Single Transformer Inverter/Charger Circuit

Last Updated on May 17, 2026 by Swagatam 243 Comments

In this post I have explained how to build an innovative inverter circuit with a single transformer that works both as an inverter and a battery charger transformer, I have explained the details from the following discussion.

Table of Contents
  • The Circuit Objective
    • How the Circuit Functions
      • Parts List
  • Using a 2-Wire Transformer

The Circuit Objective

Though you may find many inverters having an integral battery charger, the section will mostly employ a separate transformer for implementing it.

In the following post I have explained a unique design which utilizes the inverter transformer for power inverting as well as for charging the battery.

The circuit diagram below shows a design where a single power transformer is used for inverting purpose as well as for charging the battery when mains is present.

The good thing about the circuit is that the transformer doesn't employ separate winding for this, rather works with the same input winding and reverts DC to the battery with the help of a few DPDT relays.

The circuit can be understood with the following points:

How the Circuit Functions

The inverter section can be easiy recognized in the diagram, R1 to R6, including the T1 and T2 forms a general astable multivibrator circuit for producing the required 50 or 60 Hz pulses.

These pulses drive the mosfets alternately which in turn saturate the transformer by switching the battery voltage in it.

The secondary of the transformer generates the corresponding magnitude of AC which is finally used for operating the connected appliances.

The above configuration suggests an normal or ordinary inverter operation.

By adding a couple of DPDT relays in the above discussed operation, we can force the circuit to charge the battery in the prsence of an AC mains source.

The coils of the two relays are powered through a capacitive low current compact power supply, involving C6, C5, D1----D5.

The above circuit is connected to a mains AC source, this source is also connected to RL1 poles.

The second relay RL2 is wired up with input winding of the transformer.

In the absence of mains AC, the position of the relay contacts are in the N/C as shown in the figure.

In this position the mosfets get linked with the transformer input winding, and the battery with the circuit so that the inverter starts oscillating and the output appliances gets the AC power from the battery.

In the presence of mains AC the relay coils instantly get the required DC power and the contacts activate.

RL1 activates and connects the mains input to the transformer, the appliances also get connected with the mains AC in the process.

Also due to the action of RL2 the mosfets get disconnected from the transformer, while the the lower tap connects with D6.

Since the center is already connected to battery positive, the inclusion of D6 provides a half wave rectified voltage to the battery, which is effectively filtered by C3 so that the battery is able to get the required sufficient charging voltage.

The above charging process continues until mains is present, so it should be monitored manually. When mains fails, the action reverts into inverting mode without interrupting the appliance operations and by using a single transformer for both the operations.

C4 makes sure that RL1 always activates a shade later than RL2 for safety reasons.

CAUTION: THIS CIRCUIT IS DEFINITELY NOT RECOMMENDED FOR THE NEW HOBBYISTS, IT'S SUITABLE ONLY FOR THE EXPERTS. IF YOU ARE A NOVICE AND INTERESTED TO TRY THIS.... BUILD IT AT YOUR OWN RISK.

Parts List

  • R1, R2 = 27K,
  • R3, R4, R5, R6 = 470 Ohms,
  • C1,C2 = 0.47uF/100V metallized
  • T1, T2 = BC547,
  • T3, T4 = any 30V, 10amp mosfet, N-channel.
  • C3 = 47000uF/25V
  • C4 = 220uF/25v
  • C5 = 47uF/100v
  • C6 = 105/400V
  • R7 = 1M
  • D1---D5 = 1N4007
  • D6 = 1N5402
  • RL1, RL2 = DPDT, 400 OHMS, 12V, 7 AMPS/220V
  • Transformer = 12-0-12V, current as per requirement.

For only inverter design please refer to this ARTICLE

Using a 2-Wire Transformer

If you do not want to use a center tap transformer for the inverter, then you can use the following P-channel and N-channel MOSFET H-bridge inverter module for getting an identical single transformer inverter/charger results:

You'll also like:

  • highcurrentbatterycharegrcircuitLead Acid Battery Charger Circuits
  • Simple 48V Automatic Battery Charger Circuit
  • Nicd Charger circuitSimple Ni-Cd Battery Charger Circuits Explored
  • batterychargercircuit3v, 4.5v, 6v, 9v, 12v, 24v, Automatic Battery Charger Circuit with Indicator

Filed Under: Battery Charger Circuits Tagged With: Charger, Inverter, Single, Transformer

About Swagatam

I am an electronics engineer and doing practical hands-on work from more than 15 years now. Building real circuits, testing them and also making PCB layouts by myself. I really love doing all these things like inventing something new, designing electronics and also helping other people like hobby guys who want to make their own cool circuits at home.

