Last Updated on January 2, 2024 by Swagatam 106 Comments

In this article I have explained how to make a cheap yet effective mains operated AC overload and over-current protector circuit using very ordinary discrete components.

Introduction

I have published a few mains voltage stabilizer circuits in this blog, these units are designed and intended for safeguarding the connected appliances at their outputs.

However these equipment lack one protection which is the overload protection.

The Importance of an Overload Protection Circuit

A particular stabilizer unit may be rated for handling a maximum specified limit of power, beyond which it's effects may start diluting or might become inefficient.

Overloading a voltage stabilizer might also result in heating of the transformer and fire hazards.

A simple circuit shown below may be incorporated with a stabilizer circuit or any such protection circuit for reinforcing the safeguarding capabilities of the units.

How it Works

The diagram shows a very simple and straightforward configuration where only a couple of transistors and few other passive parts are used for forming the intending design.

The mains stabilized AC is derived from the stabilizer outputs and allowed to switch through another RL1, via its N/C contacts.

One of the wires of the AC mains connections is added with a series resistor of a calculated value.

As the load across the mains output increases, a proportionate magnitude of voltage starts developing across this resistor.

The value of the resistor is so selected that the voltage across it becomes just enough to light up a connected LED in response to a load that might be considered as dangerous and over the maximum tolerable limit.

When this happens, the LED just lights up, an LDR positioned and enclosed in front of the LED instantly drops its resistance in response to the illumination generated by the LDR.

The sudden reduction in the resistance of the LDR, switches ON T1 which in turn switches ON T2 and the relay, initiating the latching effect of the circuit and the relay.

The load or the appliance at the output is thus immediately switched off when an overload situation is detected.

The whole action takes place within a fraction of a second, giving no chance for any untoward consequence and the whole system is safeguarded by the inclusion of this simple AC mains overload protection circuit.

Formula for Calculating Current limiting Resistor

R1 = 1.5 / I(intended current limit),

For example if I =15 amps, then R1 = 1.5/15 = 0.1 Ohms, and it's wattage will be 1.5 x 15 = 22.5 watts

Mains AC Overload protection Circuit for Voltage Stabilizers

Parts List

  • All resistors are 1/4 watt 5% except R1 (see text)
  • R4 = 56 ohms
  • R4, R7 = 1K
  • R5 = 10K
  • R6 = 47K
  • P1 = 100K preset
  • Diodes = All are 1N4007
  • T1 = BC547
  • T2 = BC557
  • C2 = 10uF/25V
  • LD1 = red LED 20 mA
  • Relay = 12 V/200mA 30 amps

The LED/LDR device can be assembled manually as per the following example image

You'll also like:

  • boost converter working modelSimple Boost Converter Circuit Diagrams using Transistors
  • LM324 Operational Amplifier5 KVA to 10 KVA Automatic Voltage Stabilizer – 220 Volts, 120 Volts
  • Explained: Snubber Circuit for MOSFET H-Bridge
  • ntc 2Using an NTC Thermistor as a Surge Suppressor

Filed Under: Voltage Control and Protection Tagged With: AC, Mains, Overload, Protection, Stabilizers, Voltage

About Swagatam

I am an electronics engineer and doing practical hands-on work from more than 15 years now. Building real circuits, testing them and also making PCB layouts by myself. I really love doing all these things like inventing something new, designing electronics and also helping other people like hobby guys who want to make their own cool circuits at home.

And that is the main reason why I started this website homemade-circuits.com, to share different types of circuit ideas..

If you are having any kind of doubt or question related to circuits then just write down your question in the comment box below, I am like always checking, so I guarantee I will reply you for sure!

Previous Post: « 2 Easy Automatic Inverter/Mains AC Changeover Circuits
Next Post: Easiest Single Axis Solar Tracker System »

Reader Interactions

Comments

Godson says:
September 14, 2017 at 8:00 am

Hello sir Swagatam,
Please I have one more question on this schematic. Can I connect the positive rail of the schematic to the same 12V regulator that is supplying the inverter driver without it affecting anything?

