Voltage spikes  can sometimes be a big nuisance as far as the safety of the various electronic appliances are concerned. I have explained how to make a simple AC Mains surge protector circuits at home.

Table of Contents
  • What is a Surge Protector
    • What is Voltage In Rush
  • Working Design
    • Metal Oxide Varistor (MOV) Calculations and Formulas
  • Transient Protector Using Inductors and MOV
    •  
    • Using an NTC and MOV
  • Formulas for Calculating MOV and NTC Parameters
    • NTC (Negative Temperature Coefficient) Thermistor Formulas
    • Additional Formulas:
    • RFI Line Filter and Surge Suppression Circuit
    • Sources

What is a Surge Protector

A surge protector is an electrical device which is designed to neutralize minor electrical spikes and transients that normally keep appearing in the mains utility lines.

These are normally installed in sensitive and vulnerable electronic equipment to prevent them from getting damaged due to these sudden unprecedented surges and voltage fluctuations.

They work by instantaneously short circuiting any excess high voltage that may appear in the mains AC line for a very duration.

This duration is usually lasts in microseconds. Anything above this period of time may cause the surge suppressor itself to burn or get damaged

What is Voltage In Rush

A sudden voltage spike is basically a sharp rise in the voltage lasting not more than a few milliseconds but enough to cause damage to our precious equipment almost instantly.

It thus becomes imperative to stop or block these from entering vulnerable electronic gadgets like our personal computers.

Commercial spike busters are though available pretty easily and cheaply too, cannot be trusted and moreover have no reliability test arrangement so it becomes just a "assuming" game, until it's all over.

Working Design

The circuit of a Simple AC Mains Surge Protector Device below, which shows how to make a simple homemade AC mains high current protector device is based on very simple principle of "speed breaking" the initial jolt through components who are well equipped in the field.

A simple iron resistor and MOV combination are more than enough to provide the protections we are looking for.

Here R1 and R2 are 5 turns of iron wire (0.2mm thick) over a 1 inch diameter air core each followed by an appropriately rated varistor or an MOV connected across them to become a full fledged spike protector system.

Sudden high AC entering the input of spike  are effectively tackled and the "sting" absorbed in the course by the relevant parts and a safe and clean mains is allowed to go through the connected load.

Metal Oxide Varistor (MOV) Calculations and Formulas

The calculation of energy during application of such a pulse is given by the formula:

E = (Vpeak x I peak) x t2 x K
where:
Ipeak = peak current
Vpeak = voltage at peak current
β = given for I = ½ x Ipeak to Ipeak
K is a constant depending on t2, when t1 is 8 μs to 10 μs
A low value of β corresponds to a low value of Vpeak and then to a low value of E.

Transient Protector Using Inductors and MOV

inductor MOV based surge suppressor circuit diagram

Question Regarding Surge Prevention in Electronic Ballast

Hi swagtam, I found your email address from your blog. I really need yr help.

Actually my company has customer in china we make UV lamps and we use electronic ballast for it.

Now the problem is in china because of Over Voltage the ballast burn out so i design circuit which is in attachment which doesn't help either?

So I found your Ultimate High/Low Voltage Protector Circuit which i wants to build. or can you tell me the update if i can do in my circuit that will be great.

Solution

According to me the problem may not be with the voltage fluctuations, rather it's because of the sudden voltage surges that's blowing of your ballast circuit.

The diagram shown by you may not prove very effective, because it does not incorporate a resistor or any kind of barrier with the MOVs.

You may try the following circuit, introduce it at the entry point of the ballast circuit.

Hope it works:

surge suppressor circuit diagram using resistors, MOV and fuse

 

Using an NTC and MOV

The following image shows how two different sudden high voltage suppressor devices could be tied up with the mains line for achieving a double edged safety.

The NTC here enables an initial switch ON current in rush protection by offering a higher resistance due to its initial lower temperature, but in the course of this action its temperature begins increasing and it begins allowing more current for the appliance until a normal working conditions achieved.