And that is the main reason why I started this website homemade-circuits.com, to share different types of circuit ideas..

If you are having any kind of doubt or question related to circuits then just write down your question in the comment box below, I am like always checking, so I guarantee I will reply you for sure!



Previous Post: « Single Phase Preventor Circuit
Next Post: How to Generate PWM Using IC 555 (2 Methods Explored) »

Reader Interactions

Questions & Answers

Total Posts: 243
Newest Oldest
SwagatamAdmin
September 6, 2013 • 13 years ago #14956

Acquiring 24V from 12V is difficult and is not recommended, because the transformer can become hot.

Wattage rating can be controlled by controlling the battery current through some circuit stage.

Reply
Arun Dev
October 7, 2013 • 13 years ago #15949

DEar sir,
Can i use a 10 A relay instead of the 7 A one used here

What precaution should be taken in order to safeguard the entire circuit before applying the ac mains to transformer's primary ?

And one more doubt sir
What does the connection (which seems like inductor coil )in the upper circuit means ? I realize that these are the connections across two relay pins and the upper circuit is the power feeding circuit for the relays. But i can't understand the 2 pins that i specified here. Please help me sir. I am not at all familiar with relays. Hoping your reply very soon sir……

Reply
SwagatamAdmin
October 8, 2013 • 13 years ago #15963

Dear Arun,

Use a 100 watt bulb in series with one of the input mains wires for safety.

The inductors are the relay coils, a relay cannot be activated unless its coils are energized therefore these coils are supplied through the capacitive power supply shown at the upper section of the diagram.

Reply
SwagatamAdmin
October 8, 2013 • 13 years ago #15964

….you may refer to this post for knowing more about relays:

https://www.homemade-circuits.com/2012/01/how-to-understand-and-use-relay-in.html

Reply
Arun Dev
October 8, 2013 • 13 years ago #15969

Sorry for disturbing you again sir. But what to do…. I have to be completely free of doubts before going for the design….. This time i am also coming with another doubt which may feel silly to you, please dn' t neglect it since i am not having deep knowledge in Electronics, but i like it.

I have a 300 W 12 V transformer having 4 thick windings at primary and 5 at secondary. I know it is a multi-tap one. But don't know how to wire them to suit for the single transformer inverter design.. Please help me……

How can i link the images with the comments in this blog ?

Reply
SwagatamAdmin
October 8, 2013 • 13 years ago #15976

You can connect the 220V wires to mains and measure the tap voltages with a multimeter, in this way you would be able to figure out the tap values.

Reply
SwagatamAdmin
October 8, 2013 • 13 years ago #15977

you can upload the images on any free image hosting site and provide me the link.

Reply
Arun Dev
October 8, 2013 • 13 years ago #15982

Sir that was not enough….. I need a better suggestion…….
My transformer is a locally made one. No markings ( even no separate colors for wires ) are there. The only thing that i could see that some set of the terminal wires are thicker than other set. From basic calculations of transformer design, i think the wires to bear large current are of secondary ( 300 W/ 12V ) and they have to be thick enough than the primary. Am i right ? If not please correct me…..
I am in a little bit confusion that how to connect the neutral and earth lines of ac mains into the transformer if it has 5 primary terminals as i calculated….. Please help me sir… Can you please suggest the exact connection schematics…..
Since it is an ac transformer, i willn't be able to measure the tap voltages exactly without a brige type rectifiers. Taking each tap voltage by changing the polarities supplied to the rectifier will be very time consuming..
I couldn't upload the images of the transformer…. SO PLZ HELP ME

Reply
SwagatamAdmin
October 9, 2013 • 13 years ago #15993

you won't need a bridge rectifier at each tap for checking, you can do it with your meter on AC 220V range.

you can also check the taps by measuring their resistances…the one which gives the highest resistance can be assumed to be the mains input winding, connect a 100 watt bulb in series which testing with mains for avoiding possible hazards.

Reply
Ramsreevasanth
October 10, 2013 • 13 years ago #16024

Very nice circuit sir.
Can i use a 300 W transformer in this circuit ? How much high will be the currents in both terminals ? Can i use the formula P= IV for its calculation. If i am doing so i will get maximum current
In primary : 1.304 A and
In secondary : 25 A…….. Is that will happen ?

