Simple Triac Triggering Circuits Explained

Last Updated on November 17, 2023 by Swagatam 119 Comments

In this post I have explained the fundamental methods of triggering a triac, and also discuss the right way to connect the terminals of a triac.

Triacs are solid-state bidirectional thyristors that can switch across both the AC half cycles on a 120-volt or 240-volt Ac power system.

A triac could be activated (switched on and latched) with the AC line both synchronously or asynchronously.

However, if the triac's gate terminal current drops just below its lowest holding threshold, it will be switched off instantly at the completion of each AC half-cycle (180 electrical degrees).

WARNING: ALL THE CIRCUITS DISCUSSED IN THE FOLLOWING ARTICLE INVOLVE LETHAL 220 V MAINS AC. THEREFORE YOU MUST BE EXTREMELY CAREFUL WHILE USING AND TESTING THESE CIRCUITS, MAKING SURE THAT YOU APPLY ALL THE NECESSARY PRECAUTIONS DURING THE PROCEDURES. ALL THESE CIRCUITS ARE STRICTLY RECOMMENDED ONLY FOR THE EXPERTS.

Synchronous vs Asynchronous Switching

In an asynchronous switching, the triac is triggered ON randomly at any point of the phase cycle.

Due to this, asynchronous switching of triacs can produce substantial radio-frequency interference (RFI), especially at the first switching cycle.

In a synchronous triac switching, the switching periods consistently arrive on at the same moment for each AC half-cycle (typically right after the zero-crossing period) and therefore produce negligible RFI.

All the circuits I have I have explained in this article use asynchronous power switching. Figures 1–8 depict a number of asynchronous triac power-switching circuits for elementary ON/OFF AC line switching.

How to Connect a Triac

A triac has 3 terminals, which are MT1, MT2, and the Gate. The MT stands for main terminal.

Therefore, the main terminals MT1 and MT2 are used for switching heavy AC mains operated loads, through 220V or 120V AC mains supply.

This switching happens in response to a small DC voltage applied to the gate terminal of the triac.

New hobbyists often get confused and ask the question how the MT1 and MT2 terminals should be configured with the AC load and through a DC at the gate?

Remember, the correct method to connect the triac MT1 amd MT2 terminals is by ensuring that the AC load is always connected in series with the MT2 terminal, and the MT1 is connected directly with the other AC line of the mains supply.

how to connect triac with mains AC, load and DC gate trigger

Also, it is extremely important to note that the AC line associated with the MT1 terminal must be also linked with the negative or the ground line of the DC supply, which is being used for triggering the triac gate.

Failing to do this will not allow the triac to respond to the gate signals.

Triac Switching

A basic AC power switch using a triac is shown in Figure 1.

This triac circuit can be used to control the flow of AC power to lamps, heaters, motors, and a variety of other appliances and devices.

However, the triac for this circuit should have the appropriate power handling capacity to reliably switch AC power for the particular application.

how to connect triac with AC mains with snubber

All of the components in this article's schematics were chosen to switch only 120 volts, 50/60 Hz AC.

During the time the switch S1 is open, the triac is turned off and functions as an open switch.

However, when switch S1 is closed, it operates as a closed switch which is powered from the mains AC line via the load and R1 right at the start of each AC half-cycle.

When the triac is turned on, its main terminal voltage decreases to just a few hundred millivolts, thus R1 and S1 draw relatively negligible current.

Please remember that as soon as S1 is initially closed, the triac's turn ON threshold is not synchronized with the AC line, but it gets synchronized with the successive AC half-cycles.

The snubber network formed by resistor R1 and capacitor C1 reduces voltage spikes which develop whenever inductive loads are switched and when current and voltage are out of phase.

Most of the triac circuits discussed in this article incorporate snubber connections.

The triac works like a power switch that may be actuated by DC supply derived from AC supply, as shown in Figure 2 below.

a triac may be actuated by DC supply derived from AC supply

Each positive line half-cycle charges capacitor C1 to +10 volts via resistor R1 and Zener diode D1.

When S1 is turned ON, the charge from C1 initiates the triac. Here the resistor R1 always gets exposed to approximately to the whole AC line voltage.

