In this article I have explained how to make a 2 relay or two stage mains AC voltage stabilizer circuit for controlling and regulating 220V or 120V mains voltages through a simple circuit.

Table of Contents
  • Introduction
  • Circuit Operation
  • How to Wire the Relay Contacts
  • How to Assemble the Circuit
  • Parts List
  • How to Convert an Ordinary Transformer into a Stabilizer Transformer
  • How to Set Up the Unit

Introduction

In this power stabilizer circuit, one relay is wired to select the high or the low tap from the stabilizer transformer at some particular voltage level; whereas the second relay keeps the normal mains voltage switched in.

However, the moment there’s a voltage fluctuation it toggles and selects the appropriate HOT tap via the first relay contacts.

A simple power stabilizer circuit discussed here is very easy to build and yet is able to provide a 2-stage correction of the input mains.

A simple method of converting a normal transformer into a stabilizer transformer has also been discussed using circuit schematics.

Circuit Operation

As shown in the adjoining figure, the whole circuit operation can be understood with the following points:

warning message: electricity is dangerous, proceed with caution
2-Stage Mains Power Stabilizer circuit diagram

Basically the idea here is to make relay #1 switch at two different mains voltage extremes (high and low), which are considered not suitable for the appliances.

This switching enables this relay to select an appropriately conditioned voltage from another relay through its N/C contacts.

How to Wire the Relay Contacts

The contacts of this second relay #2 makes it sure that it selects a appropriate voltages from the stabilizer transformer and keeps it ready for the relay #1 whenever it toggles during dangerous voltage levels.

At normal voltages, relay #1 remains activated and selects the normal voltage through its N/O contacts.

Transistor T1 and T2 are used as voltage sensors. Relay #1 is connected to this configuration at the collector of T2.

As long as the voltage is normal, T1 stays switched off. Consequently T2 at this moment remains switched on. Relay #1 is activated, and its N/O contacts connect the NORMAL AC to the appliance.

If the voltage tends to rise, T1 slowly conducts, and at a certain level (decided by the setting of P1), T1 fully conducts and shuts off T2 and relay #1.

The relay immediately connects the corrected (lowered) voltage supplied by relay #2 through its N/C contacts to the output.

Now, in case of a low voltage T1 and T2 both will stop conducting, producing the same result as above.

However, this time the supplied voltage from relay #2 to relay #1 will be high, so that the output receives the required corrected level of voltage.

Relay #2 is energized by T3 at a particular voltage level (as per the setting of P3) in between the two voltage extremes.

Its contacts are wired to the stabilizer transformer tapping so that it selects the desired voltage appropriately.

How to Assemble the Circuit

The construction of this circuit is very simple. It may be done by with the following steps:

Cut a small piece of a general purpose board (about 10 by 5 mm).

Begin the construction by inserting the transistors first, keeping ample space between them so that the other can be accommodated around each of them. Solder and cut off their leads.

Next, insert the rest of the components and interlink them with each other and the transistors by soldering. Take the help of the circuit schematic for their proper orientations and placements.

Finally, fix the relays to complete the board assembly.

The next page deals with the construction of the power stabilizer transformer and the testing procedure. After these procedures are completed, you may integrate the tested circuit assembly to the appropriate transformers.

The whole set up then may be housed inside a tough metal enclosure and installed for the desired operations.

Parts List

  • R1, R2, R3 = 1K, 1/4W,
  • P1, P2,P3 = 10K, LINEAR PRESETS,
  • C1 = 1000uF/25V
  • Z1, Z2, Z3 = 3V, 400mW ZENER DIODE,
  • T1, T2,T3 = BC 547B,
  • RL1, RL2= RELAY 12V,SPDT,400 OHMS,
  • D1--D4 =1N4007,
  • TR1 =0-12V, 500mA,
  • TR2 = 25- 0 - 25 VOLTS, 5 AMPS. WITH SPLIT CENTER TAP,GENERAL PCB,METALLIC ENCLOSURE, MAINS CORD, SOCKET, FUSE HOLDER ETC

How to Convert an Ordinary Transformer into a Stabilizer Transformer

Convert an Ordinary step down Transformer into a Stabilizer Transformer

Stabilizer transformers are normally made to order and are not available ready made in the market.

