You are here: Home / Home Electrical Circuits / Build a 2-Stage Mains Power Stabilizer Circuit – Whole House

Build a 2-Stage Mains Power Stabilizer Circuit – Whole House

Last Updated on December 31, 2018 by Swagatam 20 Comments

In this article we learn how to make a 2 relay or two stage voltage stabilizer circuit for controlling and regulating 220V or 120V mains voltages through a simple circuit.

Introduction

In this power stabilizer circuit, one relay is wired to select the high or the low tap from the stabilizer transformer at some particular voltage level; whereas the second relay keeps the normal mains voltage switched in, but the moment there’s a voltage fluctuation it toggles and selects the appropriate HOT tap via the first relay contacts.

A simple power stabilizer circuit discussed here is very easy to build and yet is able to provide a 2-stage correction of the input mains.

A simple method of converting a normal transformer into a stabilizer transformer has also been discussed using circuit schematics.

Circuit Operation

As shown in the adjoining figure, the whole circuit operation can be understood with the following points:

2-Stage Mains Power Stabilizer

Basically the idea here is to make relay #1 switch at two different mains voltage extremes (high and low), which are considered not suitable for the appliances.

This switching enables this relay to select an appropriately conditioned voltage from another relay through its N/C contacts.

How to Wire the Relay Contacts

The contacts of this second relay #2 makes it sure that it selects a appropriate voltages from the stabilizer transformer and keeps it ready for the relay #1 whenever it toggles during dangerous voltage levels. At normal voltages, relay #1 remains activated and selects the normal voltage through its N/O contacts.

Transistor T1 and T2 are used as voltage sensors. Relay #1 is connected to this configuration at the collector of T2.

As long as the voltage is normal, T1 stays switched off. Consequently T2 at this moment remains switched on. Relay #1 is activated, and its N/O contacts connect the NORMAL AC to the appliance.

If the voltage tends to rise, T1 slowly conducts, and at a certain level (decided by the setting of P1), T1 fully conducts and shuts off T2 and relay #1.

The relay immediately connects the corrected (lowered) voltage supplied by relay #2 through its N/C contacts to the output.

Now, in case of a low voltage T1 and T2 both will stop conducting, producing the same result as above, but this time the supplied voltage from relay #2 to relay #1 will be high, so that the output receives the required corrected level of voltage.

Relay #2 is energized by T3 at a particular voltage level (as per the setting of P3) in between the two voltage extremes. Its contacts are wired to the stabilizer transformer tapping so that it selects the desired voltage appropriately.

How to Assemble the Circuit

The construction of this circuit is very simple. It may be done by with the following steps:

Cut a small piece of a general purpose board (about 10 by 5 mm).

Begin the construction by inserting the transistors first, keeping ample space between them so that the other can be accommodated around each of them. Solder and cut off their leads.

Next, insert the rest of the components and interlink them with each other and the transistors by soldering. Take the help of the circuit schematic for their proper orientations and placements.

Finally, fix the relays to complete the board assembly.

The next page deals with the construction of the power stabilizer transformer and the testing procedure. After these procedures are completed, you may integrate the tested circuit assembly to the appropriate transformers.

The whole set up then may be housed inside a tough metal enclosure and installed for the desired operations.
Parts List

R1, R2, R3 = 1K, 1/4W,

P1, P2,P3 = 10K, LINEAR PRESETS,

C1 = 1000uF/25V

Z1, Z2, Z3 = 3V, 400mW ZENER DIODE,

T1, T2,T3 = BC 547B,

RL1, RL2= RELAY 12V,SPDT,400 OHMS,

D1--D4 =1N4007,

TR1 =0-12V, 500mA,

TR2 = 25- 0 - 25 VOLTS, 5 AMPS. WITH SPLIT CENTER TAP,GENERAL PCB,METALLIC ENCLOSURE, MAINS CORD, SOCKET, FUSE HOLDER ETC

How to Convert an Ordinary Transformer into a Stabilizer Transformer

 

Convert an Ordinary Transformer into a Stabilizer Transformer

Stabilizer transformers are normally made to order and are not available ready made in the market. Since multiple mains AC voltage taps (high and low) outputs are required from them and also since these are specific for a particular application, it becomes much difficult to procure them ready made.

The present circuit also needs a power regulator transformer, but for the ease of construction a simple method may be incorporated to convert an ordinary power supply transformer into a voltage stabilizer transformer.

As shown in the figure, here we require a normal transformer rated at 25-0-25/ 5 Amp. The centre tap should be split, so that the secondary may consist of two separate windings. Now it’s just a matter of connecting the primary wires to the two secondary windings as shown in the diagram.

Thus, by following the above procedure, you should be able to successfully convert an ordinary transformer into a stabilizer transformer, very handy for the present application.

How to Set Up the Unit

You will require a variable 0-24V/500mA power supply for the set up procedure. It may be completed with the following steps:

Since we know that the AC mains voltages fluctuations will always create a proportionate magnitude of the DC voltage fluctuations from a transformer, we may assume that for input voltages of 210, 230 and 250, the correspondingly obtained equivalent DC voltages should be 11.5, 12.5 and 13.5 respectively.