As a result, it demands a significant power rating (5 watts in ous case).

Due to the fact that all portions of this circuit are "active," it can create a fatal electrical-shock hazard.

Furthermore, since it lacks an isolator or complementing mechanism, this circuit is impossible to integrate with outer control circuitry.

Isolated Triac Control using Opto-Couplers

The next Figure 3 below demonstrates how to modify the circuit in Figure 2 to make it easier to connect with external control circuits.

Bipolar junction transistor Q1 is used in instead of switch S1 and is operated by the output stage of an optocoupler (or optoisolator) IC1.

An infrared light-emitting diode (IRED) is optically linked to a phototransistor in this system. Any of the commercially available transistor-output optoisolators can be implemented in these application.

Isolated Triac Control using Opto-Couplers

The opto couplers like TIL111, TIL 112, 4N27, and 4N28 are among the several. Using resistor R1, a 5 volt or larger DC source could be used to power the optocoupler.

Only after switch S1 connects the input circuit supply to a 5 volt or larger power source, the triac is switched on.

Typical isolation values (Viso) for optocouplers are 5000 volts AC, with some having ratings as large as 7500 volts AC.

This implies that the DC input circuit is completely isolated from the triac output side circuit powered by the AC line.

By substituting S1 with an appropriate electronic detector, this fundamental triac switching circuit may be modified to provide any desired type of automated "remote" triac switching.

Figure 4 below shows a modification of the circuit seen in Figure 3.

remote triac switching

Using capacitor C1 and the series resistor R1, along with the back-to-back Zener diodes D5 and D6, the triac is AC actuated on each line half-cycle in this design.

The amount of the triac gate current is determined by C1's AC line impedance, while the power dissipation of the capacitor C1's is almost around zero.

The series connection of Zener diodes D5, D6, and R3, that is loaded by transistor Q1, is coupled across the bridge rectifier built using diodes D1, D2, D3, and D4.

The bridge is essentially open while transistor Q1 is off, and triac TR1 switches on following the onset of each AC half-cycle.

As soon as  transistor Q1 is turned on, an almost a short circuit like condition is developed across D5, D6, and R3, which shuts off the Triac gate current, eventually turning off the triac TR1.

The optocoupler from the isolated external input stage drives transistor Q1, thus the triac is typically on, but it switches off as soon as the switch S1 is closed.

Using DC for Triggering a Triac

Figures 5 and 6 as given below, illustrate how to use a DC power source from a transformer power supply and a transistorized switch to activate a triac AC power switch.

When S1 is closed, both the transistor and the triac are both turned on, and as soon as S1 is open, both the devices are turned off.

In Figure 5, switch S1 can be substituted by a sensor device that can detect and respond to physical changes.

Transistor Q1 can be a BC557 transistor, not shown in the diagram.

switching a triac from transformer DC power supply

For example, If the ambient temperature decreases below a predetermined level, a thermistor, can be incorporated to activate the triac circuit.

Similarly, photoconductive cell can be installed to detect light levels, a pressure sensor may detect changes in air or liquid pressure, and a flow metre can react to variations in liquid or air flow rate.

Please be cautioned that the  Fig. 5 circuit, is "live" and poses a lethal shock threat.

Figure 6 below demonstrates how to adapt the Fig. 5 circuit to use an optocoupler for its control.

This circuit could be actuated through a completely independent and isolated external circuit due to the presence of the optocoupler.

Triggering through Unijunction Transistor

Figures 7 and 8 as shown below, depict many different methods for triggering a triac through a completely isolated external circuit.

A unijunction transistor (UJT) placed in a pulse-generating relaxation oscillator provides the triggering operation in both of these circuits.

The oscillator circuit, which contains UJT Q2, provides the triggering pulses in these two circuits.

It works with a frequency of many kHz and feeds its output pulses to triac's gate via the pulse transformer T1, that ensures the intended isolation.

Triggering triac through Unijunction Transistor

During the ON periods of the oscillator, the triac is turned on immediately at the start of each AC half-cycle due to the UJT device's relatively high working frequency.

