• Skip to main content
  • Skip to primary sidebar

Homemade Circuit Projects

Need circuit help? Post them in the comments! I've answered over 50,000!

Blog | Categories | About | Contact | Calculators-online
You are here: Home / Voltage Control and Protection / SCR/Triac Controlled Automatic Voltage Stabilizer Circuit

DIY Circuits | Learn Basics | Arduino Coding




SCR/Triac Controlled Automatic Voltage Stabilizer Circuit

Last Updated on April 9, 2025 by Swagatam 77 Comments

In this article I have explained a relatively simple triac controlled automatic mains voltage stabilizer circuit, which uses logic ICs and a few triacs for controlling the mains voltage levels.

Why Solid State

Being solid state in design, the voltage switching transitions are very smooth with minimum wear and tear, resulting in efficient voltage stabilization.

Discover the whole construction procedure of this unique, solid state mains voltage stabilizer.

The proposed circuit of a triac controlled AC voltage stabilizer will provide an excellent 4 step voltage stabilization to any appliance at its output.

With no moving parts involved its efficiency is further enhanced. Find out more of this silent operator: power guard.

The circuit of an automatic voltage stabilizer discussed in one of my previous articles, though useful, due to its simpler design, does not have the capability of controlling the different levels of varying mains voltages discretely.

The proposed idea though not tested, looks pretty convincing, and if the critical components are properly dimensioned, should work as expected.

The present circuit of triac controlled AC voltage stabilizer is outstanding in its performance and is almost an ideal voltage stabilizer in every respect.

As usual the circuit has been exclusively designed by me. It is able to control and dimension the input AC mains voltage accurately through 4 independent steps.

The use of triacs make it sure that the changeovers are quick (within 2 mS) and with no sparks or transients usually associated with relay type of stabilizers.

Also since no moving parts are employed, the entire unit becomes completely solid state and almost permanent.

Let’s proceed to see how the circuit functions.

CAUTION:
EACH AND EVERY POINT OF THE CIRCUIT PRESENTED HERE MAY BE AT AC MAINS POTENTIAL, THEREFORE EXTREMELY DANGEROUS TO TOUCH IN SWITCHED ON POSITION. UTMOST CARE AND CAUTION IS ADVISED, USE OF A WOODEN PLANCK UNDER YOUR FEET IS STRICTLY RECOMMENDED WHILE WORKING WITH THIS DESIGN .... NEWBIES PLEASE KEEP AWAY.

Circuit Operation

The functioning of the circuit may be understood through the following points:

Transistors T1 to T4 are all arranged to sense the gradual rise in the input voltage and conduct one after the other in sequence as the voltage rises and vice versa.

Gates N1 to N4 from IC 4093 are configured as buffers. The outputs from the transistors are fed to the inputs of these gates.

All the gates are interconnected to each other in such away that the output of only a particular gate remains active at a given period of time according to the level of the input voltage.

Thus, as the input voltage rises the gates respond to the transistors and their outputs subsequently become logic hi one after the other making sure that the previous gate’s output is shut OFF and vice versa.

The logic hi from the particular buffer is applied to the gate of the respective SCR which conducts and connects the relevant “hot” line from the transformer to the external connected appliance.

As the voltage rises, the relevant triacs subsequently select the appropriate “hot” ends of the transformer to increase or decrease the voltage and maintain a relatively stabilized output.

How to Assemble the Circuit

The construction of this triac control AC power guard circuit is simple and just a matter of procuring the required parts and assembling them correctly over a general PCB.

It is pretty obvious that the person who is attempting to make this circuit knows a bit more than just the basics of electronics.

Things may go drastically wrong if there is any error in the final assembly.

You will require an external variable (0 to 12 volts) universal DC power supply for setting up the unit in the following way:

Assuming that an output supply of 12 volts from TR1 corresponds to 225 volts input supply, through calculations we find that it will produce 9 volts at an input of 170 volts, 13 volts will correspond to 245 volts and 14 volts will be equivalent to an input of approximately 260 volts.

How to Set Up and Test the Circuit

Initially keep the points “AB” disconnected and make sure the circuit is totally disconnected from the AC mains.

Adjust the external universal power supply to 12 volts and connect its positive to the point “B” and negative to the common ground of the circuit.

Now adjust P2 until LD2 is just switched ON. Reduce the voltage to 9 and adjust P1 to switch ON LD1.

Similarly, adjust P3 and P4 to illuminate the relevant LEDs at voltages 13 and 14 respectively.