Now the setting of the relevant presets becomes very simple as per the above voltage levels.

  • Initially keep the both the transformers TR1 and TR2 disconnected from the circuit.
  • Keep the slider of P1, P2, and P3 at somewhere around midway position.
  • Connect the external variable power supply to the circuit. Adjust the voltage to about 12.5.
  • Now slowly start adjusting P3 until RL2 just activates.
  • Decrease the supply voltage to about 11.5 volts (RL2 should deactivate in the course), adjust P1 so that RL1 just deactivates.
  • Gradually increase the supply to about 13.5 – this should make RL1 and RL2 to energize one after the other, indicating the correctness of the above settings.
  • Now slowly adjust P2 so that RL1 again deactivates at this voltage (13.5).
  • Confirm the above settings by varying the input voltage from 11.5 to 13.5 back and forth. You should get the following results:
  • RL1 should deactivate at 11.5 and 13.5 voltage levels, but should remain activated in between these voltages. RL2 should switch ON above 12.5 and switch off below 12 volts.

The setting procedure is now complete.

The final construction of this power regulator unit may be concluded by connecting the tested circuit with the relevant transformers and concealing the whole section inside a well ventilated metallic enclosure as suggested in the previous page.




Previous: 5 Interesting Flip Flop Circuits – Load ON/OFF with Push-Button
Next: Cell Phone Controlled Door Lock Circuit

About Swagatam

I am an electronic engineer (dipIETE ), hobbyist, inventor, schematic/PCB designer, manufacturer. I am also the founder of the website: https://www.homemade-circuits.com/, where I love sharing my innovative circuit ideas and tutorials.
If you have any circuit related query, you may interact through comments, I'll be most happy to help!

You'll also like:

  • 1.  How to Test a MOV (Metal Oxide Varistor) Surge Protector Device
  • 2.  Mains AC Overload protection Circuit for Voltage Stabilizers
  • 3.  Simple Water Heater Alarm Circuit
  • 4.  Emergency Generator Circuit Power Distribution
  • 5.  Simple Refrigerator Protector Circuit
  • 6.  Room Air Ionizer Circuit – For Pollution Free Living

Please Subscribe (Only if you are Genuinely Interested in our Newsletters)


 

Reader Interactions

Comments

    Your Comments are too Valuable! But please see that they are related to the above article, and are not off-topic! Cancel reply

    Your email address will not be published. Required fields are marked *

  1. Search Related Posts for Commenting

  2. selva says

    Will the stabilizer gives accurate output voltage (like 220 V ) or output voltage of certain range (like 215-230 V) of varying input voltage

    Reply
    • Swagatam says

      It will not give exact 220V, rather within a certain range

      Reply
  3. Usa Juana says

    hello sir . i build this circuit and it works. but during setting up the first step at 12.5 volts worked ,while adjusting p3 relay 2 activated at 11.5 relay 1 deactivated also. adjusting power from 11.5-13.5 activated both relays simultaneously. now the problem is,at 13.5 relay1 remain activated . i adjusted p2 end to end no change . how ever at lower volts say 11.8 p2 deactivated relay1 but is not working at the right place 13.5 . please can u assist me rectify the problem?

    Reply
    • Swagatam says

      USA, while adjusting the power supply pot the voltage could rise or fall abruptly due to pot inefficiency and hand inaccuracy and this could produce random relay activation.

      you must adjust the pot very very slowly and skillfully to actually see the relay sequence in the correct way.

      connect LEDs in series with each of the transistor emitters, this will help you to see the changeovers visually.

      the circuit is too straightforward and I don't think it needs much explanation or any critical troubleshooting.

      Reply
  4. ayman bakr says

    Hi Sir,

    can this stabilizer be connected to the main house power source, I main can I use it to the whole house, sorry if my question seems stupid but I'm very new to power circuits
    thanks

    Reply
    • Swagatam says

      Hi ayman,

      yes it can be used for a house or even for the entire building, the circuit just needs to be upgraded accordingly.

      The relay and the transformer needs to be upgraded with appropriate wattage rating so that it can safely handle the connected load current

      Reply
    • ayman bakr says

      Hi Swagatam,

      Thank you for your reply and for the efforts you do to help us Improve our hobby

      what do you advice for the upgraded relay and transformer (the house is 220V, and I have Air condition, two refrigerators, 3 TV's , 2 water heaters , 2 electric ovens) this is all the appliances in my house, please suggest what is the relay and transformer proper wattage I should use
      thanks

      Reply
    • Swagatam says

      Hi Ayman,

      divide the total wattage of the loads with 220, and multiply the result with 2…that will provide you the required relay contact rating, the transformer wattage will need to be twice that of the total wattage of the load

      Reply
    • ayman bakr says

      Hi Swagatam,

      The house total wattage load = 15499/220 * 2 =140.9
      the relay I have 7A 250VAC | 10A 125VAC
      12A 120VAC | 10A 28VDC
      (what should be mentioned on the relay that I have to use )??

      which transformer I should upgrade TR1 or TR2 (the transformers I have TR1 = 0-12V, 500mA, TR2 = 24 – 0 – 24 VOLTS, 5 AMPS
      ( what I should use)??