With a resistor R3 is connected between the emitter and the base B2 of the UJT Q2, and a capacitor C1 hooked up between the emitter and the base B1, the UJT Q2 now works like a relaxation oscillator.

In this configuration UJT is able to switch rapidly to charge/discharge the capacitor at high speeds, as soon as the capacitor voltage reaches a certain threshold.

The time consumed by the capacitor to discharge could be evaluated, using the sawtooth's frequency calculations which is around 1/ time.

Since Q1 is in series with the UJT's primary timing resistor R3 in the Fig. 7 circuit, the UJT and the triac only switch on when S1 is closed.

UJT triac switching with a pulse transformer

On the other hand, in Figure 8 above since Q1 is in parallel with the UJT's primary timing capacitor C1 in the Fig. 8 circuit, the UJT and triac only switch on when S1 is open.

S1 could be substituted by a sensor or transducer in each of these circuits to provide an automated power-switching operation as mentioned previously.

The Q1 in the above figure should be an NPN transistor, such as a BC547.

You'll also like:

  • checking DC level of VbeHow to Troubleshoot Transistor (BJT) Circuits Correctly
  • inverterHow an Inverter Functions, How to Repair Inverters – General Tips
  • sineDCwaveformdigaramDifference Between Alternating Current(AC) and Direct Current(DC)
  • transformer workingHow Transformers Work

Filed Under: Electronics Theory Tagged With: Circuits, Explained, Simple, Triac, Triggering

About Swagatam

I am an electronics engineer and doing practical hands-on work from more than 15 years now. Building real circuits, testing them and also making PCB layouts by myself. I really love doing all these things like inventing something new, designing electronics and also helping other people like hobby guys who want to make their own cool circuits at home.

And that is the main reason why I started this website homemade-circuits.com, to share different types of circuit ideas..

If you are having any kind of doubt or question related to circuits then just write down your question in the comment box below, I am like always checking, so I guarantee I will reply you for sure!

Previous Post: « 10 Useful Active Filter Circuit Diagrams Explored
Next Post: Wheatstone Bridge Circuits Explained with Calculations »

Reader Interactions

Comments

KW says:
December 13, 2022 at 2:10 am

I think you have drawn the zener diodes incorrectly in Figure 4. They are not shown back to back, they are shown in series. The two anodes should be connected together and the cathodes connected to the bridge rectifier and the gate respectively for this circuit. See the February 2002 Nuts and Volts article on triacs.

Reply
Swagatam says:
December 13, 2022 at 9:38 am

Thank you for the information. I hope the readers will understand this issue and do the necessary corrections while building the project.

Reply
David says:
November 16, 2022 at 12:03 pm

I am still not understanding something. I am trying to trigger a triac with an Arduino microprocessor. I am using 24v AC solenoids, like what is found in a sprinkler system. It is my intension to use a TVS diode to protect against transient voltage spikes, and not use an opto-coupler. How can the DC and AC signals be mixed? How can the DC signal from the controller trigger the triac’s gate and not be part of the AC circuit?

Reply
Swagatam says:
November 16, 2022 at 12:48 pm

The first circuit shown in the above article is the correct way of connecting a triac with AC load to a DC source. However in this circuit the AC cannot be isolated from the DC triggering circuit. Nevertheless, the AC will never interfere with the DC and will not cause any problems.
If you want to isolate the AC from DC then you will have to use an opto-coupler.

Reply
Nil says:
November 15, 2022 at 10:39 am

Hello Sir
i am facing a Triac (BTA12 -800) failure with my remote circuit , used pic16f676 with capacitive ( transformer less ) power supply & MOC3021 opto coupler with Triac for control AC220 v , From total 7 Triac i used 5 Triac for for of/off without snubber & 2 Triac for fan speed control with snubber calculation. i placed all Triac at very nearest area i mean all touch to gather with each other & no sort of it’s heat sink with each other. So what the reason of failure , it’s placement problem ? Or may i used some line filter & any other spike protector element in primary side.
If u used snubber for on /off then it create problem of flicker on electronics led driver load ( due to main capacitor after bridge is charged ) .