Reply
Swagatam says:
September 14, 2017 at 11:13 am

Hello Godson, yes you can do that without any problems

Reply
Godson says:
September 1, 2017 at 10:22 am

Replying to your response…
So for example, supposing I build a 2KVA inverter which I want to use for a maximum load of 1,600W.
Shutdown current = 1,600/220 = 7.27A
R1 = 2/7.27 = 0.28Ohm
R1 wattage = (1.2 + 2) x 7.27 = 23W (approx)
Is this correct sir?

Reply
Swagatam says:
September 1, 2017 at 12:37 pm

yes, that looks correct to me!

Reply
Godson says:
September 1, 2017 at 2:26 pm

Alright sir. Thank you so so much. I do appreciate you sir.

Reply
Swagatam says:
September 1, 2017 at 4:19 pm

you are welcome Godson!

Reply
Swagatam says:
September 1, 2017 at 12:39 pm

sorry, you must include 1.2V also in the R1 formula….

R1 = (1.2 + 2) / 7.27

Reply
Godson says:
September 1, 2017 at 9:08 pm

Ok,
So R1 = (1.2 + 2)/7.27 = 0.44ohm
And wattage = 23W as above.
Is that right sir?

Reply
Swagatam says:
September 2, 2017 at 2:07 am

yes that’s right!

Reply
maruti more says:
May 26, 2016 at 12:49 pm

Hello sir,
I made this circuit and I use 230v a.c. as I/p and 300w o/p. R1- 0.56/2w
but circuit didn't work.

Reply
Swagatam says:
May 26, 2016 at 4:20 pm

Hello Maruti, it will be difficult for me to guess what mistake you might have done in your circuit, please read the article and check what might be missing in your circuit

Reply
Unknown says:
May 26, 2016 at 12:46 pm

Sir, in this circuit u used stabilizer o/p as circuit i/p.
Can i apply direct 230v ac in I/p?
If I can then how I select all components?

Reply
anmol mishra says:
May 5, 2016 at 7:32 pm

Hello sir I m anmol from Lucknow
I started STYBLIZAR menufecturing as a business will u help me for my business technical support I need your help my watsup no. 08115720798

Reply
Swagatam says:
May 6, 2016 at 5:50 am

Hello Anmol, phone or wattsapp communication may not be possible, but you can consult the issues through email, I'll try to help.

Please make sure to write the questions in proper English and elaborately because I would be publishing it in my site also.

Reply
Sivaraj Palanichamy says:
May 1, 2016 at 7:49 am

Brother actually p1 is for sensitivity only know, i need to adjust current limit resistor? And the above circuit is only for overload current limit, also i need a under load current limit circuit?

Reply
Swagatam says:
May 1, 2016 at 8:42 am

Brother, at lower P1 setting the circuit will activate at higher currents, and at higher P1 value it will operate at lower current….so it can be used effectively for setting up current.

for under current cut off we might require two opamp circuits, one for controlling the upper limit and other for the lower limit….I'll think about it.

Reply
Sivaraj Palanichamy says:
April 30, 2016 at 2:47 pm

Dear Brother i need under and overload protection circuit for my openwell submersible water pumb 5hp 4kw 415v 10amp , for that i have to use variable protection should be 5amps to 20amps? if you have any circuit like this? Or pls design a circuit for me? If you need some more details pls ask me…

Reply
Swagatam says:
May 1, 2016 at 4:03 am

Dear Brother, the above design already has an adjustable feature in it through P1, you can set P1 to different positions for achieving any desired cut off point

Reply
mayoor says:
April 22, 2016 at 7:06 pm

Please there is a small confusion about the actual constant need for calculating various values of R1.. The post said 1.5 you said it is 2 and later said 3 so please explain the changes. Thanks

Reply
Swagatam says:
April 23, 2016 at 12:23 pm

Here's the formula

R1 = LED fwd drop value / cut-off current value

Reply
Nikhil Kachare says:
April 19, 2016 at 4:28 pm

Hiee sir
Can u tell about any circuit that will convert DC to ac (square wave).
Without using transformer.

Reply
Swagatam says:
April 20, 2016 at 11:49 am

Hi Nikhil, you can use the circuit which is shown in this article:

https://www.homemade-circuits.com/2014/01/simplest-full-bridge-inverter-circuit.html

Reply
mexzony says:
August 14, 2015 at 6:02 pm

Hello sir
I don't quite get how vijay set up the 1ohm 20w and the 10k preset.
Then what value can we use for P1.
Also there seem to be some confusion as to how to calculate R1 value as I read through the comments.