Since multiple mains AC voltage taps (high and low) outputs are required from them and also since these are specific for a particular application, it becomes much difficult to procure them ready made.

The present circuit also needs a power regulator transformer, but for the ease of construction a simple method may be incorporated to convert an ordinary power supply transformer into a voltage stabilizer transformer.

As shown in the figure, here we require a normal transformer rated at 25-0-25/ 5 Amp.

The center tap should be split, so that the secondary may consist of two separate windings. Now it’s just a matter of connecting the primary wires to the two secondary windings as shown in the diagram.

Thus, by following the above procedure, you should be able to successfully convert an ordinary transformer into a stabilizer transformer, very handy for the present application.

How to Set Up the Unit

You will require a variable 0-24V/500mA power supply for the set up procedure. It may be completed with the following steps:

Since we know that the AC mains voltages fluctuations will always create a proportionate magnitude of the DC voltage fluctuations from a transformer, we may assume that for input voltages of 210, 230 and 250, the correspondingly obtained equivalent DC voltages should be 11.5, 12.5 and 13.5 respectively.

Now the setting of the relevant presets becomes very simple as per the above voltage levels.

  • Initially keep the both the transformers TR1 and TR2 disconnected from the circuit.
  • Keep the slider of P1, P2, and P3 at somewhere around midway position.
  • Connect the external variable power supply to the circuit. Adjust the voltage to about 12.5.
  • Now slowly start adjusting P3 until RL2 just activates.
  • Decrease the supply voltage to about 11.5 volts (RL2 should deactivate in the course), adjust P1 so that RL1 just deactivates.
  • Gradually increase the supply to about 13.5 – this should make RL1 and RL2 to energize one after the other, indicating the correctness of the above settings.
  • Now slowly adjust P2 so that RL1 again deactivates at this voltage (13.5).
  • Confirm the above settings by varying the input voltage from 11.5 to 13.5 back and forth. You should get the following results:
  • RL1 should deactivate at 11.5 and 13.5 voltage levels, but should remain activated in between these voltages. RL2 should switch ON above 12.5 and switch off below 12 volts.

The setting procedure is now complete.

The final construction of this power regulator unit may be concluded by connecting the tested circuit with the relevant transformers and concealing the whole section inside a well ventilated metallic enclosure as suggested in the previous page.

You'll also like:

  • 1.  High Power Industrial Mains Surge Suppressor Explored
  • 2.  Grid Transformer Fire Hazard Protector Circuit
  • 3.  SG 3525 Automatic PWM Voltage Regulation Circuit
  • 4.  Automatic Voltage Stabilizer Circuit for TV sets and Refrigerator
  • 5.  TPS24710/11/12/13 Hot-Swap Controller Circuit Explained
  • 6.  Transformerless Voltage Stabilizer Circuit

About Swagatam

I am an electronics engineer with over 15 years of hands-on experience. I am passionate about inventing, designing electronic circuits and PCBs, and helping hobbyists bring their projects to life. That is why I founded homemade-circuits.com, a website where I share innovative circuit ideas and tutorials. Have a circuit related question? Leave a comment.... I guarantee a reply!

Previous Post: « 5 Interesting Flip Flop Circuits – Load ON/OFF with Push-Button
Next Post: Mobile Phone Controlled Door Lock Circuit »

Reader Interactions

Comments

  1. Moses says

    December 13, 2021 at 4:52 pm

    THANKS FOR THIS GREAT LECTURE. NOW MY QUESTION IS THIS; FROM THE CONFIGURATION PROVIDED ASSUMING THAT THE STABILIZER IS REQUIRED WORKING WHEN AC MAINS DROPS TO 160VOLTS HOW DO WE SET UP THE PRESET. I HOPE THAT IS REALLY POSSIBLE FOR THE CIRCUIT PROVIDED AND THE TRANSFORMER RATINGS. THANKS!