Reply
Swagatam says:
November 15, 2022 at 1:07 pm

Hello Nil,
The BTA12/800 is a very powerful and rugged triac and will never burn, unless the load exceeds 800 V/ 12 amps, or if the triac overheats or if the triac itself is a duplicate part.
If you are using many triacs together make sure there bodies do not touch with each other.
I hope you are not using a capacitive power supply for the PIC16F, I hope you are using a 5V regulated AC to DC adapter for the PIC.
The triacs are not sensitive devices like MOSFETs so placement is not the problem.
If your load side is not using above 800 V or above 12 amps, and if the triacs are not over heating then possibly the triacs are duplicate and faulty in nature.

Reply
Nil says:
November 17, 2022 at 11:52 am

Dear Sir
Thanks for prompt reply. My load is become house hold tube light & led driver tube light & regulars ceiling fan 500 ohms with BTA12 800.
instead of it can u give me other parameter by which i will be gudge that its origin.
I will take care of SMPS 5 v reg instead of Capacitive with PIC 16F.
After this all change does it require to add any spike suppresser like Line filter and 0.1 X2 type cap in input circuit?

Reply
Swagatam says:
November 17, 2022 at 12:53 pm

Hello Nil,
If you have taken care of the mentioned things then there’s no need of any snubber for the triac BTA12 800.
By the way the MOC circuit itself has a snubber network added across the external triac.

Reply
Nil says:
November 18, 2022 at 8:43 am

Thanks
How can we judge that Triac is original Or dummy. Any test method. May i check its break down?
There is no need to add line filter in input side if we go with +5v Regulated SMPS ?

Reply
Swagatam says:
November 18, 2022 at 10:05 am

It can mostly be judged by its bad printing and poor external finishing. For practical testing, you can setup the first circuit from the above article, and test it with a heavy AC load.
If your load is not a high frequency type load then no need to add any filter. However if you feel it needs to be added to can go ahead and add it.

Reply
Nil says:
November 19, 2022 at 10:02 am

Thanks
ok clear all things.

Reply
suat kaleli says:
August 11, 2022 at 11:06 am

Hi Swagatam;
In my circuit there are 3 bulbs (220 AC) controlled by BT136 and BT136 is being driven by PIC16F877A (working voltage 5 V DC). LM35 cheks the heat and if it is above 38 degrees C then BT136 is OFF but if it is under 36 degrees C then BT136 is ON. My problem is there are to much blinking events between the 38 and 36 degrees. Plase advise if those blinkings would damage the BT136 or not. Regards

Reply
Swagatam says:
August 11, 2022 at 5:36 pm

Hi Suat,

You can try connecting a 470uF/25V capacitor between gate and ground of the triac and see if that helps or not.

Reply
Suat Kaleli says:
July 19, 2022 at 8:31 am

Hi Swagatam;
Duty of my circuit; to switch a 220 V AC bulb by BT136 and lights a led on by a NPN transistor (emitter voltage is 5 V DC). However, although no base trigger voltage I measure about 160 V DC at the output of the transistor. So I need your commentary-Best Regards
P.S.: BT136 Neutral and DC ground are common as known.

Reply
Swagatam says:
July 19, 2022 at 9:16 am

Hi Suat,
Since we have AC mains line connected with the DC circuit, all the points in the circuit will float with mains AC, or at least there will be some leakage AC floating across all the points. The meter has an high input impedance therefore even the leakage AC mains will be indicated on the meter as a high voltage.

Reply
Suat Kaleli says:
July 19, 2022 at 11:25 am

I am sorry Swagatam;
After I sent the second message I have checked the circuit although there is no trigger voltage to the base of the transistor led is always ON. Kind Regards

Reply
Swagatam says:
July 19, 2022 at 11:32 am

Hi Suat, where did you connect the LED? Please connect it in series with the gate resistor of the triac

Reply
Suat Kaleli says:
July 19, 2022 at 1:32 pm

Excuse me but I am confused;
As I understood from your above suggestion the led will be on whenever the triac is on
Whereas I do not them (220 AC bulb and the led) on at the same time. Bulb will heat the environment and sometimes the led which resembles the fan will be on free from the triac activity. Best Regards

Reply
Swagatam says:
July 19, 2022 at 1:52 pm

Yes the LED will be ON when a voltage is applied to the gate through the LED which will finally enter the MT1 lead, which is the ground lead of the triac. If you check the MT1/Gate connection with a multi-meter you will a find a continuity across these two terminals, so if a voltage is applied to gate it will pass to the MT1 lead.