The setting procedure is now complete. Remove the external supply and join points “AB” together.

The whole unit may now be connected to the mains AC so that it can start working right away.

You may verify the performance of the system by supplying a varying input AC through an auto transformer and checking the output using a digital multimeter.

This triac controlled AC voltage stabilizer will shut OFF at voltages below 170 and above 300 volts.

IC 4093 Internal Gate Pinout Arrangement

IC 4093 pinout details

Parts List

You will require the following parts for the construction of this SCR control ac voltage stabilizer:
All resistors are ¼ Watt, CFR 5%, unless otherwise stated.

  • R5, R6, R7, R8 = 1M ¼ watt,
  • All Triacs are 400 volts, 1KV rated,
  • T1, T2, T3, T4 = BC 547,
  • All zener diodes are = 3 volts 400 mW,
  • All Diodes are = 1N4007,
  • All presets = 10K linear,
  • R1, 2, 3, 4, 9, 10, 11, 12, 13, 14, 15, 16, 17, 18, 19, 20 = 1K ¼ watt,
  • N1 to N4 = IC 4093,
  • C1 and C3 = 100Uf/ 25 volts,
  • C2 = 104, ceramic,
  • Power Guard Stabilizer Transformer = “Made to order” having 170, 225, 240, 260 volts output Taps at 225 volts input supply, or 85, 115, 120, 130 volts taps at 110 AC input supply.
  • TR1 = Step down transformer, 0 – 12 volts, 100 mA.

You'll also like:

  • Passive Power Factor Correction (PFC) Calculator
  • c7cdc4f94ef3e4ab7b7c626cfb034114e7b774e0 orig2-Stage Mains AC Voltage Stabilizer Circuit
  • LM324 Operational Amplifier5 KVA to 10 KVA Automatic Voltage Stabilizer – 220 Volts, 120 Volts
  • WindingAutomatic Voltage Regulator (AVR) Circuit

Filed Under: Voltage Control and Protection Tagged With: Automatic, Controlled, SCR, Stabilizer, Triac, Voltage

About Swagatam

I am an electronics engineer and doing practical hands-on work from more than 15 years now. Building real circuits, testing them and also making PCB layouts by myself. I really love doing all these things like inventing something new, designing electronics and also helping other people like hobby guys who want to make their own cool circuits at home.

And that is the main reason why I started this website homemade-circuits.com, to share different types of circuit ideas..

If you are having any kind of doubt or question related to circuits then just write down your question in the comment box below, I am like always checking, so I guarantee I will reply you for sure!

Previous Post: « Simple Hi Efficiency LED Torch Circuit
Next Post: 5 Interesting Flip Flop Circuits – Load ON/OFF with Push-Button »

Reader Interactions

Comments

Imran Khan says:
May 20, 2015 at 11:19 am

Hello, Sawagatam, thanks for your circuit, I guess you do not have good idea about the transformer winding and design, I can make the transformer for you here, i need tow thins here I want to add one more tap and 5kv load so what have to change the triacs? I will draw the pcb and i will send here for all users.
thanks

Reply
Swagatam says:
May 20, 2015 at 12:00 pm

Thank you Imran, I appreciate your help. The only difficult part with an autotransformer is the number of turns, core dimension and the wire gauge, but making it can be actually easy, it's just about winding one long single continuous winding with taps removed at appropriate points across the length of the winding.

For 5kv you can upgrade the tracs with BTA41/600 it will be strong enough to handle 5kva easily

I'll make sure it gets posted in the above article, as soon as you send me the mentioned details

best regards.

Reply
Imran Khan says:
May 20, 2015 at 11:15 am

HELLO, SWAGATAM, THANKS FOR THIS CIRCUIT, I WILL MAKE THE PCB AND POST IT HERE AND I CAN DESIGN THE AUTOTRANSFORMER FOR THIS PROJECT, SO I NEED THE MORE LOAD I MEN 5 KV THEN WHICH TRIACS I HAVE TO USE.
THANKS

Reply
José Simões says:
May 19, 2015 at 8:37 pm

Hello Friend !
Nice Job !
But I have a question !
Can i use your project to do this :
In – 85 ~ 240 vac
Out – always 225vac

Reply
José Simões says:
May 20, 2015 at 12:03 pm

Ow sure !

Thank you that was prompt ! And how about the Resistors in base & emitter of all the transistors(T1-T4) ? I know they are not crucial, so can I pick 10k 1/4w value ?