    Reply
    • Swagatam says

      December 13, 2021 at 7:24 pm

      Glad you liked it, you will have to carefully adjust the preset 3 so that it switches OFF RL2 at 180V, adjust preset 2 so that it switches OFF RL1 at 170V

      Reply
  2. selva says

    December 3, 2020 at 10:52 am

    Will the stabilizer gives accurate output voltage (like 220 V ) or output voltage of certain range (like 215-230 V) of varying input voltage

    Reply
    • Swagatam says

      December 3, 2020 at 11:25 am

      It will not give exact 220V, rather within a certain range

      Reply
  3. Usa Juana says

    July 22, 2016 at 7:50 pm

    hello sir . i build this circuit and it works. but during setting up the first step at 12.5 volts worked ,while adjusting p3 relay 2 activated at 11.5 relay 1 deactivated also. adjusting power from 11.5-13.5 activated both relays simultaneously. now the problem is,at 13.5 relay1 remain activated . i adjusted p2 end to end no change . how ever at lower volts say 11.8 p2 deactivated relay1 but is not working at the right place 13.5 . please can u assist me rectify the problem?

    Reply
    • Swagatam says

      July 23, 2016 at 4:04 am

      USA, while adjusting the power supply pot the voltage could rise or fall abruptly due to pot inefficiency and hand inaccuracy and this could produce random relay activation.

      you must adjust the pot very very slowly and skillfully to actually see the relay sequence in the correct way.

      connect LEDs in series with each of the transistor emitters, this will help you to see the changeovers visually.

      the circuit is too straightforward and I don't think it needs much explanation or any critical troubleshooting.

      Reply
  4. ayman bakr says

    August 9, 2015 at 1:49 am

    Hi Sir,

    can this stabilizer be connected to the main house power source, I main can I use it to the whole house, sorry if my question seems stupid but I'm very new to power circuits
    thanks

    Reply
    • Swagatam says

      August 9, 2015 at 9:32 am

      Hi ayman,

      yes it can be used for a house or even for the entire building, the circuit just needs to be upgraded accordingly.

      The relay and the transformer needs to be upgraded with appropriate wattage rating so that it can safely handle the connected load current

      Reply
    • ayman bakr says

      August 11, 2015 at 8:36 am

      Hi Swagatam,

      Thank you for your reply and for the efforts you do to help us Improve our hobby

      what do you advice for the upgraded relay and transformer (the house is 220V, and I have Air condition, two refrigerators, 3 TV's , 2 water heaters , 2 electric ovens) this is all the appliances in my house, please suggest what is the relay and transformer proper wattage I should use
      thanks

      Reply
    • Swagatam says

      August 11, 2015 at 2:15 pm

      Hi Ayman,

      divide the total wattage of the loads with 220, and multiply the result with 2…that will provide you the required relay contact rating, the transformer wattage will need to be twice that of the total wattage of the load

      Reply
    • ayman bakr says

      August 12, 2015 at 7:49 am

      Hi Swagatam,

      The house total wattage load = 15499/220 * 2 =140.9
      the relay I have 7A 250VAC | 10A 125VAC
      12A 120VAC | 10A 28VDC
      (what should be mentioned on the relay that I have to use )??

      which transformer I should upgrade TR1 or TR2 (the transformers I have TR1 = 0-12V, 500mA, TR2 = 24 – 0 – 24 VOLTS, 5 AMPS
      ( what I should use)??

      Sorry for asking many questions but I hope to build a perfect stabilizer with your help
      thanks and regards

      Reply
    • Swagatam says

      August 12, 2015 at 4:05 pm

      Hi ayman,

      for a 15000+ watt load the relay contact must be rated at above 100 amps…so 10amp is out of question…it's nowhere near.