Reply
Suat Kaleli says:
July 20, 2022 at 5:53 am

Hi Swagatam;
The subject is complicated for me and may be I did mislead you but I got the answer of my question by trying and getting wrong. I have realized that when I placed the led to wrong side of the NPN transistor it is always ON even there is no base voltage. Kind Regards.

Reply
Swagatam says:
July 20, 2022 at 9:29 am

Hi Suat,

If you are using the emitter of the NPN to trigger the triac, then the LED can be connected in series with the emitter pin of the transistor along with a series resistor. The anode of the LED will be towards the emitter, cathode will be towards the triac gate.

Reply
Suat Kaleli says:
July 19, 2022 at 11:16 am

Thanks Swagatam;
What I understand from your commentary; “there might be shock hazard but technically no problem on the circuit.”
Kind Regards

Reply
Swagatam says:
July 19, 2022 at 11:31 am

Yes that’s perfectly correctly. There may be floating voltage which may not affect the circuit but can produce lethal shock if touched

Reply
Ehsan Firouzi says:
June 29, 2022 at 7:06 pm

Hello dear Mr Swagatam
I am using a triac as an on/off switch
I drive it with a moc3021z and my load is a 220v led string . When i stop triggering moc3021z my led starts blinking . How can i fix this issue ?
Thank you♥️♥️♥️

Reply
Swagatam says:
June 30, 2022 at 9:34 am

Hello Ehsan, Did you build the circuit according to the schematic given in the datasheet of the MOC3021?
Try connecting a 1uF capacitor across the input triggering terminals of the MOC3021 and see if that help.

Reply
Suat Kaleli says:
June 28, 2022 at 7:58 pm

Hi Swagatam;
I have seen the info as “Logic Level” and “Sensitive Gate” for the triacs BT136-600D and 600E. Please advise if those are the same for simple switching purpose or not.
Thanks and regards

Reply
Swagatam says:
June 29, 2022 at 9:43 am

Hi Suat,
Sensitive gate triacs are those triacs which require very less current at their gate for operating. But I am not sure what logic gate triacs are, because all triacs can operate using a logic gate or a logic signal. They all can be used for simple switching purposes.

Reply
Suat Kaleli says:
June 24, 2022 at 10:08 am

Hi Swagatam;
Today I used pic programming with 16f877a and triggered the BT136 gate thru DC 5 V like flip flop led circuit. The result was successful and as a load 220 AC bulb was on and off. Referring the first diagram I need your confirmation about the below matter. I did care that in my circuit, MT1 was connected both of (-) DC ground and AC mains neutral side. Now the point and my question is; Let’s say somebody changed the direction of 220 power plug and now MT1 is live and also in touch of DC – pole. In the case of this situation there is no problem or circuit would be damaged? Best regards

Reply
Swagatam says:
June 24, 2022 at 10:26 am

That’s great Suat, I am glad your circuit was successfully built.
As far as my experience goes and my knowledge goes, the polarity of the LIVE neutral in the first circuit does not matter, Even if you connect the LIVE or the phase to the ground side of the circuit there will be no harm done to the circuit, but yes the entire circuit will float with AC mains and will produce a lethal shock if any part of the circuit is touched with bare hands. But the circuit will not be damaged.

Reply
James says:
June 22, 2022 at 5:47 pm

Sir,
How would I modify the circuit in fig 3 to control either 12 VAC or 240VAC ?

Reply
Swagatam says:
June 22, 2022 at 7:02 pm

James, when you feed 12V AC at the input it will control 12V AC, when you feed 240V AC at the input it will control 240V AC, you can use a DPDT switch to switch between the two input supplies.