The MOV on the other hand complements the NTC output and makes sure that in case the NTC is unable to stop the up-surge onslaught correctly, it switches ON itself shorting the residual high transient content to ground and as a result establishing a safest possible supply for the connected load or the appliance.

surge suppressor circuit diagram using MOV and NTC

Highly Recommended for you: 220 V AC Filter Circuit


Formulas for Calculating MOV and NTC Parameters

NTC (Negative Temperature Coefficient) Thermistor Formulas

Resistance-Temperature Relationship (NTC Thermistor)Using the Beta Parameter Equation:

R(T) = R0 * e(β * (1/T - 1/T0))

Where:

  • R(T) = resistance at temperature T (in ohms, Ω)
  • R0 = resistance at a reference temperature
  • T0 (in ohms, Ω)
  • β = material constant (in K)
  • T = temperature in kelvins (K)
  • T0 = reference temperature in kelvins (K), usually 298 K (25°C)

Using the Steinhart-Hart Equation (more accurate):

1/T = A + B * ln(R) + C * (ln(R))3

Where:

  • T = temperature in kelvins (K)
  • R = resistance at temperature T (in ohms, Ω)
  • A, B, C = constants that depend on the specific thermistor.

Thermal Time Constant (NTC Thermistor)τ = (Cth * R) / P

Where:

  • τ = thermal time constant (in seconds, s)
  • Cth = thermal mass of the thermistor (in joules per degree Celsius, J/°C)
  • R = resistance of the thermistor (in ohms, Ω)
  • P = power dissipated by the thermistor (in watts, W)

Inrush Current Limiting (NTC Thermistor)I(t) = V / R(T(t))Where:

  • I(t) = current at time t (in amperes, A)
  • V = supply voltage (in volts, V)
  • RT(t) = resistance of the thermistor at the temperature T(t) (in ohms, Ω)

Additional Formulas:

MOV:

Voltage-Resistance Relationship:
R(V) = (Vr2) / (V2 - Vr2) * Rmax

Energy Absorption:
E = 1/2 * C * Vmax2

Clamping Voltage:
Vclamp = Vr * (I / Irated)α

NTC Thermistor:

Beta Parameter Equation:
R(T) = R0 * e(β * (1/T - 1/T0))

Steinhart-Hart Equation:
1/T = A + B * ln(R) + C * (ln(R))3

Thermal Time Constant:
τ = (C_th * R) / P

Inrush Current Limiting:
I(t) = V / R(T(t))

    RFI Line Filter and Surge Suppression Circuit

    If you are looking for a mains AC line filter circuit having a combined protection against radio frequency interference (RFI) suppression, along with voltage surge control, then the following design could prove quite handy.

    RFI line filter circuit diagram with surge suppression

    As we can see, the input side is protected with an NTC and MOV. The MOV grounds any instantaneous over voltage surge, while the NTC limits an over current surge.

    The next stage constitutes an RFI line filter, comprising of a small ferrite transformer and a few capacitors.

    The transformer arrests and blocks the passage of any incoming or outgoing RFI across the line, while the capacitor network reinforces the effect by grounding the residual high frequency content across the line.

    The transformer is built over a small ferrite rod, having two identical winding wrapped one over the other, and one of the winding end connections swapped between the input/output Neutral line.

    Sources

    • ti.com
    • bourns.com
    • littelfuse.com

    You'll also like:

    • partslistSG 3525 Automatic PWM Voltage Regulation Circuit
    • passive 2Power Factor Correction (PFC) Circuit – Tutorial
    • avr analyzer circuitAutomatic Voltage Regulator (AVR) Analyzer
    • wiringAutomatic Voltage Stabilizer Circuit for TV sets and Refrigerator

    Filed Under: Voltage Control and Protection Tagged With: 120V, 220V, AC, Mains, Protector, Surge

    About Swagatam

    I am an electronics engineer and doing practical hands-on work from more than 15 years now. Building real circuits, testing them and also making PCB layouts by myself. I really love doing all these things like inventing something new, designing electronics and also helping other people like hobby guys who want to make their own cool circuits at home.

    And that is the main reason why I started this website homemade-circuits.com, to share different types of circuit ideas..

    If you are having any kind of doubt or question related to circuits then just write down your question in the comment box below, I am like always checking, so I guarantee I will reply you for sure!



    Previous Post: « Simple Peltier Refrigerator Circuit
    Next Post: How to Configure a Solar Panel System – Living of the Grid »

    Reader Interactions

    Questions & Answers

    Total Posts: 177
    Newest Oldest
    Max johnson
    July 3, 2026 • 2 weeks ago #209324

    How does this differ than an AC powerline inlet filter?