      TR2 is the one which need to be upgraded…and it should be rated at around 20,000 watts to safely handle 15000 watt load.

      Reply
  5. Don Corleon says

    May 20, 2015 at 12:18 pm

    Your description: "…..T1 fully conducts and shuts off T1 and relay #1."

    I think it should be: "…..T1 fully conducts and shuts off T2 and relay #1."

    Regards,
    Don

    Reply
    • Swagatam says

      May 21, 2015 at 3:36 am

      OK thanks, I'll correct the typo soon.

      Reply
  6. Wazir Ahmad says

    July 25, 2014 at 8:36 am

    plz send 4-relay stabilizer circuit with delay timer if possible ,regards.
    ch wazir.

    Reply
    • Swagatam says

      July 26, 2014 at 4:09 am

      try the following circuit, use only 4 stages out of the shown 7 stages:

      https://www.homemade-circuits.com/2011/12/how-to-make-accurate-7-stage-op-amp.html

      Reply
      • Moses says

        December 16, 2021 at 11:22 am

        I think the best thing is to disconnect the relay and IC part of the circuit and run ac mains through the input part of TR1 and then read the dc through bridge rectifier and smoothing capacitor network. The dc voltage recorded at a given ac mains voltage value can now be used as reference instead of assuming that 210acv produces 11.5dcv. Is it conventional to assume.

        Reply
        • Swagatam says

          December 16, 2021 at 1:27 pm

          yes that’s correct!

          Reply
  7. Swagatam says

    June 19, 2014 at 4:40 am

    yes surely you can, Oliver

    Reply
  8. oliver oliveros says

    June 18, 2014 at 3:18 pm

    Hi Swagatam,

    now i can use my contactors… thank you very much.

    Regards,
    Oliver

    Reply
  9. Swagatam says

    June 18, 2014 at 4:11 am

    Hi Oliver, yes only a transformer would sufficient for your requirement, wire it up as shown in the second diagram.

    Reply
  10. oliver oliveros says

    June 17, 2014 at 2:59 pm

    Hi Swagatam,

    only the trafo without the circuit will do?

    Thanks,
    Oliver

    Reply
  11. Swagatam says

    June 17, 2014 at 11:36 am

    Hi Oliver,

    you need an approximately fixed and constant 200V for your contactor unit, right?

    So you would need only a transformer wired accordingly for getting the required 200V output, as given in the second design.

    In the second design, the lower section could be used for your application.

    Actually, since you require a step down voltage only, the upper 0-25V winding becomes meaningless, so may be only a 0-25V transformer could be just enough.

    Reply
  12. oliver oliveros says

    June 17, 2014 at 12:04 am

    Hi Swagatam,

    How can i use this to my 200V contactor? how will i adjust the voltage?

    for TR1… can i use transformerless power supply?

    can i use 24-0-24 for TR2?

    Regards,
    Oliver

    Reply
    • Moses says

      December 16, 2021 at 1:31 am

      Decrease the supply voltage to about 11.5 volts (RL2 should deactivate in the course), adjust P1 so that RL1 just deactivates.
      I copied this from your guide in the above circuit. I thought should be adjust p1 so that RL1 activates at 11.5 since it represents the 210acv. Because the referenced statement has it that RL1 gets deactivated when P1 is adjusted at 11.5v dc supply as if it was previously activated before then. Thanks.

      Reply
      • Moses says

        June 28, 2022 at 1:04 am

        The circuit above and the transformer configuration is very comprehensive. My question is in transformers with multiple tappings, 170,190, 210, 230,250 volts and two auxiliary tapings; 0 – 18v, 0 – 18v each. How can the transformer be configured to get the buck and boost effect expected of the stabilizer. I have seen a lot of stabilizers with only a single transformer and so I begin to wonder how the configuration is done to create that effect.