Reply
James says:
June 23, 2022 at 3:41 am

Hi Swagatam, thanks for the reply . I think I didn’t frame the question properly . What I would like to know is what component values would need to change to handle a voltage of either 12VAC or 240VAC ? I’m not asking for a circuit to handle both values with one circuit. I would be building two separate circuits to be used individually for each respective voltage to switch on entirely different loads. Thanks again.

Reply
Swagatam says:
June 23, 2022 at 10:39 am

Thank you James for the explanation. You can use the same circuit values for both the versions except R1. For 240V R1 will be 22K 5 watt, and for 12V R1 can be removed entirely and replaced with a wire link.

Reply
Suat Kaleli says:
June 11, 2022 at 1:20 pm

Hi Swagatam;
There is a dimmer circuit with BT136 but another BT136 will switch that dimmer circuit. Please advise if switch circuit would be in serial connection or parallel to the dimmer. Thanks and regards.

Reply
Swagatam says:
June 11, 2022 at 1:42 pm

Hi Suat, the two circuits along with the load must be in series. However, I have never heard of this concept using two light dimmers in series, so not sure how it will work.

Reply
Suat Kaleli says:
June 11, 2022 at 1:51 pm

thanks too much I realized that my test circuit in serial did mislead me since there had been open contact on it however now it has worked best regards

Reply
Swagatam says:
June 11, 2022 at 4:25 pm

Glad it is working now!

Reply
Suat Kaleli says:
June 10, 2022 at 1:15 pm

Hi Swagatam;
Referring to above first diagram as seen trigger voltage is 3 Volts so then to use 2 diodes after 3 volts trigger source is better in case that if AC reverse voltage is applied to the circuit.(I mean if inadvertently MT1 is live and MT2 is neutral connected) or not necessary – Thanks

Reply
Swagatam says:
June 10, 2022 at 2:06 pm

Hi Suat, diodes are not necessary according to me. I have never used diodes at the gate of a triac and my circuits never had problems. Internally the triac is designed in such a way that reverse voltage from MT1 can never reach the gate.

Reply
Suat Kaleli says:
June 11, 2022 at 12:26 am

Excuse me Swagatam. Please let me explain my concern: As we can see at the diagram DC (-) 3 V and AC mains input voltage are both of them connected to the MT1 and I assume that MT1 AC voltage is not live but neutral. I feel as if our DC power supply may be subject to be damaged since it will be in contact of AC voltage. Or in other words in case we connect live pole of AC main inputs to M1 and DC (-) I think then 3 V DC transformer may be damaged. Or simply it is possible to say that either live or neutral but only one pole of AC 220 may touch to the any pole of the DC transformer and no damage risk, no problem. Kind Regards

Reply
Swagatam says:
June 11, 2022 at 9:25 am

I can understand your concern Suat, but you don’t have to worry at all, because when a mains operated triac is connected with a DC circuit it is connected in this standard way only, there’s no other way. The LIVE/Neutral does not matter, you can connect the LIVE to MT1 and neutral to the load still there will be no damage to the circuit. But the only thing is that the entire circuit will float with dangerous mains AC and if you touch anywhere on the circuit in switched ON condition you may get a lethal electric shock….but any other electronic parts can not get damaged for sure, because I have myself built this configuration many times without any damage to the circuit.
The transformer secondary/primary winding are fully isolated from each other so the mains from the triac can never enter the transformer primary side.

Still if you have any fear, you can add a diode on the gate of the triac, as recommended by you earlier.

Reply
Suat Kaleli says:
June 10, 2022 at 10:07 am

Hi Swagatam;
My switching voltage is DC 5V to the gate pin of BT136 and load is a AC 220 heater resistance less than 2 Amps. Please advise proper circuit for that. And also I think DC (-) ground and AC neutral poles should be connected together in the circuit. Thanks a lot.

Reply
Swagatam says:
June 10, 2022 at 10:51 am

Hi Suat,
are you trying to build a PWM heater controller circuit. I think the better option would be to use a light dimmer circuit instead, which can be compact and very reliable.