Reply
Swagatam says:
August 15, 2015 at 3:49 pm

Hello Michael, the delay effect shouldn't be so critical actually….and yes all the above parameters will interact some and influence the delay effect, so it may require a little experimentation until the right delay is determined…

Reply
adelusi oluwatosin says:
February 17, 2016 at 12:56 pm

sir please kindly help me design a 12vdc to 36vdc converter.sir i am ready for any output services rendered.

Reply
Swagatam says:
February 18, 2016 at 2:50 am

you can try any IC 555 based boost converter circuit or 555 IC based flyback converter circuit, please Google this you will find many

Reply
adelusi oluwatosin says:
February 17, 2016 at 12:51 pm

Sir assuming i want to use this circuit for 3kv inverter overload protection how could i calculate R1? sir the relay connection it seem not clear well to me, first, connection to coil terminal is not show in the circuit,secondly, N/O terminal and N/C seem some how confusion. Thanks, hope to hear from you soon.

Reply
Swagatam says:
February 18, 2016 at 2:41 am

Adelusi,

the formula is given in the article, please use it to calculate. the current limit in the formula could be calculated by dividing 3kv with the voltage.

please click the diagram to enlarge, you will be able to see both the contacts although slightly faded, but anyway the N/O is unconnected so its not important, the N/C is the one which is associated with the load and the current.

Reply
mexzony says:
August 14, 2015 at 5:09 pm

Hello Sir
Just stumbled upon this post.
Since vijay made it work then I think I can use it as an overload protector with some changes
1) I get rid of the relay and instead pass the positive signal from collector of PNP transistor to pin10 of my sg3524.
2) while I am studying the other post you referred me to this one looks more sophisticated.
3) where and how will I include a time delay before passing to in 10 of IC so the when the current goes above the limit it first gives a de lay of say 5secs and if load does not reducez current then it shuts off inverter
4) if per adventure the load settles to normal like in the case of surge loads capacitor should discharge rapidly so that it does not trigger shut down since starting current has reduced to normal

Reply
Swagatam says:
August 15, 2015 at 3:04 pm

Hello Michael,

for including a delay effect, you can simply add a high value capacitor across the base and ground of T1…make sure the signal from the opto comes through a resistor if you are using an opto coupler…this resistor value can also be tweaked for setting the delay response

Reply
Vijay says:
May 12, 2015 at 9:41 am

Hi Swagatam,

I redesigned this circuit and assembled. As my stabilizer is 1KVA and it can handle 4A, I have used a 1ohm 20W resistor as the voltage sensor. I know this is a little high value but I have created a voltage divider using a 10K preset and adjusted the voltage so that only at 4A the optocoupler is triggered. Even that's not perfect because even a tiny current through the optocoupler triggers T1. To mitigate this I played around and connected a 100K resistor between the optocoupler and T1 base. I tried the 4A current using an induction stove, set the power at 1000W, and I measured exactly 4A using a multimeter. This seems to work fine. When I increase the power to 1200W, it triggers.I haven't yet tried 1050W, 1100W etc yet, which I'll do a little later. While doing this, I found another issue; when I connect the output to my voltage stabilizer (already assembled using one of your circuits but this is 500VA), because of the inrush current to the autotransformer, the circuit triggers. I mitigated this issue by connecting a 47mf capacitor (anything less doesn't do the trick) between P1. Now when I increase the power to 1200, the circuit triggers but takes about 1 second to do so.

I have one query: Since this circuit allows a second of over current, will it damage the autotransformer? I feel it can take more current than it is rated at for some time but I just wanted to be sure.

Thanks,
Vijay

Reply
Swagatam says:
May 13, 2015 at 9:34 am

OK, that's fine Vijay, everything's well that ends well..

Reply
Vijay says:
May 13, 2015 at 6:33 am

Hi Swagatam, Thanks. I used MCT2E. I was thinking of trying an LED/LDR combo if 100K between MCT2E and T1 base didn't do the trick but it did.

Vijay

Reply
Swagatam says:
May 12, 2015 at 12:07 pm

Hi Vijay, congrats to you!

You have done all the modifications correctly, and everything seems perfect to me, a 1 second delay will not affect your autotransformer in any manner, because before getting damaged the transformer will first have to heat up, and when it reaches above 150 degrees only then it might start smoking and this might take more than 20 to 30 seconds.

