

Hi Duminda, you can try the following circuit:
Earth fault indicator circuit
This will indicate whether the earthing is working good or not…
The circuit is not isolated from mains AC, so be extremely careful while testing this circuit…

Reply
Sammu
January 24, 2022 • 4 years ago #110396

I check My whole ckt all Ckt is ok ..and the vtg between T1 and T2 is 12v

Reply
SwagatamAdmin
January 24, 2022 • 4 years ago #110400

I have explained the circuit correctly please read and understand how it works, then you will be able to troubleshoot….12V is wrong, it should be 0.6V between base ofT1 and emitter of T2.

Make the first circuit, and try again.

Reply
Samu
January 24, 2022 • 4 years ago #110385

Hii sir i made these ckt but ..when i start the ckt R2 is start burning and no no led is glows..why this happen please help

Reply
SwagatamAdmin
January 24, 2022 • 4 years ago #110386

Samu, did you make the test set-up using 12V? R2 cannot burn at 12V

Reply
Saamu
January 24, 2022 • 4 years ago #110389

No sir i apply 12v supply directly through transform becoz bulb is is not available..is that i doing the right way ..becoz bulb is not available please help

Reply
SwagatamAdmin
January 24, 2022 • 4 years ago #110391

I am sorry, R2 is not 1K, but is supposed to be a small value resistor, and that is why a bulb is required, otherwise it will burn.
For the time being you can use 470 ohms for R2, just to check the LED behavior.

Reply
Samu
January 24, 2022 • 4 years ago #110393

Sir.is change R2 but sir LED is not glow ..

Reply
SwagatamAdmin
January 24, 2022 • 4 years ago #110395

measure voltage across T1 base and T2 emitter, it should be 0.6V minimum….there may be some fault in your circuit that is why no LED is glowing…..

Reply
SwagatamAdmin
January 24, 2022 • 4 years ago #110390

Even if you apply 12V directly to 1K (R2), still it should not burn.

Reply
S Raja
August 22, 2020 • 6 years ago #81592

Sir,
How much DC voltage we will get in this circuit after AC rectification?
Can I install 12 volt relay in parallel with LED (R3 circuit) so that it will work as circuit tripper? 🙂

Reply
S Raja
August 25, 2020 • 6 years ago #81683

Thank you Sir

Reply
SwagatamAdmin
August 22, 2020 • 6 years ago #81597

S Raja, for a relay you will have to use C0 as 105/400V or 1uF/400V…to get 50 mA out

Reply
sumalya saha
July 7, 2016 • 10 years ago #42377

Dear Sir,
When I stimulate the test circuit in multisim the optocoupler does not get activated ,so the red led does not glow .Why?

Reply
Rahul
October 18, 2017 • 9 years ago #54914

Sir, could you post on how to interface force resistor sensor with Arduino and the Arduino program..

Reply
Rahul
October 18, 2017 • 9 years ago #54921

Thank you sir

Reply
SwagatamAdmin
October 18, 2017 • 9 years ago #54918

Rahul,

you can reefer to this article or more info

https://www.homemade-circuits.com/2016/05/force-sensing-resistor-explained.html

Reply
SwagatamAdmin
July 9, 2016 • 10 years ago #42436

that's great Sumalya, thanks for updating the info.

Reply
sumalya saha
July 9, 2016 • 10 years ago #42426

Sir,I have solved the problem by decreasing the resistances R3 and R5 and it works fine!!!

Reply
SwagatamAdmin
July 7, 2016 • 10 years ago #42386

Dar Sumalaya, I'll redesign an easier circuit and post it soon…

Reply
Derin'Hakan Karakurt
September 29, 2015 • 11 years ago #34416

Hi. I've prepared the circuit but leakage LED never turns off. Where am I missing? Also the capacitor is 100uF or nF? Best regards.

Reply
SwagatamAdmin
September 30, 2015 • 11 years ago #34440

…the electrolytic cap is 100uF, not 100nF

Reply
SwagatamAdmin
September 30, 2015 • 11 years ago #34439

Hi, if the earthing is not good enough it will not be able to ground the T2 base and therefore the red LED will continue to glow.

connect a 3V or 6V zener between the emitter of T2 and the neutral line, and check the response if still it doesn't solve the issue, let me know, I'll try to upadte an easier one

Reply
Andreas Chris
June 22, 2015 • 11 years ago #31688

I guess this circuit its not so usefull to any user, since cannot trip the appliance's power,it can only show its status by means of a led.
The most important thing its the RCB (Residual Circuit Breaker)it will certainly cut off the power to your appliance in case of leakage and you can tell from NOT working !

Reply
SwagatamAdmin
June 23, 2015 • 11 years ago #31693

a tripping action may not be mandatory for minor leakages, because small leakages may not be hazardous but might increase the utility bill.

the above circuit in intended to get a visual indication if there's some kind of leakage which is rather common in every house.

Once the user sees this, the issue can be corrected by identifying the cause.

By the way I have an ELCB design which includes a cut-off feature:

https://www.homemade-circuits.com/2011/12/make-simple-earth-leakage-circuit.html

Reply
sskopparthy
May 30, 2014 • 12 years ago #23032

(Continuation of above comment)…….sir, just observed clearly, transistor T3 blew off, it melted and its emitter and collector melted and cut…..

Reply
SwagatamAdmin
June 5, 2014 • 12 years ago #23207

..if you have any issues with the post, feel free to express them under the article.

Reply
SwagatamAdmin
June 5, 2014 • 12 years ago #23205

Thank you SS, you have done a nice job.

Please see the published post here:

https://www.homemade-circuits.com/2014/06/making-helping-third-hand-for-aiding.html

Yes you may send your pic, I'll post it in the article.