Reply
Suat Kaleli says:
June 10, 2022 at 11:23 am

Thanks for quick response, my aim is briefly; first of all I will use dimmer to the heater resistance since it causes dry air when heats full capacity then I have been using pic16f877 to control lm35 for environment temperature to keep it between 36 and 38 degrees so the pic16f877 will trigger the heater resistance thru its 5 V DC output if temperature is below to run the heater or over to cut-off.(egg incubator) Kind regards

Reply
Swagatam says:
June 10, 2022 at 11:27 am

OK, so you want to know how to connect the triac with the 5V trigger source? right? In that case you can use the connections as given in the first diagram of the above article.

Reply
Moses says:
May 8, 2022 at 1:25 am

Can triac based dimmer switch be used to drive 120ac load through 220 acv mains by mere adjustment of the potentiometer to 120acv

Reply
Swagatam says:
May 8, 2022 at 9:04 am

It can be tried, but I won’t recommend this, because although the voltage could be reduced to 120V, but the peak can still remain at around 300V.

Reply
Moses says:
May 8, 2022 at 11:47 am

How can I build ac to ac converter that do the job more effectively without the use 220 to 120acv transformer. I need it to drive 115acv rated air conditioner cooling fan.

Reply
Swagatam says:
May 8, 2022 at 1:31 pm

That is not possible without transformers. It can be possibly done through an SMPS circuit but that would be a lot costlier and much complicated

Reply
Venkat Mamidala says:
January 24, 2022 at 11:25 am

Dear sir,
I have a doubt that, normally triac needs +ve and -ve gate supply to make conduction of both SCR’s, but in your circuit (First circuit) you gave 3v dc through 1k resistor. Can you please clearly explain how triac operating here.

Reply
Swagatam says:
January 24, 2022 at 1:30 pm

Hello Venkat, triac will switch an AC signal only when a DC is applied at its gate….a 0V at the gate will turn OFF the triac at the zero crossing of the AC cycle, while a negative voltage will turn off the triac instantly regardless whether the waveform is at zero crossing or not.

Reply
Venkat says:
February 1, 2022 at 11:50 am

Dear sir,
I have few doubts , please give me some clarity regarding my doubts

In my circuit, gate is negative (ground by using IC) and here T1 connected to both phase(230v AC) and 5v dc from rectifier circuit and T2 connected to single phase motor . Here capacitor is connected between gate and T2.

When ever I want to turn on triac, I will supply 5v from micom to IC then IC output will be grounded(gate terminal)and triac turned on till micom supply is there.

My question is
1) Here T1 connected to both phase and 5v dc . Means here we shorted Ac and DC lines. Is this acceptable?
2) what is the role of capacitor here.?
3) How trigger happening here.( I want to know how triac differentiate ac and dc signal when gate connected to ground)?

Sir you didn’t understand my doubts please send me your mail ID i will share circuit and explain it properly

Reply
Swagatam says:
February 1, 2022 at 1:41 pm

Hello Venkat, I did not understand your question. My email ID is given in the contact page. Please make sure the schematic is drawn correctly.

Reply
Venkat says:
February 1, 2022 at 11:52 am

Sorry
*****capacitor connected between T1 and g
ate

Reply
Nosa says:
November 15, 2021 at 10:59 am

Good morning sirI’m trying to figure out the alternator booster diagram where the traic circuits posted

Reply
Swagatam says:
November 15, 2021 at 11:12 am

Hello nosa, here’s the link you are looking for:

https://www.homemade-circuits.com/generatoralternator-ac-voltage-booster/

Reply
ulises says:
November 11, 2021 at 7:45 am

grate information

Reply
Swagatam says:
November 11, 2021 at 10:10 am

thank you!

Reply
Cris P says:
October 25, 2021 at 1:41 am

Pardon my ignorance, but I missed the point of why one would want to do this and not just use a mechanical switch. Perhaps remote controlled switching? But many of the circuits do have mechanical triggers, so I’m still confused what the benefit is.

Reply
Cris p says:
October 25, 2021 at 9:56 pm

Thank you!

Reply
Swagatam says:
October 25, 2021 at 7:55 am

It is because mechanical switches are bulky, prone to wear and tear, and they make noise and sparking while operating. The small switch shown in the circuit diagrams are only for indicative purpose, they can be actually replaced with sensors or other forms of external signal inputs.