      Sorry for asking many questions but I hope to build a perfect stabilizer with your help
      thanks and regards

      Reply
    • Swagatam says

      Hi ayman,

      for a 15000+ watt load the relay contact must be rated at above 100 amps…so 10amp is out of question…it's nowhere near.

      TR2 is the one which need to be upgraded…and it should be rated at around 20,000 watts to safely handle 15000 watt load.

      Reply
  5. Don Corleon says

    Your description: "…..T1 fully conducts and shuts off T1 and relay #1."

    I think it should be: "…..T1 fully conducts and shuts off T2 and relay #1."

    Regards,
    Don

    Reply
    • Swagatam says

      OK thanks, I'll correct the typo soon.

      Reply
  6. Wazir Ahmad says

    plz send 4-relay stabilizer circuit with delay timer if possible ,regards.
    ch wazir.

    Reply
    • Swagatam says

      try the following circuit, use only 4 stages out of the shown 7 stages:

      https://homemade-circuits.com/2011/12/how-to-make-accurate-7-stage-op-amp.html

      Reply
  7. Swagatam says

    yes surely you can, Oliver

    Reply
  8. oliver oliveros says

    Hi Swagatam,

    now i can use my contactors… thank you very much.

    Regards,
    Oliver

    Reply
  9. Swagatam says

    Hi Oliver, yes only a transformer would sufficient for your requirement, wire it up as shown in the second diagram.

    Reply
  10. oliver oliveros says

    Hi Swagatam,

    only the trafo without the circuit will do?

    Thanks,
    Oliver

    Reply
  11. Swagatam says

    Hi Oliver,

    you need an approximately fixed and constant 200V for your contactor unit, right?

    So you would need only a transformer wired accordingly for getting the required 200V output, as given in the second design.

    In the second design, the lower section could be used for your application.

    Actually, since you require a step down voltage only, the upper 0-25V winding becomes meaningless, so may be only a 0-25V transformer could be just enough.

    Reply
  12. oliver oliveros says

    Hi Swagatam,

    How can i use this to my 200V contactor? how will i adjust the voltage?

    for TR1… can i use transformerless power supply?

    can i use 24-0-24 for TR2?

    Regards,
    Oliver

    Reply


  13. COMMENT BOX IS MOVED AT THE TOP


Primary Sidebar

Electronic Projects Categories

  • 3-Phase Power (15)
  • 324 IC Circuits (19)
  • 4017 IC Circuits (51)
  • 4060 IC Circuits (25)
  • 555 IC Circuits (92)
  • 741 IC Circuits (18)
  • Amplifiers (49)
  • Arduino Engineering Projects (82)
  • Audio Projects (84)
  • Battery Chargers (75)
  • Car and Motorcycle (87)
  • Datasheets (45)
  • Decorative Lighting (Diwali, Christmas) (31)
  • DIY LED Projects (81)
  • Electronic Components (97)
  • Electronic Devices and Circuit Theory (35)
  • Electronics Tutorial (99)
  • Fish Aquarium (5)
  • Free Energy (34)
  • Games (2)
  • GSM Projects (9)
  • Health Related (17)
  • Heater Controllers (23)
  • Home Electrical Circuits (98)
  • Incubator Related (6)
  • Industrial Electronics (26)
  • Infrared (IR) (39)
  • Inverter Circuits (94)
  • Laser Projects (10)
  • LM317/LM338 (21)
  • LM3915 IC (24)
  • Meters and Testers (54)
  • Mini Projects (153)
  • Motor Controller (64)
  • MPPT (7)
  • Oscillator Circuits (12)
  • PIR (Passive Infrared) (8)
  • Power Electronics (33)
  • Power Supply Circuits (66)
  • Radio Circuits (9)
  • Remote Control (46)
  • Security and Alarm (56)
  • Sensors and Detectors (115)
  • SG3525 IC (5)
  • Simple Circuits (72)
  • SMPS (30)
  • Solar Controllers (60)
  • Timer and Delay Relay (51)
  • TL494 IC (5)
  • Transformerless Power Supply (8)
  • Transmitter Circuits (38)
  • Ultrasonic Projects (12)
  • Water Level Controller (45)

Follow Homemade Circuits

Facebook
Twitter
YouTube
Instagram
My Facebook-Page
Quora

Feeds

Post RSS
Comment RSS

Circuit Calculators

  • AWG to Millimeter Converter
  • Battery Back up Time Calculator
  • Capacitance Reactance Calculator
  • IC 555 Astable Calculator
  • IC 555 Monostable Calculator
  • Inductance Calculator
  • LC Resonance Calculator
  • LM317, LM338, LM396 Calculator
  • Ohm’s Law Calculator
  • Phase Angle Phase Shift Calculator
  • Power Factor (PF) Calculator
  • Reactance Calculator
  • Small Signal Transistor(BJT) and Diode Quick Datasheet
  • Transistor Astable Calculator
  • Transistor base Resistor Calculator
  • Voltage Divider Calculator
  • Wire Current Calculator
  • Zener Diode Calculator

© 2021 · Swagatam Innovations