Reply
Swagatam says:
May 20, 2015 at 11:42 am

Hello Jose,

yes it is possible but that might require the inclusion of more number of triac stages, may be up to 10 or 12, and corresponding numbers of tapping from the stabilizer transformer.

Reply
Sandeep sharma says:
April 24, 2015 at 4:03 pm

sir, can u tell me where should i connect the terminal of tapping transformer with the triac terminals. i have done all the things and the sensor circuit is working accurately but i couldn't get the output., and the entire tapping transformer connection

Reply
Swagatam says:
April 30, 2015 at 4:34 pm

OK, no problem!

Reply
Sandeep sharma says:
April 30, 2015 at 8:37 am

actually sir we have a holiday of 3 days. so college is closed and we dont have the required equipments. i will do it on monday and i will tell u the result.

Reply
Swagatam says:
April 30, 2015 at 8:12 am

OK… please check it and let me know

Reply
Sandeep sharma says:
April 29, 2015 at 2:09 pm

this circuit should work because previously the load was in series with the main input. we can not get the constant output voltage across load.

Reply
Swagatam says:
April 29, 2015 at 12:23 pm

I have updated the corrected diagram, you can check it now.

Reply
Swagatam says:
April 29, 2015 at 11:49 am

I have reassessed the transformer wiring/triac/load and I think I have understood the problem, I'll correct it and try to update it soon…

Reply
Swagatam says:
April 28, 2015 at 4:29 pm

Sandeep, the theoretical part that you are confused with is a simple electrical wiring, since you have reached and successfully built the complex section of the circuit, troubleshooting this simple electrical issue should not be a problem at all according to me, the triacs are just acting like switches, so replace the triac MT1/MT2 with a manual short as I mentioned earlier to identify and trace the electrical path.

I have not checked it practically but as you have tested it yourself the circuit sections actually work as explained, it's only a simple electrical path that you are not able troubleshoot, imagine a design without the circuit rather only with the trafo, the load and switches, simulate it practically and then replace it with triacs to check the results, you can seek an experts help if you finally fail to troubleshoot the fault

Reply
Sandeep sharma says:
April 28, 2015 at 3:15 pm

sir we have already done it. theoratically it is correct but practically it is not giving the output. sir, have u done it practically? this project belongs to our final yr project and we have to submit it within 1 week and we dont know what to do. we went through all the possibilies but result is still zero. practically u have done it na sir.

Reply
Swagatam says:
April 28, 2015 at 11:42 am

0V refers to the first tap which may be near most to the "hot tap" assigned with the minimum volts, in the diagram its the 170V tap

if your triacs are connected in the manner you have specified then they must conduct, and if any one of the triac conducts, the input entering through the load has to pass through the triac and reach the other end of the mains through MT1 to MT2…and since the load is connected in series with this mains line it has no other option but to switch ON.

as I mentioned before, try shorting the MT1/MT2 of the triac which has its gate LED illuminating, this should toggle the load ON/OFF, confirm this manual operation. if this happens would indicate towards a non-conducting triac….this could be due to a insufficient gate voltage/current, reduce the gate resistor value and recheck…

Reply
Sandeep sharma says:
April 28, 2015 at 10:13 am

LEDs are working sequentially and triacs too. sir, we have 3 terminals of the triac. MT1 is shorted with ground. gates are trigeering. MT2 are connected with 4hot wires(tapping) of transformer. and load is connected according to the diagram. what is the meaning of this 0V? we have connect load across i/p voltage and output of the transformer(say 220v, taken 0V as 220v). still problem is same,

Reply
Swagatam says:
April 28, 2015 at 9:41 am

Do the LEDs light up in sequence while testing with an variable input?

if yes, then you can confirm whether the triac corresponding to the illuminated LED is conducting or not….short the MT1, MT2 of the triac with a wire manually this should actuate the load, if it doesn't then probably there could be some problem with the triac…. check it as per its datasheet…if not then the trafo configuration could be assumed to be incorrect and not as per the shown diagram…

Reply
Sandeep sharma says:
April 28, 2015 at 7:21 am

sir, my transformer has 4 hot wire(tapping) 1 common terminal and 1 output wire. and i have done all the thins as u mentioned in the diagram but still the circuit is not working and we are not getting the output as desired. sensor part is working properly, if we connect the transformer according to the diagram we are not gettng the output. please help us.

Reply
Sandeep sharma says:
April 26, 2015 at 5:30 pm

okay sir and thanks for the help.. thanku..