Reply
Harry Vincent says:
October 22, 2021 at 2:12 am

Hi Mr. Swagatam, I am looking for a voltage sensing circuit to control a relay to start my solar inverter when the solar cell reaches 15.5 V. do you know of anything suitable ??
thanks in advance
kind regards Harry Vincent

Reply
Swagatam says:
October 22, 2021 at 4:04 pm

Hi Harry, you can apply the following circuit for controlling the solar panel voltage:

solar panel voltage limit controller circuit

you will have to adjust the 10k preset to set the exact tripping voltage level.

Reply
Moses says:
October 23, 2021 at 1:57 am

The above descriptions are wonderful. Please I would like see a schematic involving triac for regulating ac motor or as light dimmer capable of controlling up to 2000w worth of power

Reply
Swagatam says:
October 23, 2021 at 11:22 am

Thank you Moses. I already have a light dimmer related article, whose triac can be upgraded for controlling heavier loads.

Reply
Moses says:
October 23, 2021 at 9:24 pm

Thanks sir,I have seen them and they are very useful.

Reply
Swagatam says:
October 24, 2021 at 9:15 am

You are welcome Moses!

Reply
Harry Vincent says:
October 23, 2021 at 1:00 am

Many thanks for the circuit Swagatam. Much appreciated

Reply
Swagatam says:
October 23, 2021 at 8:12 am

Thank you Harry! Glad you liked it!

Reply
Back to Newest

Need Help? Please Leave a Comment! We value your input—Kindly keep it relevant to the above topic! Cancel reply

Your email address will not be published. Required fields are marked *

Primary Sidebar

circuit simulator image



Subscribe to get New Circuits in your Email



Categories

  • Arduino Projects (93)
  • Audio and Amplifier Projects (133)
  • Automation Projects (17)
  • Automobile Electronics (101)
  • Battery Charger Circuits (85)
  • Datasheets and Components (109)
  • Electronics Theory (149)
  • Energy from Magnets (27)
  • Games and Sports Projects (11)
  • Grid and 3-Phase (20)
  • Health related Projects (27)
  • Home Electrical Circuits (13)
  • Indicator Circuits (16)
  • Inverter Circuits (95)
  • Lamps and Lights (159)
  • Meters and Testers (71)
  • Mini Projects (28)
  • Motor Controller (68)
  • Oscillator Circuits (28)
  • Pets and Pests (15)
  • Power Supply Circuits (91)
  • Remote Control Circuits (50)
  • Renewable Energy (12)
  • Security and Alarm (64)
  • Sensors and Detectors (106)
  • SMPS and Converters (34)
  • Solar Controller Circuits (60)
  • Temperature Controllers (43)
  • Timer and Delay Relay (49)
  • Voltage Control and Protection (42)
  • Water Controller (36)
  • Wireless Circuits (30)





Other Links

  • Privacy Policy
  • Cookie Policy
  • Disclaimer
  • Copyright
  • Videos
  • Sitemap



People also Search

555 Circuits | 741 Circuits | LM324 Circuits | LM338 Circuits | 4017 Circuits | Ultrasonic Projects | SMPS Projects | Christmas Projects | MOSFETs | Radio Circuits | Laser Circuits | PIR Projects |

Social Profiles

  • Twitter
  • YouTube
  • Instagram
  • Pinterest
  • My Facebook-Page
  • Stack Exchange
  • Linkedin



Recent Comments

  • Swagatam on IC IR2111 H-Bridge MOSFET, IGBT Driver IC: Full Datasheet, Circuit Diagram
  • Swagatam on Electronic Circuit Projects, Tutorials, and Practical Engineering Solutions
  • arj on IC IR2111 H-Bridge MOSFET, IGBT Driver IC: Full Datasheet, Circuit Diagram
  • Moldyhvac on Electronic Circuit Projects, Tutorials, and Practical Engineering Solutions
  • Swagatam on IC IR2111 H-Bridge MOSFET, IGBT Driver IC: Full Datasheet, Circuit Diagram

© 2026 · Swagatam Innovations