By the way what did you use for the opto coupler? is it a readymade LED/phototransistor opto or the recommended LED/LDR type homemade opto?….the LED/LDR would provide better and more reliable results compared to the conventional one.

Reply
Vijay says:
April 23, 2015 at 6:59 am

Yes, I used two .47E resistors in series as I couldn't get 1 ohm for a 3amp load. Anyway, I'll try again and update.

Thanks,
Vijay

Reply
Swagatam says:
April 23, 2015 at 11:11 am

OK! thanks

Reply
Vijay says:
April 22, 2015 at 5:40 pm

Hi Swagatam,

Just like your voltage stabilizer circuit using opamps, I have also tried this circuit (with an optocoupler) and it works. But it triggers quite often even when there is not so much load. Adjusting the preset does not help. Any ideas?

Reply
Swagatam says:
April 23, 2015 at 6:26 am

Hi Vijay,

did you calculate R1 correctly? please calculate such that the opto led lights up only when there is a true overload as per the required specifications.

alternatively you may also try adding a 1uF capacitor across base and ground of the T1

Reply
Precious Ubani says:
November 1, 2013 at 4:32 pm

Thank you very much. I will build this circuit using an optocoupler and give you feedback.

Reply
Precious Ubani says:
October 29, 2013 at 4:42 pm

Thank you for the answer on P1 but what is the value of R2. Is it 56 ohms?

Reply
Swagatam says:
October 30, 2013 at 5:09 am

yes 56 ohms, it's the LED current limiting resistor

Reply
Precious Ubani says:
October 27, 2013 at 12:17 pm

please, what is the function of P1?

Reply
Swagatam says:
October 28, 2013 at 2:55 pm

For adjusting the sensitivity of the circuit….

Reply
Ajay says:
July 17, 2013 at 5:42 pm

Hello Swagatam,

Thanks very much for your kind and prompt response, need your advice to decide on the relay and T1, as I will be using a relay that can bear a minimum load of 15Amps, and have decide to build the the following:

https://www.homemade-circuits.com/2011/12/simple-mains-high-and-low-voltage.html

Regards,

Ajay

Reply
Swagatam says:
July 18, 2013 at 5:48 am

Hello Ajay

You may use the relay which is shown below:

http://www.oenindia.com/images/57.gif

OEN/12V/285ohms/16amp/SPDT

Reply
Ajay says:
July 16, 2013 at 7:26 pm

Hello Swagatam,

Thanks for the quick response, to be very precise I have recently bought a Hitachi AC model RAW318KTD, my previous AC compressor was blown due to the stabilizer was generating 300VAC. I have got the stabilizer repaired how ever want to be very cautious this time.

My AC specs are Current drawn-4.7 amps, Rated power supply -(230/50/1 Volts/Hz/Phase), Total Power input-1055 Watts.

Sorry for bothering you again.

Regards,

Ajay

Reply
Swagatam says:
July 17, 2013 at 5:29 am

Hello Ajay,

You will need an over voltage protector circuit in that case. You can make the following circuit:

https://www.homemade-circuits.com/2011/12/simple-mains-ac-over-voltage-and-under.html

It will protect your AC from high voltages as well as low voltages.

Reply
Ajay says:
July 15, 2013 at 6:24 pm

Hello Swagatam,

I want to apply this CKT to my Air Condition stabilizer which is 3Kva can you help me decide on the relay rating and R1 my AC is 1400Watts.

Regards,

Ajay

Reply
Swagatam says:
September 21, 2016 at 2:42 am

P = VI….V = voltage drop across resistor

Reply
Godson says:
August 31, 2017 at 1:09 pm

Hello sir Swagatam. I really appreciate your effort. I’ve been looking for an overload protection for inverter circuit. You have so far referred me to two post but this one is just the perfect one for the intended purpose. I’ve read through the comments and have gotten more info from your responses. Thank you sir. I have a few questions:
1. In your response above as regards how to calculate the sensing resistor wattage, you said that: P = VI, V = voltage drop across resistor. How do we determine this voltage?
2. I want to design the circuit in such a way as to use it to power off the inverter when overload is sensed at the transfo output. So i want to use a smaller relay such that the contacts will be used to disconnect power to the inverter oscillator during overload condition. So what i want to do is to allow the output of the transfo to pass through the sensing resistor directly to the load. Can i go ahead with that arrangement?
3. From the schematic, which side/pin of C2 is positive?