    Like TE dotcom 6amp:
    2-1609109-1

    I am actively searching for something that will stop reading light flickering while the window attached airconditioner runs

    One outlet in room with two sockets

    Top socket for air conditioner

    Botton socket for non-surge power strip:

    ♦️spigen 100watt PD USB (20v 3a laptop),
    ♦️ 65waa pd usb (iphone),
    ♦️ reading lamp multibulb

    It would be interesting to have an engineer evaluate Spigen’s claim about their “ArcStation Pro” feature reducing noise and ripple. Spigen is a brand designing quality pd usb chargers (and garage phone cases).

    Reply
    SwagatamAdmin
    July 4, 2026 • 1 week ago #209342

    The above circuits are just for safety, where the MOV stops big voltage spikes like lightning and the NTC stops big sparks when turning things on, but they don’t clean the power. The TE filter is for cleaning high-frequency electric noise so your electronics don’t buzz or mess with each other.

    Your lamp flickers because when the AC compressor turns on, it takes a huge amount of power instantly, making the voltage in your wall outlet drop for a split second. Neither the above circuits nor the TE filter can fix this because they can’t put dropped power back into the load. It’s the same for Spigen’s tech—it makes the DC power going into your phone very smooth, but it can’t fix the bad AC power coming from the wall. The easiest fix is to change your lamp bulb to a good, dimmable LED bulb because they have better parts inside that can handle that quick voltage drop without blinking!

    Reply
    Olugbenga
    September 24, 2025 • 10 months ago #186349

    Hi Swagatam,
    I am trying to build a automatic Change over circuit. this circuit will be used for switching from Generator set to public mains supply, that will be made up of switching cct, Surge protector cct and filtering cct. indicator lights and alarm will be added. thank you.

    Reply
    Mahesh
    August 18, 2024 • 2 years ago #158298

    Require TVs diode rating for 4 kV surge suppressor input voltage is 230 vAC.
    Require solar flasher circuit for beacon light

    Reply
    Mahesh
    August 19, 2024 • 2 years ago #158375

    Thanks for the Reply
    I require circuit for solar opearted flasher, solar panel is 5v 150mA, LED 5mm Red 20mA ..8nos,Battery 3.6v Lithium 2600mAH with Dusk to Dawn switch

    Reply
    SwagatamAdmin
    August 20, 2024 • 2 years ago #158461

    I have published the diagram at the end of the following post, please check it out:
    https://www.homemade-circuits.com/rotating-beacon-led-simulator-circuit/

    Reply
    SwagatamAdmin
    August 18, 2024 • 2 years ago #158309

    Sorry, I do not sell electronic components in this website, you can try other online stores, there are plenty of them.

    Reply
    Mahesh
    August 18, 2024 • 2 years ago #158312

    I want only correct rating ,so that I can buy from market.

    Reply
    SwagatamAdmin
    August 19, 2024 • 2 years ago #158344

    If we consider the diode breakdown voltage to be 400V, then the peak current of the diode must be 4000/400 = 10 amp.
    You can search for 400V, 10 amp TVS diode for your application.
    For the beacon light please provide more details regarding the voltage and load current…

    Reply
    KRAB Babu
    May 20, 2024 • 2 years ago #152428

    We designed the PS for triggering solenoids for Pneumatic circuits and using 230 to 24 ac step transformer. But, used a fuse alone in the input side. But customer believes that we did consider for spikes and noises, We have taken earth connection through Transformer leg. Now, i am looking for a cheap surge protector and put that in series to transformer, take the surge protector pin out and connect to load, neutral and earth. 230v ac, SINGLE Phase. Is that correct. what else we need to consdier sir. Thank you.

    Reply
    SwagatamAdmin
    May 20, 2024 • 2 years ago #152431

    Hi Krab, according to me, the following design is the cheapest and the best suitable for your application

    MOV NTC compressed

    Reply
    KRAB Babu
    May 20, 2024 • 2 years ago #152434

    thank you, but could you help me know how and which is connected to Phase , neutral and mainly in Ground Earth please. thanks once again. Why not add GDT for fast discharge . may i seek your view.