If so, that diode (IN5402) used in Charging section sufficient to overcome this high amperage ?
What about the diodes at the primary if i am using the inverter to be run on a 300 W load. Reply me soon plz……. Sorry for the bad english…

Reply
SwagatamAdmin
October 10, 2013 • 13 years ago #16044

Thanks Ramsree,

You can use P = IV, 25amps is right but that might be too high for the battery, because as per rules the ideal charging current should be 1/10th of batery AH, so we may have to upgrade the circuit with an additional current limiter circuit and also some modification in the relay wiring…..

Reply
Ramsreevasanth
October 10, 2013 • 13 years ago #16052

What modification you mean sir ? How can i modify this circuit to charge a 60 Ah battery bank effectively ? Can i use your one of previous post on ' 3 stage smart battery charger for 12 V ' with this.circuit ? What modifications to be done sir ?

Reply
SwagatamAdmin
October 11, 2013 • 13 years ago #16086

a simpler approach would be to add a calculated current limiting resistor in series with D6

Reply
Ramsreevasanth
October 10, 2013 • 13 years ago #16055

Dear sir,
Can you please give a model current limiting circuit to fullfill my need ? Can i have it to be used prior to the rectification section ? Thereby i can avoid using high ampere diodes there. that is why

Reply
Ramsreevasanth
October 10, 2013 • 13 years ago #16056

Another doubt too sir,
If i am using battery rated below 100 Ah along with the current limiting circuit , will it be possible for the inverter to run maximum load that i am expecting with ?

Reply
SwagatamAdmin
October 11, 2013 • 13 years ago #16087

As mentioned in the previous comment, the series resistor with D6 will not interfere with inverter power outputs, it will work with the specified full capacity

Reply
Adeleke Abiola Benjamin
October 18, 2013 • 13 years ago #16439

Thank you so much for this post. I will like to give you feed back after I complete the work and I will also prefer to know about circuit diagram.

Kindly, let me ask this question.
1. Is it possible to use this circuit with 24volts battery without any damage to the cell of the circuit?

Reply
SwagatamAdmin
October 18, 2013 • 13 years ago #16446

Yes, 24V can be used, provided the transformer and the relays are also rated at 24V.

Reply
Adeleke Abiola Benjamin
October 18, 2013 • 13 years ago #16443

Hi Swag,
is it possible to use transformer with 6v – 0 – 6v and if yes what will be the output of it?

Thanks.

Reply
SwagatamAdmin
October 19, 2013 • 13 years ago #16468

Hi Adeleke,

it would work with a 6V battery…output would be equal to the output rating of the transformer, if it's 220v then it would generate 220V

Reply
Venkitesh krishna
October 26, 2013 • 13 years ago #16702

Hai sir,
Can i ask you something……
What modification to be done to the present circuit if i am using high current transformer ??
A series current limiting resistor alone will not do this purpose i think. What extra things to be added to the oscillation section to prevent ir from accidental damage due to high current flow. Also i want to know the necessary changes to be made on relay wiring also. Please try to REPLY MY ALL QUESTIONS SIR

Reply
SwagatamAdmin
October 26, 2013 • 13 years ago #16713

Hi Venkitesh,

I'll try to find some appropriate solution and update it soon.

Reply
Prithviraj singh
November 6, 2013 • 13 years ago #17024

Hai sir it is again prithviraj speaking…..
A serious doubt is now disturbing me….
As per your suggestion, the inverter o/p after successful testing can be connected directly to the ac wall outlet. But in this inverter schematics, the relay coils are actuated by the ac mains. So if i am gonna follow my strategy, will the relay actuate on getting supply during inverter operation and continously turn ON and OFF ?????

Reply
SwagatamAdmin
November 6, 2013 • 13 years ago #17028

Hi Prithviraj,

You are right, the above inverer cannot be inserted in the wall socket, because the relays would start vibrating ON/OFF due to the particular configuration employed in the circuit.

Reply
Prithviraj singh
November 6, 2013 • 13 years ago #17034

Thank you Sir for replying me fast. Now i want to know whether any modification can be done to the present structure to suit my need or can you suggest any other design for me. I know i am disturbing you a lot. But what to do, i willn't get a better sleep if the problem is kept unsolved….
I am not at all interested in connecting appliances directly to inverter terminal out, because it will cause discomfort in turning a particular device on at a room

Reply
SwagatamAdmin
November 7, 2013 • 13 years ago #17046

I am sorry Prithviraj, there's no possible way out with the above circuit We can consider a manual option using DPDT switch for the changeovers.