Reply
Swagatam says:
April 26, 2015 at 4:33 pm

I have updated the diagram, please check it out.

do not use D8…remove it

Reply
Sandeep sharma says:
April 26, 2015 at 9:50 am

if we do like this then we get 2-3V across triac but we have connected one of the wire of the transformer(say 135v) to the triac.we can not step up this voltage to 220V. if we take same common it will effect the circuit because one side is electronic circuit and other side electrical circuit, if we take same common the entire circuit changes abruptly and its behaviour changes.

Reply
Swagatam says:
April 26, 2015 at 6:00 am

you can do one thing, connect the load in series with the common mains input of the transformer.

suppose your transformer has 5 wires, one out of these will be the common "cold" input wire and other will be the "hot" ends…connect these hot ends with the triacs as shown in the diagram and connect the load in series with the common or the "cold" wire

Reply
Sandeep sharma says:
April 25, 2015 at 1:14 pm

thanks for your concern sir, please correct it as soon as possible for you.

Reply
Swagatam says:
April 25, 2015 at 11:55 am

Sandeep, the load should be between the MT1 of all triacs and ground, that is between the left leads and the common ground, however it seems this could pose some problems, I'll try to correct it soon if possible within two days.

Reply
Swagatam says:
October 15, 2013 at 3:57 am

Thanks!

You will require a variable DC power supply for setting up the relay activation thresholds, there's no other way.

Here's one circuit that you can try:

https://www.homemade-circuits.com/2011/12/how-to-make-accurate-7-stage-op-amp.html

voltage level meter can be built by modifying the following circuit:

https://www.homemade-circuits.com/2013/08/make-this-10-step-battery-voltage.html

Reply
Swagatam says:
October 6, 2013 at 3:30 pm

Hi Anil, you will need an appropriately designed autotransformer with outputs ranging from 90 to 450V for tacking this issue, then use this transformer with the following circuit the automatic changeover actions.

https://www.homemade-circuits.com/2011/12/how-to-make-accurate-7-stage-op-amp.html

Reply
Back to Newest

Need Help? Please Leave a Comment! We value your input—Kindly keep it relevant to the above topic! Cancel reply

Your email address will not be published. Required fields are marked *

Primary Sidebar

circuit simulator image



Subscribe to get New Circuits in your Email



Categories

  • Arduino Projects (93)
  • Audio and Amplifier Projects (133)
  • Automation Projects (17)
  • Automobile Electronics (101)
  • Battery Charger Circuits (85)
  • Datasheets and Components (109)
  • Electronics Theory (149)
  • Energy from Magnets (27)
  • Games and Sports Projects (11)
  • Grid and 3-Phase (20)
  • Health related Projects (27)
  • Home Electrical Circuits (13)
  • Indicator Circuits (16)
  • Inverter Circuits (95)
  • Lamps and Lights (159)
  • Meters and Testers (71)
  • Mini Projects (28)
  • Motor Controller (68)
  • Oscillator Circuits (28)
  • Pets and Pests (15)
  • Power Supply Circuits (91)
  • Remote Control Circuits (50)
  • Renewable Energy (12)
  • Security and Alarm (64)
  • Sensors and Detectors (106)
  • SMPS and Converters (34)
  • Solar Controller Circuits (60)
  • Temperature Controllers (43)
  • Timer and Delay Relay (49)
  • Voltage Control and Protection (42)
  • Water Controller (36)
  • Wireless Circuits (30)





Other Links

  • Privacy Policy
  • Cookie Policy
  • Disclaimer
  • Copyright
  • Videos
  • Sitemap



People also Search

555 Circuits | 741 Circuits | LM324 Circuits | LM338 Circuits | 4017 Circuits | Ultrasonic Projects | SMPS Projects | Christmas Projects | MOSFETs | Radio Circuits | Laser Circuits | PIR Projects |

Social Profiles

  • Twitter
  • YouTube
  • Instagram
  • Pinterest
  • My Facebook-Page
  • Stack Exchange
  • Linkedin



Recent Comments

  • Swagatam on 9 Simple Solar Battery Charger Circuits
  • Gagana on 9 Simple Solar Battery Charger Circuits
  • Swagatam on Arduino 2-Step Programmable Timer Circuit
  • Swagatam on Simple Buck-Boost Converter Circuits Explained
  • Swagatam on IC IR2111 H-Bridge MOSFET, IGBT Driver IC: Full Datasheet, Circuit Diagram

© 2026 · Swagatam Innovations