    Reply
    SwagatamAdmin
    May 21, 2024 • 2 years ago #152435

    Can you please tell me what exactly are you trying to protect from voltage and current surge?

    Surge protectors like, MOV, NTC, TVS, GDT all these are intended for protecting sensitive electronic circuits and devices, because electronic devices can burn even with a surge lasting only a few milliseconds.

    However, in your case the load seems to be a solenoid mechanism and a transformer which are hugely rugged compared to electronic devices.

    The surge current or voltage which may be capable of burning your transformer or solenoid circuit will also burn all other surge protection devices. So surge suppressors cannot be effective.

    Because to burn a transformer or a solenoid the surge has to last a few seconds which is sufficient to burn any type of surge suppressor.

    So a fuse is the best option that you have chosen to safeguard your inductive equipment.

    If you are using an electronic circuit to control the pneumatic system, in that case the surge suppressors must be separately included within these electronic circuits, and you have to also make sure the solenoid coils include a parallel diode to control the generation of back EMFs.

    Reply
    KRAB Babu
    May 21, 2024 • 2 years ago #152439

    Swagatham, i thank you for a detailed reply. This is a basic protection mechanism for the transformer powered solenoid valves energised through a bridge circuit. In fact, the normal expected failure mode at customer site, is huge inductive loads due to rotating components in their manufacturing site. So, whatever we supply them , need to take care of inductive loads . This is my view. A Basic protective mechanism. In addition, i had taken earth from the transformer body and given to customer location. Having said all these, the only fear is fluctuating inductive loads and some ground disturbances (??) less probability though. Hence, i wanted to request if GDT Will also help.

    Reply
    SwagatamAdmin
    May 21, 2024 • 2 years ago #152440

    Thank you Krab,
    That’s right. Your approach of using a GDT on the AC input side and grounding the transformer body is perfectly correct.
    However an inductive load can get damaged due to sustained over voltage conditions also, which can be protected using a fuse, or a circuit breaker.

    Reply
    SAGAR
    September 5, 2023 • 3 years ago #145054

    Hi Swagatam.
    Can i use three MOV instead of one
    one is for L to N
    one is for L to E
    and one is for N to E
    I am asking you because some extension board company uses 3 MOV

    Reply
    SwagatamAdmin
    September 5, 2023 • 3 years ago #145055

    Hi Sagar,

    Yes you can do that!

    Reply
    SAGAR
    September 5, 2023 • 3 years ago #145056

    Thank you for your reply I have one doubt. So should I use three of the same size of MOV?

    Reply
    SwagatamAdmin
    September 5, 2023 • 3 years ago #145057

    Yes, all the 3 MOVs must be with the same specifications…

    Reply
    kitt
    August 2, 2023 • 3 years ago #144475

    HI Swagatam.
    How do we know if the MOV or NTC has been used up already and need to be replaced? It seems most surge suppressing devices in the market do not have indicator when the surge suppressing mechanism is already done and over? Any ideas on this? Thank you! You are awesome! 🙂

    Reply
    SwagatamAdmin
    August 2, 2023 • 3 years ago #144482

    Thank you Kitt,
    Unfortunately an LED indication might not be possible for indicating a burned or damaged MOV/NTC. The only way perhaps is through a visual identification. Examine the MOV/NTC for any visible signs of physical damage, such as cracks, burns, or discoloration. If you see any of these signs, it’s likely that the thermistors has been damaged and needs replacement.

    Reply
    kitt
    August 6, 2023 • 3 years ago #144567

    Ok, thanks very much, Swagatam. Moreover, regarding MOVs, what is the recommended MOV to protect an inductive, resistive machine (with small 110v AC fan, 110V heater, with solenoid coli) that consumes 500Watts, 220volts? Is the Joule rating the required parameter? And the equipment will be used continuously for 5 years (8 hours off/ 16 hours on)? Thank you again! 🙂

    Reply
    SwagatamAdmin
    August 6, 2023 • 3 years ago #144568

    You are welcome Kitt,
    For a 110V load the MOV rating can be around 130 V RMS. 220V would be too high or the required protection.
    Yes, while choosing a MOV for surge protection, the Joule rating is a vital factor to consider. An MOV’s Joule rating shows its ability to absorb energy. It specifies how much energy the MOV can withstand before degrading or failing.