Reply
Prithviraj singh
November 7, 2013 • 13 years ago #17052

Sir i think it is possible to solve the issue by any of these,,,,,,,,
What about using a descriminator circuit to distinguish the sinewave from the square wave( which is produced by the inverter ) and actuating the relay only on sine wave, i.e, during mains is present.
Another way i think, is to slightly make a change to the existing frequency of square wave ( which is 50 Hz ) and thereby identifying the power on condition by counting frequency of the incoming signal to the relay coil fed.

But i don't know how this will take effect or will be effective and also don't know how to arrange these modifications. ….. So can you please help me

Reply
SwagatamAdmin
November 8, 2013 • 13 years ago #17080

I don't think that would help, in that case when the mains comes back it will first clash with the inverter AC and cause undesirable things to happen, a fire, a blown fuse etc. because once the the inverter AC gets into the wall socket it's bound to mix with the mains AC unless a DPDT is employed for isolating the respective ACs manually

Reply
Rishikesh
November 27, 2013 • 13 years ago #17558

Hellow sir, how did you calculate the value of resistors and capacitors incorporating the AMV stage of two.coupled transistors. I have to place available and suitable components there

Reply
SwagatamAdmin
November 27, 2013 • 13 years ago #17573

Hello Rishikesh,

you can use the following formula
f = 1/1.4CR. where C = C1 = C2, and R = R1 = R2

R will be be in OHMs and C in FARADS

Reply
ifeanyi anthony nwaobasi
December 3, 2013 • 13 years ago #17778

If the relay fails, won't it be dangerous to the inverter?

Reply
SwagatamAdmin
December 4, 2013 • 13 years ago #17792

yes it could be dangerous, we can include a safety fuse for that in the circuit

Reply
Agbadu Sesugh
December 6, 2013 • 13 years ago #17869

hello Swagatam,
I interested in this circuit diagram but being novice, I'm finding difficult to understand the connect basically the operation of dpdt relay.
how many relays are required in this circuit diagram and how do I connect it pls
Thanks

Reply
SwagatamAdmin
December 7, 2013 • 13 years ago #17887

Hello Agbadu,

If you are new in the field please do not try this circuit, it's strictly for the experts.

2nos DPDT relays are used in this circuit.

Reply
Agbadu Sesugh
December 9, 2013 • 13 years ago #17982

but pls sir can you explain the charging section relay connection for me
also can this circuit be converted to 2.5kva, if yes how?
Thanks

Reply
SwagatamAdmin
December 10, 2013 • 13 years ago #18003

I have already explained it in the article, if you have a specific doubt you can ask it.

if the above basic model is confirmed then it can be modified for 2kva also.

Reply
Kolley
April 8, 2014 • 12 years ago #21299

Sir, tanks for the post
Pls I don't get how to connect RL2 to the two mosfet since one Relay is specified for the two I can only connection one successfully. Pls help explain

Reply
SwagatamAdmin
April 9, 2014 • 12 years ago #21314

RL2 could be a DPDT type relay having two sets of contacts but a single coil controlling both the contacts simultaneously

Reply
Kolley
April 10, 2014 • 12 years ago #21349

Thanks, try to DPDT type Relay

Reply
Kolley
April 10, 2014 • 12 years ago #21351

Hi sir, I'm unable to lay me hand on DPDT type relay, can I use 4 SPDT relay instead of DPDT relay, pls quick reply will be appreciated, thanks

Reply
SwagatamAdmin
April 11, 2014 • 12 years ago #21385

Hi kolley, yes that will also do.

Reply
Kolley
April 11, 2014 • 12 years ago #21392

Thanks

Reply
Kolley
April 13, 2014 • 12 years ago #21436

Hi Swagatam, thanks for the he'll so far. Pls which capacitor can I use instead of C1,C2,C3 and C6 am unable to get those capacitors here. Thanks

Reply
SwagatamAdmin
April 14, 2014 • 12 years ago #21451

Hi Kolley,

the capacitor values cannot be changed, so you'll have to use as suggested.

the ones which are polarized need to be electrolytic while the others metallized polyester type.

please note that this project is not for the newbies and requires expert knowledge in the field…the circuit has the potentials of causing fire hazard and explosion if not done correctly.