Reply
sskopparthy
June 4, 2014 • 12 years ago #23199

And by the way sir, you also asked my picture for posting the article with my name, if i am not wrong….. should I submit it sir………?

Reply
sskopparthy
June 4, 2014 • 12 years ago #23198

Dear sir, please contact me on my mail Id or here if anything is wrong or if any further information is required from my side…….and Thank you once again………….

Reply
SwagatamAdmin
June 3, 2014 • 12 years ago #23166

You are welcome Srinivas,

I'll check it out soon. thanks!

Reply
sskopparthy
June 3, 2014 • 12 years ago #23158

Dear Sir, I have sent all the details to your mail(homemadecircuits@gmail.com). please check them out. And thank you very much for posting the photos sent by me regarding "Self Regulating, Automatic Lead Acid Battery Charger Circuit". Thank you very much Sir……
Regards,
Sai Srinivas.K

Reply
SwagatamAdmin
June 2, 2014 • 12 years ago #23124

Dear Srinivas, thank you very much! I appreciate it, please go ahead!

Reply
sskopparthy
June 1, 2014 • 12 years ago #23104

Dear sir, thank you very much for your support. And sorry for including external links, but there is no other way i could convey the information to you…… . And I will send you all the deteils and photos of th e instrument to your mail id(homemadecircuits@gmail.com) soon maybe within 3-4 days. Thank you very much for your support to me. 🙂
Thanks and best regards,
Sai Srinivas.K.

Reply
SwagatamAdmin
June 1, 2014 • 12 years ago #23084

Thank you dear SS, I appreciate all your efforts, and yes if you can submit the article with all the details, I'll make sure it gets published in my blog with your name and picture.

I would be deleting this conversation shortly since there are a few external website links here.

Reply
SwagatamAdmin
May 31, 2014 • 12 years ago #23058

Dear SS, that's a wise decision, learn all the basics first and come back with confidence.

I appreciate your wise decision.

You are always welcome here….

good luck and best wishes to you!

Thank you for being a part of this blog.

Reply
sskopparthy
May 31, 2014 • 12 years ago #23055

Dear sir, i wanted to do this circuit as our apartment's earth is very weak and it does not absorb any of the leakages….and any leakage in anyone's home shows effect on our appliances and we get a strong shock at that time. so this circuit is to be made in order to help ourselves from not getting shocks….otherwise, i never prefer this type of circuits which are not isolated from mains. But as you are cautioning me this many times for my sake, I prefer quitting than making…..NOw I dont understand how to make an earth leakage indicator circuit to help me and protect us….Anyway, thank you very much for all your help, I disturbed you a lot…..sorry for that…..But I learnt a lot, thank you for that…….have a nice time….bye, I'll be back after 1 year as my summer holidays are over.

By the way, all the circuits that I made from your blog are still working and I installed them in my house like automatic plant watering system, rain sensor, automatic day/night switch, auto wiper switch for car, auto battery charger, low battery and overload cutoff, and many many more(maybe 25-28 circuits). Thank you for all that. You're indeed a good teacher.I never like to miss you, I need your help maybe in future, I'll keep in touch with you, bye for now…..

yours,
sai srinivas.K, with bunch of thanks.

Reply
SwagatamAdmin
May 30, 2014 • 12 years ago #23034

SS I won't recommend this circuit to you because it's for experienced hobbyists only, so please quit, and go for other simpler projects:)

Reply
View Older Comments

Need Help? Please Leave a Comment! We value your input—Kindly keep it relevant to the above topic! Cancel reply

Your email address will not be published. Required fields are marked *

Primary Sidebar



Categories

  • Arduino Projects (95)
  • Audio and Amplifier Projects (134)
  • Automation Projects (18)
  • Automobile Electronics (103)
  • Battery Charger Circuits (88)
  • Datasheets and Components (109)
  • Electronics Theory (150)
  • Energy from Magnets and Earth (40)
  • Games and Sports Projects (11)
  • Grid and 3-Phase (20)
  • Health related Projects (27)
  • Home Electrical Circuits (13)
  • Indicator Circuits (16)
  • Inverter Circuits (100)
  • Lamps and Lights (163)
  • Meters and Testers (72)
  • Mini Projects (28)
  • Motor Controller (68)
  • Oscillator Circuits (29)
  • Pets and Pests (15)
  • Power Supply Circuits (91)
  • Remote Control Circuits (50)
  • Security and Alarm (65)
  • Sensors and Detectors (107)
  • SMPS and Converters (46)
  • Solar Controller Circuits (61)
  • Temperature Controllers (43)
  • Timer and Delay Relay (50)
  • Voltage Control and Protection (44)
  • Water Controller (37)
  • Wireless Circuits (31)



Circuit Simulator

circuit simulator image



Subscribe to get New Circuits in your Email



Other Links

  • Privacy Policy
  • Cookie Policy
  • Disclaimer
  • Copyright
  • Videos
  • Sitemap

People also Search

555 Circuits | 741 Circuits | LM324 Circuits | LM338 Circuits | 4017 Circuits | Ultrasonic Projects | SMPS Projects | Christmas Projects | MOSFETs | Radio Circuits | Laser Circuits | PIR Projects |



Recent Comments

  • Swagatam on Phase Shift Oscillator Circuits – Wien-Bridge, Buffered, Quadrature, Bubba
  • Swagatam on PWM Inverter Using IC TL494 Circuit
  • Swagatam on Bicycle Generator Circuit
  • Swagatam on Digital Capacitance Meter Circuit Using Arduino
  • Swagatam on 7 Easy Voltage Doubler Circuits Discussed

Social Profiles

  • Twitter
  • YouTube
  • Instagram
  • Pinterest
  • My Facebook-Page
  • Stack Exchange
  • Linkedin

© 2026 · Swagatam Innovations