    Reply
    kitt
    August 7, 2023 • 3 years ago #144588

    Thanks Swagatam. May I know the MOV rating or label that you used in this example above? The image is not quite clear but the NTC is quite clear. Up to what voltage or current or load does your MOV/NTC combination example above protect?

    Reply
    SwagatamAdmin
    August 8, 2023 • 3 years ago #144599

    Hi Kitt, sorry I cannot figure out the number printed on the MOV, it is too blurred. The load is not relevant to MOV but it is relevant to an NTC since NTC is in series with the load. You will have to select the NTC current as per the load current. The voltage of the MOV can be slightly higher than the peak voltage of the AC input supply, and current can be around 1 amp.

    Reply
    Dhananjay Shah
    July 15, 2023 • 3 years ago #144094

    It was not the series connection of capacitor but the multiple capacitor connection in parallel.

    Say as 1pf 1kv can hold a spike or surge of 6.28 Pico sec as it has 1 ohm impedance @ 159 M Hz.

    Now in the same way if the spike is in nano sec an another suitable capacitor has to be introduce. Say as 1000pf will hold spike of 6.28 nano sec as it has 1 ohm impedance @ 0.159 M Hz 

    And so on for micro sec and milli sec

    Reply
    SwagatamAdmin
    July 15, 2023 • 3 years ago #144095

    The 0.1uF capacitor is doing the same thing and in a more efficient way.

    Reply
    Dhananjay Shah
    July 13, 2023 • 3 years ago #144073

    Hello sir,
    Conceptually the circuit is clear, but I would like to know that the capacitors connected with the mains will also draw necessary power from mains.
    Secondly why we are not using the series of capacitors with different values to cope up the different surges of different timings,say as in milli sec, micro sec , tens of millisec, tens of micro sec, etc.,,i.e. 10 pf 630 v , 100pf 400v and so on.
    Please clarify my doubt.

    Reply
    SwagatamAdmin
    July 14, 2023 • 3 years ago #144082

    Hello Dhananjay,
    I guess you are referring to the last schematic. The capacitors have very low values so the consumption will be within 5 to 10mA only which is negligible. I am not sure where the series capacitors can be used, because series capacitors will block a lot current and prevent the load from working normally. By the way a capacitor will never block surge current, in fact it will pass all the surge current through it during the switch ON periods.

    Reply
    Dave
    March 11, 2023 • 3 years ago #140941

    Hi Swagatam,
    I am interested in building a device to plug into an unused 115 VAC outlet on a generator to protect from airborne EMP pulses. Plan to use a ferrite in series and MOV in parallel. This would not be inline with a load. Any suggestions?

    Reply
    SwagatamAdmin
    March 12, 2023 • 3 years ago #140949

    Hi Dave, you can try the last circuit explained in the above article. It has a ferrite core based inductor and an MOV both

    Reply
    parag bari
    January 30, 2023 • 3 years ago #139721

    hello . thanks for sharing the simple home made circuits for voltage and current breakage. i need to know more in details for how NTC is going to stop high current. is it depending on the temperature ?? I am designing one small circuit to make safe home equipment’s like TV , Fridge in villages. as they start their pump , surge comes to main and other home equipment’s get damage. required simple and cost effective circuit for this purpose.

    Reply
    SwagatamAdmin
    January 30, 2023 • 3 years ago #139724

    Hi, yes, NTC prevents current surge through temperature variations.
    Initially, when power is switched ON the temperature of NTC is cooler which causes it resistance to be relatively higher. Due to this higher resistance NTC blocks the switch ON surge.
    However, in the process, it warms up and the NTC temperature rises. When this happens it starts passing more current until the normal amount of current is allowed to pass.

    Reply
    parag bari
    January 30, 2023 • 3 years ago #139725

    Hi… thanks for revert and clearing me.
    so will this NTC sense the surrounding temperature or temperature rise because of high current spike in wire ??
    and if current spike comes , this NTC gets blow down or its just raise the resistance and when current is on normal again the resistance comes down !!