Reply
Swagatam says:
August 31, 2017 at 2:08 pm

Hello Godson, you can use the relay contact for the mentioned purpose, so in that case connect the indicated relay contact wire directly with the load.

watt of the resistor will be = bridge drop + LED drop / shut down current
= 1.2 + 1.5 / D current.
the white side of c2 is the positive.

Reply
Godson says:
August 31, 2017 at 4:55 pm

Please pardon me sir, I still don’t fully understand the explanation you gave in your response to how to calculate the wattage of the sensing resistor. Please could use the example you gave above for a 3KVA inverter to explain, I’ll understand it better that way. Thank you sir.

Reply
Swagatam says:
September 1, 2017 at 2:22 am

Godson, the wattage will equal to the voltage drop across the resistor multiplied by the shut down current limit selected by you.

the voltage drop across the resistor can be achieved by adding the bridge rectifier drop (approximately 1.2V) and the LED FWD voltage drop (approximately 2V)

Reply
Rajeev Mehndiratta says:
September 20, 2016 at 7:40 am

How you are calculating power of resistor R1? P=I2XR or P=VI ? Please explain.

Reply
Swagatam says:
July 16, 2013 at 5:07 am

…for 1400 watts it would be

1400/220 = 6.36amps

R1 = 0.3 ohms/ 2 watts

Relay contacts @10 to 12 amps.

Reply
Swagatam says:
July 16, 2013 at 5:04 am

Hello Ajay,

Here are the details

3000/220 = 13 amps

Therefore R1 = 2v/13 = 0.15ohms 3watts

Relay contacts must be rated at 20 amps

Reply
Back to Newest

Need Help? Please Leave a Comment! We value your input—Kindly keep it relevant to the above topic! Cancel reply

Your email address will not be published. Required fields are marked *

Primary Sidebar

circuit simulator image



Subscribe to get New Circuits in your Email



Categories

  • Arduino Projects (93)
  • Audio and Amplifier Projects (133)
  • Automation Projects (17)
  • Automobile Electronics (101)
  • Battery Charger Circuits (85)
  • Datasheets and Components (109)
  • Electronics Theory (149)
  • Energy from Magnets (27)
  • Games and Sports Projects (11)
  • Grid and 3-Phase (20)
  • Health related Projects (27)
  • Home Electrical Circuits (13)
  • Indicator Circuits (16)
  • Inverter Circuits (95)
  • Lamps and Lights (159)
  • Meters and Testers (71)
  • Mini Projects (28)
  • Motor Controller (68)
  • Oscillator Circuits (28)
  • Pets and Pests (15)
  • Power Supply Circuits (91)
  • Remote Control Circuits (50)
  • Renewable Energy (12)
  • Security and Alarm (64)
  • Sensors and Detectors (106)
  • SMPS and Converters (34)
  • Solar Controller Circuits (60)
  • Temperature Controllers (43)
  • Timer and Delay Relay (49)
  • Voltage Control and Protection (42)
  • Water Controller (36)
  • Wireless Circuits (30)





Other Links

  • Privacy Policy
  • Cookie Policy
  • Disclaimer
  • Copyright
  • Videos
  • Sitemap



People also Search

555 Circuits | 741 Circuits | LM324 Circuits | LM338 Circuits | 4017 Circuits | Ultrasonic Projects | SMPS Projects | Christmas Projects | MOSFETs | Radio Circuits | Laser Circuits | PIR Projects |

Social Profiles

  • Twitter
  • YouTube
  • Instagram
  • Pinterest
  • My Facebook-Page
  • Stack Exchange
  • Linkedin



Recent Comments

  • Swagatam on 9 Simple Solar Battery Charger Circuits
  • Gagana on 9 Simple Solar Battery Charger Circuits
  • Swagatam on Arduino 2-Step Programmable Timer Circuit
  • Swagatam on Simple Buck-Boost Converter Circuits Explained
  • Swagatam on IC IR2111 H-Bridge MOSFET, IGBT Driver IC: Full Datasheet, Circuit Diagram

© 2026 · Swagatam Innovations