        Reply
        • Swagatam says

          June 28, 2022 at 9:30 am

          In stabilizers with multiple tap transformer, opamps are used to detect the rising or falling voltage levels and in response it activates relays that switch ON the higher voltage taps sequentially when the voltage drops, and when the voltage rises, the lower voltage taps are activated by the respective relays. You can see an example of this type of stabilizer in the following article:
          5 KVA to 10 KVA Automatic Voltage Stabilizer – 220 Volts, 120 Volts

          Reply
          • Moses says

            June 28, 2022 at 9:47 pm

            Yea! After going through your article on the working of opamps using 741 as a case study I now know how such setup is done. Am grateful.

            Reply
            • Swagatam says

              June 29, 2022 at 10:12 am

              You are welcome Moses!

              Reply

Need Help? Please Leave a Comment! We value your input—Kindly keep it relevant to the above topic! Cancel reply

Your email address will not be published. Required fields are marked *

Primary Sidebar

Subscribe to New Circuit Ideas

Categories

  • Arduino Projects (87)
  • Audio and Amplifier Projects (132)
  • Automation Projects (17)
  • Automobile Electronics (101)
  • Battery Charger Circuits (83)
  • Datasheets and Components (104)
  • Electronics Theory (143)
  • Free Energy (37)
  • Games and Sports Projects (11)
  • Grid and 3-Phase (19)
  • Health related Projects (25)
  • Home Electrical Circuits (12)
  • Indicator Circuits (14)
  • Inverter Circuits (87)
  • Lamps and Lights (142)
  • Meters and Testers (69)
  • Mini Projects (46)
  • Motor Controller (64)
  • Oscillator Circuits (27)
  • Pets and Pests (15)
  • Power Supply Circuits (108)
  • Remote Control Circuits (50)
  • Security and Alarm (64)
  • Sensors and Detectors (101)
  • Solar Controller Circuits (59)
  • Temperature Controllers (42)
  • Timer and Delay Relay (49)
  • Transmitter Circuits (29)
  • Voltage Control and Protection (37)
  • Water Controller (36)

Calculators

  • Battery Back up Time Calculator
  • Capacitance Reactance Calculator
  • IC 555 Astable Calculator
  • IC 555 Monostable Calculator
  • Inductance Calculator
  • LC Resonance Calculator
  • LM317, LM338, LM396 Calculator
  • Ohm’s Law Calculator
  • Phase Angle Phase Shift Calculator
  • Power Factor (PF) Calculator
  • Reactance Calculator
  • Transistor Astable Calculator
  • Transistor base Resistor Calculator
  • Voltage Divider Calculator
  • Wire Current Calculator
  • Zener Diode Calculator
  • Filter Capacitor Calculator
  • Buck Converter Calculator
  • Boost Converter Calculator
  • Solar Panel, Inverter, Battery Calculator
  • Wire Current Calculator
  • SMPS Transformer Calculator
  • IC SG3525, SG3524 Calculator
  • Inverter LC Filter Calculator

People Also Search

555 Circuits | 741 Circuits | LM324 Circuits | LM338 Circuits | 4017 Circuits | Ultrasonic Projects | SMPS Projects | Christmas Projects | MOSFETs | Radio Circuits | Laser Circuits | PIR Projects |

Recent Comments

  • Swagatam on 9 Simple Sine Wave Generator Circuits Explored
  • Swagatam on SG3525 Full Bridge Inverter Circuit
  • Swagatam on Timer Based Cell Phone Charger Circuit
  • Alasdair on 9 Simple Sine Wave Generator Circuits Explored
  • Swurvz on SG3525 Full Bridge Inverter Circuit

Company

  • Privacy Policy
  • Cookie Policy
  • About Me
  • Contact
  • Disclaimer
  • Copyright
  • Videos
  • Sitemap

Social Profiles

  • Twitter
  • YouTube
  • Instagram
  • Pinterest
  • My Facebook-Page
  • Quora
  • Stack Exchange
  • Linkedin
  • © 2025 · Swagatam Innovations