    Reply
    SwagatamAdmin
    January 30, 2023 • 3 years ago #139726

    When NTC temperature is cooler it blocks current when higher it passes more current. As it passes more current it gets warmer. But this change in NTC temperature is quite slow, therefore sudden current changes and spikes cannot happen and in this way the NTC suppresses current surges. However if the temperature of the NTC rises too high then ultimately it will burn and causes an open circuit.

    Reply
    Casper Mostert
    September 21, 2022 • 4 years ago #133413

    Dear Swagatam,
    I live in South Africa and we are bombarded with daily blackouts. My underfloor heating is controlled by WiFi smart switches and I’ve already lost 2x smart switches due to voltage spikes when the power utility restores power. My smart switches are rated for 10ampsp and the max amp drawn from one of the underfloor heating panels is 4.6amps (1050w, 230v) so the smart switches are well within spec. My wall space is extremely limited, so commercially available surge protectors will not fit in the space.
    I saw your circuit and was wondering if using a 2.5E 8A, 20mm disc thermistor coupled with a MOV 14mm RMS=230V 104J varistor will be adequite for the mentioned scenario?

    Any advice will be appreciated

    Thanks

    Reply
    SwagatamAdmin
    September 21, 2022 • 4 years ago #133417

    Hi Casper,
    yes I think the NTC/MOV combination should be able to tackle the switch-ON inrush problem. If it doesn’t then you can perhaps try a delay ON relay timer circuit.

    Reply
    Bob J. Lathim
    August 22, 2022 • 4 years ago #132573

    Dear Sir,
    I Need a circuit to attach to my Ham Radio Power supply(13.8 VDC) and a Battery Back up of (12 Volts DC) so that when the Mains go dead from Blackout the Circuit will automatically switch to the (12 Volt DC Battery) My radio is operated from (12 Volts DC Normally) From a power supply working from the Mains 220 VAC) the radio Draws about 20 Amperes on Transmit so the circuit would have to be able to handle at least (25 amperes @ 12 Volts DC) to be safe.
    I Know they have commercial Units that do this Job, But I like Building my own Gear, I am a Ham Radio Operator.

    Thank you and Namaste

    Reply
    SwagatamAdmin
    August 22, 2022 • 4 years ago #132575

    Hi Bob,
    You can try the following relay configuration for fulfilling your requirement:

    battery to AC DC adaptor relay changeover circuit

    Reply
    Daniel
    April 11, 2022 • 4 years ago #118321

    HI Swagatam,
    I’m at a revision of a Pinball machine. Either I replace the old bulky LineFilterAssembly or I take it apart and replace the components. This Filter is already 30 years old. It contains a Thermistor to limit the inrush current and a Varistor to protect from over voltage and it contains an EMI Filter. The whole LineFilterAssembly feeds a quite big transformer with 1 primary and 9 secondary. The highest secondary is 100V and the lowest is 9V. The whole machine is fused to 220V 5A T. Do you know a compact device who can handle the requirements? Would you restore the original LineFilterAssembly and replace the onboard components?

    Reply
    SwagatamAdmin
    April 11, 2022 • 4 years ago #118343

    Hi Daniel,

    The only EMI filter circuit that I know is the one shown at the end of the above article. You can probably try the last circuit from the above article by building the RFI filter using thick wires, may be 1mm thick.

    Reply
    Roopesh Gowda B M
    March 21, 2022 • 4 years ago #116740

    Hai Swagatam,
    I am working as a hardware engineer in one of the reputed company, and i am working on a filter.
    Basically we install some electronic equipment’s in central railways and there there is 110VAC, which is regulated from railways 25000V. but when switching happens or power on off happens there is a high voltage surge and that surge is spoiling my LC filter as well, please suggest me a way to solve this issue.
    input= 110VAC
    surge = nearly 4000VAC
    surge duration= 3-4 millisec

    please suggest me a way forward to solve this issue.

    Reply
    SwagatamAdmin
    March 21, 2022 • 4 years ago #116760

    Hi Roopesh, I think you must install powerful MOVs at the input side of the AC mains. One such example can be studied in the following article:

    https://www.homemade-circuits.com/high-power-industrial-surge-suppressor/

    Reply
    KABIR ABDULRAZAK
    March 30, 2022 • 4 years ago #117502

    Good morning sir.
    Long time , please I have a question, may I use this circuit to apply it in my arduino circuit to protect my Arduino from EMF . because sometimes my Arduino hocked and stopped working at any time while in working because am using High voltage generator in the circuit.