Reply
Kolley
April 19, 2014 • 12 years ago #21620

Hello sir, I just finished testing the circuit,am having two problem,1.the mosfet get hot immediately I connect to d battery power and the wire that come from transformer spark to the extent of getting burnt when I connect it to + side of d battery.2 the is turns on and off repeatedly when I connect it to AC supply pls what can I do to rectify these problems.thanks. Pls a quick reply will be appreciated

Reply
SwagatamAdmin
April 20, 2014 • 12 years ago #21633

Kolley, you have surely done something terribly wrong with the connections which I cannot diagnose from here.

remove the relays and make the inverter separately first, as given in this article:

https://www.homemade-circuits.com/2012/09/mini-50-watt-mosfet-inverter-circuit.html

use a separate transformer for charging the battery, the above circuit is not suitable for newcomers.

Reply
hamza siddiqui
April 29, 2014 • 12 years ago #21898

Dear Swagatam ,
I had a home inverter which i was using for charging my car battery. One day by mistake i left battery charging wires on floor ,after that i see no voltage in battery charging wires. I checked the main Ac fuse of inverter ,it is ok but one warning sticker is there on inverter that avoid shorting of charging wires other wise its DC fuse will blow . Kindly give some information on indian make inverters DC fuse location . Inverter make is Reliable . It has only one PCB on charging side supply is going to charging wires through heat sink having 4 MODFET each side.

Reply
SwagatamAdmin
April 30, 2014 • 12 years ago #21925

Dear Hamza,

I am sorry, it'll be difficult to provide a proper suggestion regarding this since the configuration may be different for different inverters and I haven't yet opened the brand that you have mentioned.
However a fuse in any inverter will be always in series with the battery line and also could be with the output AC line, you can investigate these two positions, I am sure you would easily locate a few across these lines.

Reply
sadananda naik
May 18, 2014 • 12 years ago #22611

the relays are 12V , in Fig. it is directly connected to mains, pls explain

Reply
SwagatamAdmin
May 19, 2014 • 12 years ago #22637

the right hand side contacts are connected with mains, the coils are connected via C6

Reply
View Older Comments

Need Help? Please Leave a Comment! We value your input—Kindly keep it relevant to the above topic! Cancel reply

Your email address will not be published. Required fields are marked *

Primary Sidebar



My Youtube Channel

Circuit Simulator

circuit simulator image



Subscribe to get New Circuits in your Email



Categories

  • Arduino Projects (95)
  • Audio and Amplifier Projects (134)
  • Automation Projects (18)
  • Automobile Electronics (103)
  • Battery Charger Circuits (88)
  • Datasheets and Components (109)
  • Electronics Theory (149)
  • Energy from Magnets and Earth (40)
  • Games and Sports Projects (11)
  • Grid and 3-Phase (20)
  • Health related Projects (27)
  • Home Electrical Circuits (13)
  • Indicator Circuits (16)
  • Inverter Circuits (100)
  • Lamps and Lights (162)
  • Meters and Testers (72)
  • Mini Projects (28)
  • Motor Controller (68)
  • Oscillator Circuits (28)
  • Pets and Pests (15)
  • Power Supply Circuits (91)
  • Remote Control Circuits (50)
  • Security and Alarm (65)
  • Sensors and Detectors (107)
  • SMPS and Converters (45)
  • Solar Controller Circuits (61)
  • Temperature Controllers (43)
  • Timer and Delay Relay (50)
  • Voltage Control and Protection (44)
  • Water Controller (37)
  • Wireless Circuits (31)



Other Links

  • Privacy Policy
  • Cookie Policy
  • Disclaimer
  • Copyright
  • Videos
  • Sitemap

People also Search

555 Circuits | 741 Circuits | LM324 Circuits | LM338 Circuits | 4017 Circuits | Ultrasonic Projects | SMPS Projects | Christmas Projects | MOSFETs | Radio Circuits | Laser Circuits | PIR Projects |



Recent Comments

  • Swagatam on DPDT Relay Working, Pinouts, Testing Explained
  • Swagatam on How to Modify SMPS for Adjustable Current and Voltage Output
  • Swagatam on Pure Sine Wave Inverter Circuit Using IC 4047
  • Nare Mashiachidi on DPDT Relay Working, Pinouts, Testing Explained
  • Nare Mashiachidi on DPDT Relay Working, Pinouts, Testing Explained

Social Profiles

  • Twitter
  • YouTube
  • Instagram
  • Pinterest
  • My Facebook-Page
  • Stack Exchange
  • Linkedin

© 2026 · Swagatam Innovations