    Reply
    SwagatamAdmin
    March 30, 2022 • 4 years ago #117515

    Hi Kabir, the above circuits are meant for AC mains surge suppression, not for Arduino circuit. For Arduino circuits, you can feed the 12V to the Arduino through a 7812 IC and connect a 1000uF/25V capacitor right across the DC input pins of the Arduino. This will help you to get rid of any kind of interference from the high voltage generator.

    Reply
    Chaplin
    March 16, 2022 • 4 years ago #116128

    Hi,
    I would like to build an inductor (line reactor) as it was done in the patents used by Zero Surge, Surgex, BrickWall.
    Could you walk us through how to build this type of inductor for overvoltage protection?
    It is a 100mH air inductor in the case of Zero Surge but there are 2 inductors I believe in the case of Surgex which is even more efficient.

    In the case of this circuit, the use of a ferrite would lead to a rapid saturation that is why you propose an iron core in your answers for the protection of overvoltages and not just as a common mode filter?
    In your texts you write ferrites but I think it is rather an iron core (as you have answered to others) since ferrite indicates a mixture of metals… Otherwise, what type of ferrite do you suggest?

    Reply
    SwagatamAdmin
    March 16, 2022 • 4 years ago #116152

    Hi, sorry I do not have the exact calculations for building the kind of surge suppressor that you are referring to, so it is difficult for me to suggest anything useful.

    Yes iron core may work better for mains surge suppressor inductors since the frequency range of the input AC is within 50 and 60 Hz.

    Reply
    View Older Comments

    Need Help? Please Leave a Comment! We value your input—Kindly keep it relevant to the above topic! Cancel reply

    Your email address will not be published. Required fields are marked *

    Primary Sidebar



    My Youtube Channel

    Circuit Simulator

    circuit simulator image



    Subscribe to get New Circuits in your Email



    Categories

    • Arduino Projects (95)
    • Audio and Amplifier Projects (134)
    • Automation Projects (18)
    • Automobile Electronics (103)
    • Battery Charger Circuits (88)
    • Datasheets and Components (109)
    • Electronics Theory (149)
    • Energy from Magnets and Earth (40)
    • Games and Sports Projects (11)
    • Grid and 3-Phase (20)
    • Health related Projects (27)
    • Home Electrical Circuits (13)
    • Indicator Circuits (16)
    • Inverter Circuits (99)
    • Lamps and Lights (162)
    • Meters and Testers (72)
    • Mini Projects (28)
    • Motor Controller (68)
    • Oscillator Circuits (28)
    • Pets and Pests (15)
    • Power Supply Circuits (91)
    • Remote Control Circuits (50)
    • Security and Alarm (65)
    • Sensors and Detectors (107)
    • SMPS and Converters (45)
    • Solar Controller Circuits (60)
    • Temperature Controllers (43)
    • Timer and Delay Relay (50)
    • Voltage Control and Protection (44)
    • Water Controller (37)
    • Wireless Circuits (31)



    Other Links

    • Privacy Policy
    • Cookie Policy
    • Disclaimer
    • Copyright
    • Videos
    • Sitemap

    People also Search

    555 Circuits | 741 Circuits | LM324 Circuits | LM338 Circuits | 4017 Circuits | Ultrasonic Projects | SMPS Projects | Christmas Projects | MOSFETs | Radio Circuits | Laser Circuits | PIR Projects |



    Recent Comments

    • Swagatam on 3 Tested 220V High and Low Voltage Cut OFF Circuits Using IC LM324 and Transistors
    • ENGR BRIGHT on 3 Tested 220V High and Low Voltage Cut OFF Circuits Using IC LM324 and Transistors
    • Swagatam on IC LM393 Complete Datasheet with Circuit Diagram
    • Norman D Kelley on IC LM393 Complete Datasheet with Circuit Diagram
    • Swagatam on Simple Capacitive Discharge Ignition (CDI) Circuit

    Social Profiles

    • Twitter
    • YouTube
    • Instagram
    • Pinterest
    • My Facebook-Page
    • Stack Exchange
    • Linkedin

    © 2026 · Swagatam Innovations